Hi All,
Well finally getting some sun and decent output here in NH after a very snowy February this year. I installed a 7.2KW system 24 LG300 with Solar Edge 300 Optimizers and a 6KW SE Inverter in late December.
The question is this - in full sun the inverter AC output maxes out at 6000W AC or flat lines. I was under the impression that the 6KW inverter would max out at 7500 W AC. Here is a sample output from 11AM - 2 PM.
3/19/2015 11:00 5925.6665
3/19/2015 11:15 5994.1665
3/19/2015 11:30 5998.5
3/19/2015 11:45 6005.1665
3/19/2015 12:00 6006.1665
3/19/2015 12:15 5999.5
3/19/2015 12:30 6006.6665
3/19/2015 12:45 5992
3/19/2015 13:00 6001.8335
3/19/2015 13:15 6001.6665
3/19/2015 13:30 6014
3/19/2015 13:45 6002
3/19/2015 14:00 5989.5
Then screen shot of the inverter showing a snapshot today. It shows 250VAC, 430 VDC, and 6009 Watt AC
Then the panels showing 1.1.1 through 1.1.12 in the screen shot are averaging 230W, 6 Amps, 35 Volts, while the second string of 12 of 1.2.1 through 1.2.12 are averaging 295 watts, 8.7 Amps, 35 volts.
I would expect both sets of panels to be similar and close? What am I missing or is the inverter clipping, or do I have a problem in the first string of panels?
Thanks in advance for your help!
Carl
Well finally getting some sun and decent output here in NH after a very snowy February this year. I installed a 7.2KW system 24 LG300 with Solar Edge 300 Optimizers and a 6KW SE Inverter in late December.
The question is this - in full sun the inverter AC output maxes out at 6000W AC or flat lines. I was under the impression that the 6KW inverter would max out at 7500 W AC. Here is a sample output from 11AM - 2 PM.
3/19/2015 11:00 5925.6665
3/19/2015 11:15 5994.1665
3/19/2015 11:30 5998.5
3/19/2015 11:45 6005.1665
3/19/2015 12:00 6006.1665
3/19/2015 12:15 5999.5
3/19/2015 12:30 6006.6665
3/19/2015 12:45 5992
3/19/2015 13:00 6001.8335
3/19/2015 13:15 6001.6665
3/19/2015 13:30 6014
3/19/2015 13:45 6002
3/19/2015 14:00 5989.5
Then screen shot of the inverter showing a snapshot today. It shows 250VAC, 430 VDC, and 6009 Watt AC
Then the panels showing 1.1.1 through 1.1.12 in the screen shot are averaging 230W, 6 Amps, 35 Volts, while the second string of 12 of 1.2.1 through 1.2.12 are averaging 295 watts, 8.7 Amps, 35 volts.
I would expect both sets of panels to be similar and close? What am I missing or is the inverter clipping, or do I have a problem in the first string of panels?
Thanks in advance for your help!
Carl