Hello all,
I'm looking for a second opinion here regarding my contractors wire size calculations below. I have a 26 panel Solaredge system being installed with 2 strings of 13 panels each. The calculations below in the DC CONDUCTOR AMPACITY CALC'S ROOF CONDUIT shows "# OF STRINGS PER INVERTER: 1" and "# OF CURRENT CARRYING CONDUCTORS: 2"
I was thinking that should read 2 on the strings per inverter (since the plans say 2 strings of 13 panels) and 4 on the current carrying conductors (since it's 2 strings, not 1). If that is in fact what it should show doesn't that mean the calculations are incorrect on the REQUIRED CIRCUIT CONDUCTOR AMPACITY? Should the calc be (1.25)(1.25)(15)(2) = 46.9A instead of (1.25)(1.25)(15) = 23.4A since there are actually going to be 4 conductors in the conduit instead of 2 as shown or is not an issue with Solaredge?
If true then I'm thinking the wire sizing is incorrect since this calulation below (0.76)(1.0)(40) = 30.4A > 23.4A OK, would actually be (0.76)(.8)(40) = 24.4A > 46.9A and that's NOT OK using 10AWG THWN-2 wire. I'm coming up a need for using 4AWG THWN-2 size wire from the NEC Table 310.15(B)(16). (.76)(.8)(95) = 57.7A > 46.9A.
Am I doing this correctly?
I attached the calculations from the submitted and permitted plans below for reference. (the blue highlighting is mine)
Thoughts please,
Thank you
--------------------------
ELECTRICAL CALCULATIONS
SOLAREDGE INVERTERS ARE OPERATING IN A FIXED
STRING VOLTAGE POINT, THEREFORE THE STRING
VOLTAGE IS ALWAYS THE SAME, REGARDLESS OF THE
NUMBER OF MODULES CONNECTED IN THE STRING OR
THE IRRADIANCE POWER OR MODULES TEMPERATURE.
FROM SOLAREDGE INVERTER SPEC SHEET
MAX SYSTEM CURRENT: 15A
MAX SYSTEM VOLTAGE: 350V
DC CONDUCTOR AMPACITY CALC'S ROOF CONDUIT
# OF STRINGS PER INVERTER: 1
EXPECTED MAX AMBIENT TEMP. (°C): 53
TEMP. CORRECTION NEC, TABLE 310.15(B)(2)(a): 0.76
CIRCUIT CONDUCTOR SIZE/TYPE: 10AWG, THWN-2, 90°C
# OF CURRENT CARRYING CONDUCTORS: 2
CONDUIT FILL CORR., NEC TABLE 310.15(B)(3)(a): 1.0
CIRCUIT CONDUCTOR AMPACITY, TABLE 310.15(B)(16): 40A
REQUIRED CIRCUIT CONDUCTOR AMPACITY, NEC 690.8(B):
(1.25)(1.25)(MAX CONTINUOUS DC CONDUCTOR CURRENT)
(1.25)(1.25)(15) = 23.4A
ADJUSTED AMPACITIES FOR CONDUCTORS, NEC 310.15:
TEMP. CORRECTION, NEC TABLE 310.15(B)(2)(a) x
CONDUIT FILL CORRECTION, NEC 310.15(B)(3)(a) x
CONDUCTOR AMPACITY, NEC TABLE 10.15(B)(16)
(0.76)(1.0)(40) = 30.4A > 23.4A OK
10AWG, THWN-2, 90°C WIRE IS OK
I'm looking for a second opinion here regarding my contractors wire size calculations below. I have a 26 panel Solaredge system being installed with 2 strings of 13 panels each. The calculations below in the DC CONDUCTOR AMPACITY CALC'S ROOF CONDUIT shows "# OF STRINGS PER INVERTER: 1" and "# OF CURRENT CARRYING CONDUCTORS: 2"
I was thinking that should read 2 on the strings per inverter (since the plans say 2 strings of 13 panels) and 4 on the current carrying conductors (since it's 2 strings, not 1). If that is in fact what it should show doesn't that mean the calculations are incorrect on the REQUIRED CIRCUIT CONDUCTOR AMPACITY? Should the calc be (1.25)(1.25)(15)(2) = 46.9A instead of (1.25)(1.25)(15) = 23.4A since there are actually going to be 4 conductors in the conduit instead of 2 as shown or is not an issue with Solaredge?
If true then I'm thinking the wire sizing is incorrect since this calulation below (0.76)(1.0)(40) = 30.4A > 23.4A OK, would actually be (0.76)(.8)(40) = 24.4A > 46.9A and that's NOT OK using 10AWG THWN-2 wire. I'm coming up a need for using 4AWG THWN-2 size wire from the NEC Table 310.15(B)(16). (.76)(.8)(95) = 57.7A > 46.9A.
Am I doing this correctly?
I attached the calculations from the submitted and permitted plans below for reference. (the blue highlighting is mine)
Thoughts please,
Thank you
--------------------------
ELECTRICAL CALCULATIONS
SOLAREDGE INVERTERS ARE OPERATING IN A FIXED
STRING VOLTAGE POINT, THEREFORE THE STRING
VOLTAGE IS ALWAYS THE SAME, REGARDLESS OF THE
NUMBER OF MODULES CONNECTED IN THE STRING OR
THE IRRADIANCE POWER OR MODULES TEMPERATURE.
FROM SOLAREDGE INVERTER SPEC SHEET
MAX SYSTEM CURRENT: 15A
MAX SYSTEM VOLTAGE: 350V
DC CONDUCTOR AMPACITY CALC'S ROOF CONDUIT
# OF STRINGS PER INVERTER: 1
EXPECTED MAX AMBIENT TEMP. (°C): 53
TEMP. CORRECTION NEC, TABLE 310.15(B)(2)(a): 0.76
CIRCUIT CONDUCTOR SIZE/TYPE: 10AWG, THWN-2, 90°C
# OF CURRENT CARRYING CONDUCTORS: 2
CONDUIT FILL CORR., NEC TABLE 310.15(B)(3)(a): 1.0
CIRCUIT CONDUCTOR AMPACITY, TABLE 310.15(B)(16): 40A
REQUIRED CIRCUIT CONDUCTOR AMPACITY, NEC 690.8(B):
(1.25)(1.25)(MAX CONTINUOUS DC CONDUCTOR CURRENT)
(1.25)(1.25)(15) = 23.4A
ADJUSTED AMPACITIES FOR CONDUCTORS, NEC 310.15:
TEMP. CORRECTION, NEC TABLE 310.15(B)(2)(a) x
CONDUIT FILL CORRECTION, NEC 310.15(B)(3)(a) x
CONDUCTOR AMPACITY, NEC TABLE 10.15(B)(16)
(0.76)(1.0)(40) = 30.4A > 23.4A OK
10AWG, THWN-2, 90°C WIRE IS OK