My installer says that's it not, and that EMT is required for use inside the attic and in the wall.
The permit wiring diagram shows:
1" EMT / FMC (9)
(9) METALLIC CONDUIT SHALL BE USED WITHIN BUILDING PER NEC 690.31(E).
Section 690.31(E) seems to say it's ok, it just needs to be hung at least 10" below the decking: http://www.homepower.com/2011-nec-section-69031e
Am I missing something here? All things seem to point to it being ok.
The permit wiring diagram shows:
1" EMT / FMC (9)
(9) METALLIC CONDUIT SHALL BE USED WITHIN BUILDING PER NEC 690.31(E).
Section 690.31(E) seems to say it's ok, it just needs to be hung at least 10" below the decking: http://www.homepower.com/2011-nec-section-69031e
Am I missing something here? All things seem to point to it being ok.