I believe NEC 690.12 "Rapid Shutdown" mentions that energized wires that are longer than 10ft from a PV array are to be reduced to not more than 30 volts and 240 VA within 10 seconds of the rapid shutdown initiation.
Most PV systems that incorporate a "string" of panels wired to the inverter will see voltage much higher than 30v. Which to me means that the power has to be disconnected or reduced to 30v at each panel and not at the Inverter. So unless the panels are each rated 30v max and are all wired in parallel, you will be required to use a Micro-inverter or something similar to shut down the power coming from the panel within 10ft of the panel.
Maybe I am reading this wrong but I thought to protect the Fireman that are on your roof, all PV wires need to be de-energized or reduced to 30volts to eliminate any potential of being shocked or electrocuted.
Most PV systems that incorporate a "string" of panels wired to the inverter will see voltage much higher than 30v. Which to me means that the power has to be disconnected or reduced to 30v at each panel and not at the Inverter. So unless the panels are each rated 30v max and are all wired in parallel, you will be required to use a Micro-inverter or something similar to shut down the power coming from the panel within 10ft of the panel.
Maybe I am reading this wrong but I thought to protect the Fireman that are on your roof, all PV wires need to be de-energized or reduced to 30volts to eliminate any potential of being shocked or electrocuted.