Hah, yeah, I texted them about it earlier already. To be fair, some of that is my own doing (the bottom box if for my landscape irrigation, which I installed myself, with flex tubing).Comment
-
I agree that looks terrible. Flexible conduit shouldn't criss cross like that, or should at least be run more horizontal and a lot neater.
And that one between the new Meter pan and the inverter on the other side of the wall may be a little too long per code. They could have install intermediate up to the wall and then flex in the last couple of feet.Comment
-
I rough measured that run to be about 9.5 ft. Not sure what code is here in AZ, but someone told me its 15 ft in California. An NEC 690 article I read didn't mention anything about run length, only that is liquid-tite conduit is used, it must be secured no more than 12" from the any box/junction/etc a day least every 54" in between.I agree that looks terrible. Flexible conduit shouldn't criss cross like that, or should at least be run more horizontal and a lot neater.
And that one between the new Meter pan and the inverter on the other side of the wall may be a little too long per code. They could have install intermediate up to the wall and then flex in the last couple of feet.
It'll need to pass inspection of course and my city is supposed to be super strict so I'm guessing the installer doesn't want to do it twice and is doing it right the right time, aesthetics aside.Comment
-
That looks like typical workmanship in India where the worker thinks it might be inspected. What happens where they think the boss will never look you don't even want to know![SIGPIC][/SIGPIC]Comment
-
Comment
-
I have to look more closely at the NEC, but I thought the longest you can run flex conduit with wires energized above 50volts was 6 feet. Although i could be wrong.I rough measured that run to be about 9.5 ft. Not sure what code is here in AZ, but someone told me its 15 ft in California. An NEC 690 article I read didn't mention anything about run length, only that is liquid-tite conduit is used, it must be secured no more than 12" from the any box/junction/etc a day least every 54" in between.
It'll need to pass inspection of course and my city is supposed to be super strict so I'm guessing the installer doesn't want to do it twice and is doing it right the right time, aesthetics aside.
I hope the inspector passes your install but I would at least check it out with someone that understand the local electrical code.Comment
-
+1.
That is cheap way of doing the installation and hopefully you can pass your inspection. There is no need to look at other installation job.... the installer is cutting corner
Comment
-
derate.JPG
I had to look this up for myself.... yup... the thing starts to derate at 120 degrees, and by 135 degrees, output is cut 30% or so.
...wow.Comment
-
That's not bad. Remember, that the 120F where derate starts is ambient temperature not inverter temperature. Even here in the Valley of the Sun, ambient temps of 120+ are few and far between.Comment
-
Ambient temps are measured in the shade. If the sun beats down on this box, its much higher than ambient.
I find it odd its so temperature sensitive...Comment
-
So temp sensitive? SMA inverters derate too, according to this, at about 45 deg C. Sure, Enphase micros will go up to 65 deg C at full power, but they are intended to be mounted in a very hot location, and kind of have no choice. String inverters are not meant to be mounted in direct sunlight, and the installation manuals for most will tell you that.CS6P-260P/SE3000 - http://tiny.cc/ed5ozxComment
-
Comment
-
The inverter is on a north facing wall which is why I put it outside. I think I might have mentioned earlier already but I measured the temp in the garage at 126 degrees over the summer.Comment
-
This is the very reason that when checking vendor references beyond speaking to them on the phone I asked to visit their home so I could view the installation workmanship myself. Look at this thread where I posted photos of two different installs in which both homeowners were happy about their vendor's work. You never know what someone else is willing to accept.
http://www.solarpaneltalk.com/showth...manship-PhotosComment
Copyright © 2014 SolarReviews All rights reserved.
Powered by vBulletin® Version 6.1.3
Copyright © 2025 MH Sub I, LLC dba vBulletin. All rights reserved.
Copyright © 2025 MH Sub I, LLC dba vBulletin. All rights reserved.
All times are GMT-5. This page was generated at 12:31 AM.

Comment