    120% or 125% NEC backfeed rules as of 2014 code ?

    Ok here is my question or situation.
    I just had a new 6.25kw system installed and all along the way have been going back and fort with the installer electrician as to what was legal regarding the NEC code. Well today I had a city inspector come to do a final inspection and he immediately said my panel would not pass because it had a center-fed 100 amp service breaker and a 30 amp solar back feed breaker at the bottom of the panel. The installer electrician said no this is a 125amp panel buss de-rated to 100amps and they do center fed panels all the time. That still would not allow a 30 amp solar breaker under the 120% rule . Now the actual main switch panel says the system feeds a max of 23 amps so in theory they might be OK with replacing the 30 amp breaker with a 25 amp but . There is no markings of any kind on my panel that says it is has a 125amp bus bar the electrician just says he knows it is because he has seem panels like mine before. The inspector say nuts to that and why would a 30+ yr old service panel be de-rated when the mains are clearly the original 100amp breakers. So then the electrician calls his supervisor and they have a discussion about the fact that supposedly in the new 2014 NEC codes they can now back feed up to 125% and if the panel is indead has a 125amp bus bar it would be legal.

    So anyways as it stands now they have to go back and either prove the inspector wrong or now come out and replace my service panel as I have thought all along. The good news is they will fix it one way or another the bad news is i do not know how long this will take and it further delays my final and permission to operate.

    Has anyone else come across this supposed new 2014 NEC backfeed rule ?
  • inetdog
    Super Moderator
    • May 2012
    • 9909

    #2
    Originally posted by wanabefree
    Ok here is my question or situation.
    I just had a new 6.25kw system installed and all along the way have been going back and fort with the installer electrician as to what was legal regarding the NEC code. Well today I had a city inspector come to do a final inspection and he immediately said my panel would not pass because it had a center-fed 100 amp service breaker and a 30 amp solar back feed breaker at the bottom of the panel. The installer electrician said no this is a 125amp panel buss de-rated to 100amps and they do center fed panels all the time. That still would not allow a 30 amp solar breaker under the 120% rule . Now the actual main switch panel says the system feeds a max of 23 amps so in theory they might be OK with replacing the 30 amp breaker with a 25 amp but . There is no markings of any kind on my panel that says it is has a 125amp bus bar the electrician just says he knows it is because he has seem panels like mine before. The inspector say nuts to that and why would a 30+ yr old service panel be de-rated when the mains are clearly the original 100amp breakers. So then the electrician calls his supervisor and they have a discussion about the fact that supposedly in the new 2014 NEC codes they can now back feed up to 125% and if the panel is indead has a 125amp bus bar it would be legal.

    So anyways as it stands now they have to go back and either prove the inspector wrong or now come out and replace my service panel as I have thought all along. The good news is they will fix it one way or another the bad news is i do not know how long this will take and it further delays my final and permission to operate.

    Has anyone else come across this supposed new 2014 NEC backfeed rule ?
    1. Using a 125A bus in a panel that is delivered as an assembly with a 100A main is common practice among some manufacturers. It reduces the number of bus assemblies they need to make and stock. But the only way to tell for sure would be to get the manufacturer's specifications on the assembly or on the bus itself.

    2. There are lots of options in the 2014 code on how to do backfeed. But it still comes down to the fact that if you are not able to feed into the opposite end from the main, you are limited to 100% of the bus rating, whatever that may be.
    What is different is that, when calculating the backfeed number, instead of using the breaker size you can use 125% of the rated output of the inverter(s). Note that is the inverter output rating, not the size of the panel array feeding it.
    SunnyBoy 3000 US, 18 BP Solar 175B panels.

    Comment

    • wanabefree
      Member
      • Jan 2014
      • 81

      #3
      If i understand correctly

      Originally posted by inetdog
      1. Using a 125A bus in a panel that is delivered as an assembly with a 100A main is common practice among some manufacturers. It reduces the number of bus assemblies they need to make and stock. But the only way to tell for sure would be to get the manufacturer's specifications on the assembly or on the bus itself.

      2. There are lots of options in the 2014 code on how to do backfeed. But it still comes down to the fact that if you are not able to feed into the opposite end from the main, you are limited to 100% of the bus rating, whatever that may be.
      What is different is that, when calculating the backfeed number, instead of using the breaker size you can use 125% of the rated output of the inverter(s). Note that is the inverter output rating, not the size of the panel array feeding it.
      It is possible that I very well could have a 125amp bus panel with a 100amp breaker. However proving it may be a problem because as I stated in my original post there are no marking anywhere on the manufacturer or the ratings. No stickers nothing even the original electrician who did the survey before installation said he did not know for sure.

      Evan if that is true Since it is center fed I believe that at best they could use a 25 amp solar feed breaker and comply with the 120% rule. If I am reading your answer correctly in order to use the 125% rule the main breaker must be at the top of the bus and the solar back feed breaker at the bottom. then they may be able to justify a 30 amp feed breaker.

      Personally I would prefer they just upgrade the panel to a 150 or 200 amp service and be done with it but it is not up to me unless the city refuse to approve what i have. I have been assured that no matter what is required They will cover all costs but only to bring it up to code not just because it is my preference.

      Comment

      • inetdog
        Super Moderator
        • May 2012
        • 9909

        #4
        Originally posted by wanabefree
        Evan if that is true Since it is center fed I believe that at best they could use a 25 amp solar feed breaker and comply with the 120% rule. If I am reading your answer correctly in order to use the 125% rule the main breaker must be at the top of the bus and the solar back feed breaker at the bottom. then they may be able to justify a 30 amp feed breaker.
        Nope. If it is center fed, you get the 100% of bus rating rule, and nothing else. The 120% rule requires opposite ends and the 125% rule just covers how you calculate the backfeed in the first place.

        The idea is that if you put more than 100A of breakers (load) on the far side of the center feed from the PV backfeed the bus will be forced to carry more than 100A and no breakers will blow. No way around that.
        SunnyBoy 3000 US, 18 BP Solar 175B panels.

        Comment

        • wanabefree
          Member
          • Jan 2014
          • 81

          #5
          Still trying to understand

          Originally posted by inetdog
          Nope. If it is center fed, you get the 100% of bus rating rule, and nothing else. The 120% rule requires opposite ends and the 125% rule just covers how you calculate the backfeed in the first place.

          The idea is that if you put more than 100A of breakers (load) on the far side of the center feed from the PV backfeed the bus will be forced to carry more than 100A and no breakers will blow. No way around that.
          So it sounds like in my case there is no way the center fed panel is going to work at all. By the way it is actual not center fed exactly it just has a 40 amp AC & 30amp Dryer breaker above the 100amp main breaker there are six or so 20 & 15 amp breakers below with a 30 amp solar breaker at the bottom. I am pretty sure that is still considered a center fed main.

          I guess i just have to wait and see what they come up with. I just wanted to be at least a little informed in the process.

          Comment

          • inetdog
            Super Moderator
            • May 2012
            • 9909

            #6
            Originally posted by wanabefree
            I just wanted to be at least a little informed in the process.
            You qualify for that anyway.

            If there were some way of guaranteeing that the load above the main never changed from the initially installed 40A and 30A 240V breakers, it would be theoretically safe, but the NEC does not deal in that level of installation-dependent decisions except in a few specific areas like calculating circuit and service loading.

            Look at the full cost of the options that you are offered.
            In some cases (like LADWP) you will not be allowed to put in a 150 or 200 panel without paying for an upgrade of your utility service to a matching level, even if you still put a 100A main in the new panel.
            SunnyBoy 3000 US, 18 BP Solar 175B panels.

            Comment

            • bcroe
              Solar Fanatic
              • Jan 2012
              • 5209

              #7
              That rule is a belt-and-suspenders requirement. The issue is the main input
              and the solar feed will add up to more current on the bus. It's assumes your
              bus can handle 20% more current than the box rating, so that is the feed limit.

              But then it Is specified the 2 feed points must be at opposite ends of the bus.
              So no matter how you arrange the loads in between, its IMPOSSIBLE for the
              2 feed currents to add up on any segment of the bus.

              Comment

              • Sunking
                Solar Fanatic
                • Feb 2010
                • 23301

                #8
                Two rules apply with Inspectors and all you have to know.

                1. Inspector is always right.
                2. When Inspector is incorrect refer to rule 1.

                What it boils down to is it is not your problem to solve or worry about. It is your contractors problem to fix. You have a contract and he owns the responsibility on his dime. So relax.
                MSEE, PE

                Comment

                • wanabefree
                  Member
                  • Jan 2014
                  • 81

                  #9
                  Originally posted by Sunking
                  Two rules apply with Inspectors and all you have to know.

                  1. Inspector is always right.
                  2. When Inspector is incorrect refer to rule 1.

                  What it boils down to is it is not your problem to solve or worry about. It is your contractors problem to fix. You have a contract and he owns the responsibility on his dime. So relax.
                  Sage advice, Easier said than done.

                  However My main reason for posting about it here is to inform others with similar situations and to journal my process while educating myself and others in the process.

                  Comment

                  • Sunking
                    Solar Fanatic
                    • Feb 2010
                    • 23301

                    #10
                    Originally posted by wanabefree
                    However My main reason for posting about it here is to inform others with similar situations and to journal my process while educating myself and others in the process.
                    I understand and in the biz. This is why I would never recommend as a DIY project. Even pros have troubles jumping through the code hoops and stand no chance when code interpretation issues come up. If you DIY you own the problem and will not pass inspection or get connected until resolved. When you have a pro contractor doing the work takes you off the hook and the contractor must resolve before he collects a check and he will correct it to minimize any losses they might incur.

                    Secondly not every jurisdiction is working off 2014 code cycle. Many are still working off of 2011, 2008, and even some 2005 out there. Very few jurisdiction s adopt new code cycle when released. With each code cycle comes extra expense from lessons learned and manufactures pressure to adopt thier new and improved product lines.

                    One big fight that is still not resolved is AFCI breakers. Very expensive and still many jurisdictions do not require them. However with solar many dangers are coming into focus. They are dangerous and present significant fire dangers and FD's and insurance companies have a large loud voice with a large vote percentage in NFPA who writes the electrical codes under NEC division.
                    MSEE, PE

                    Comment

                    • russ
                      Solar Fanatic
                      • Jul 2009
                      • 10360

                      #11
                      Originally posted by wanabefree
                      Sage advice, Easier said than done.

                      However My main reason for posting about it here is to inform others with similar situations and to journal my process while educating myself and others in the process.
                      These points are nothing new - they have been discussed and explained every couple of weeks so the informing others isn't too valid.
                      [SIGPIC][/SIGPIC]

                      Comment

                      • wanabefree
                        Member
                        • Jan 2014
                        • 81

                        #12
                        dont take this personal

                        Originally posted by russ
                        These points are nothing new - they have been discussed and explained every couple of weeks so the informing others isn't too valid.
                        I think that many of the long time well informed and educate folks on this forum take for granted that everyone will just accept the wise and sage knowledge from you guys.

                        I would argue that the many new and less educated posters will always ask questions and not just accept any advise until they are educated and have built up a trust in the person or persons providing such advice.

                        I am one of them and instead of being curt and saying things that discourage them/'me to go elsewhere bear with us. I am a low voltage electrician by trade myself and understand most of the stuff being discussed here but I admit I have a lot to learn about Solar PV systems. I always question blanket remarks or posts as facts until I can be satisfied that it is from a credible source.

                        The same questions will get asked over and over and to the educated they seem just a waist of time but I am pretty sure the next new guy here will appreciate the discussion if not chastised or told to just accept the facts and move one.

                        This is not intended to flame or discount all the good advice available here just to ask for a little more patience and understanding when we post about things that seem redundant to the long time posters but fresh and important to the newcomers.

                        Comment

                        • inetdog
                          Super Moderator
                          • May 2012
                          • 9909

                          #13
                          Originally posted by russ
                          These points are nothing new - they have been discussed and explained every couple of weeks so the informing others isn't too valid.
                          On the other hand, the fine points involved in PV backfeed are subtle enough that even electricians and inspectors (especially inspectors) have very lively discussions about
                          1. What they really say and
                          2. Whether what they say makes any sense from a safety point of view.

                          So although I would be less than thrilled to hear advice and interpretations from someone who just started reading the NEC, I would definitely like to hear about peoples experiences with their local AHJ and the hoops they may have had to jump through as a result.
                          (e.g. this post from Naptown.)
                          Last edited by inetdog; 04-09-2014, 07:48 PM. Reason: added link URL
                          SunnyBoy 3000 US, 18 BP Solar 175B panels.

                          Comment

                          • Naptown
                            Solar Fanatic
                            • Feb 2011
                            • 6880

                            #14
                            Originally posted by inetdog
                            On the other hand, the fine points involved in PV backfeed are subtle enough that even electricians and inspectors (especially inspectors) have very lively discussions about
                            1. What they really say and
                            2. Whether what they say makes any sense from a safety point of view.

                            So although I would be less than thrilled to hear advice and interpretations from someone who just started reading the NEC, I would definitely like to hear about peoples experiences with their local AHJ and the hoops they may have had to jump through as a result.
                            (e.g. this post from Naptown.)
                            That cost was actually each of two panels
                            double the cost to get the result
                            NABCEP certified Technical Sales Professional

                            [URL="http://www.solarpaneltalk.com/showthread.php?5334-Solar-Off-Grid-Battery-Design"]http://www.solarpaneltalk.com/showth...Battery-Design[/URL]

                            [URL]http://www.calculator.net/voltage-drop-calculator.html[/URL] (Voltage drop Calculator among others)

                            [URL="http://www.gaisma.com"]www.gaisma.com[/URL]

                            Comment

                            • Naptown
                              Solar Fanatic
                              • Feb 2011
                              • 6880

                              #15
                              Originally posted by russ
                              These points are nothing new - they have been discussed and explained every couple of weeks so the informing others isn't too valid.
                              The 2014 code just came out.
                              little discussion about it.