    Monitoring 2 pv inverters

    I have a 2kW complete system fitted to one roof and an additional 2kW system fitted (at a later date) to a different roof.
    The systems have 2 seperate Samil Solar River 2300TL inverters mounted close to each other in the attic. Both of these feed into a single SWA cable which runs to the consumer unit and generation meter.
    I have an Elios4you monitor fitted at the CU which monitors total generation, import/export etc.
    However, since having the 2nd system fitted, obviously I can't view the actual generation data from each individual system.
    Does anyone know of a way to monitor the 2 inverters separately?

    Thanks in advance.
  • Shockah
    Solar Fanatic
    • Nov 2013
    • 569

    #2
    Originally posted by dmrolyat
    I have a 2kW complete system fitted to one roof and an additional 2kW system fitted (at a later date) to a different roof.
    The systems have 2 seperate Samil Solar River 2300TL inverters mounted close to each other in the attic. Both of these feed into a single SWA cable which runs to the consumer unit and generation meter.
    I have an Elios4you monitor fitted at the CU which monitors total generation, import/export etc.
    However, since having the 2nd system fitted, obviously I can't view the actual generation data from each individual system.
    Does anyone know of a way to monitor the 2 inverters separately?

    Thanks in advance.
    62203785.jpg

    Something like this pops into mind... although more thought should be put into it.
    [CENTER]SunLight @ Night[/CENTER]

    Comment

    • dmrolyat
      Junior Member
      • Mar 2014
      • 7

      #3
      The inverters are mounted behind attic walls.
      I need a way of remotely monitoring the generation from each inverter.i don't want to be switching each on/off individually.

      Comment

      • inetdog
        Super Moderator
        • May 2012
        • 9909

        #4
        Originally posted by dmrolyat
        The inverters are mounted behind attic walls.
        I need a way of remotely monitoring the generation from each inverter.i don't want to be switching each on/off individually.
        Although it will not give you a theoretically perfect number, you could mount a current transformer in one AC line to each inverter and just look at the output current. Instead of interrupting the AC line you could use a two piece CT which clamps around the existing wire.
        SunnyBoy 3000 US, 18 BP Solar 175B panels.

        Comment

        • Mike90250
          Moderator
          • May 2009
          • 16020

          #5
          do the inverters have any remote data capability ? Any optional add-in board ?
          Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
          || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
          || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

          solar: http://tinyurl.com/LMR-Solar
          gen: http://tinyurl.com/LMR-Lister

          Comment

          • dmrolyat
            Junior Member
            • Mar 2014
            • 7

            #6
            Originally posted by inetdog
            Although it will not give you a theoretically perfect number, you could mount a current transformer in one AC line to each inverter and just look at the output current. Instead of interrupting the AC line you could use a two piece CT which clamps around the existing wire.
            What is a 'two piece CT'?

            Comment

            • dmrolyat
              Junior Member
              • Mar 2014
              • 7

              #7
              Originally posted by Mike90250
              do the inverters have any remote data capability ? Any optional add-in board ?
              Not sure......
              They seem to have rs232 and rs485 ports......
              Does anyone know about the capability of these Samil Solar River 2300TL inverters?

              Comment

              • boostinsteve
                Member
                • Aug 2013
                • 36

                #8
                Originally posted by dmrolyat
                What is a 'two piece CT'?
                It is considered a split core ct. It is usually flexible, and allows you to open the ring, and place it around the cable while the loads stay energized. In order to do this, the X1 X2 leads need to either be shorted, or hooked up to the monitor prior to placing on the line. If not, the CT is going to generate whatever voltage it needs to short the leads together.

                I saw a guy lift a lead one time without shorting, and the arc was about a foot long before he got it back on the strip.

                Comment

                • Mike90250
                  Moderator
                  • May 2009
                  • 16020

                  #9
                  Originally posted by dmrolyat
                  What is a 'two piece CT'?
                  CT=Current Transformer used to measure current in 1 AC wire.
                  Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                  || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                  || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                  solar: http://tinyurl.com/LMR-Solar
                  gen: http://tinyurl.com/LMR-Lister

                  Comment

                  • inetdog
                    Super Moderator
                    • May 2012
                    • 9909

                    #10
                    Originally posted by boostinsteve
                    It is considered a split core ct. It is usually flexible, and allows you to open the ring, and place it around the cable while the loads stay energized. In order to do this, the X1 X2 leads need to either be shorted, or hooked up to the monitor prior to placing on the line. If not, the CT is going to generate whatever voltage it needs to short the leads together.

                    I saw a guy lift a lead one time without shorting, and the arc was about a foot long before he got it back on the strip.
                    Medium and high voltage CTs are very dangerous beasts.
                    But the CTs, especially split core, used for 120/240 volts are usually designed so that the core saturates, reducing the coupling between primary and secondary, well before a hazardous voltage is reached.
                    It is still a good practice to keep the secondary shorted though.
                    SunnyBoy 3000 US, 18 BP Solar 175B panels.

                    Comment

                    • Mike90250
                      Moderator
                      • May 2009
                      • 16020

                      #11
                      Originally posted by dmrolyat
                      Not sure......
                      They seem to have rs232 and rs485 ports......
                      Does anyone know about the capability of these Samil Solar River 2300TL inverters?
                      Try asking the installer, or the Mfg ?

                      OPEN. INTERACTIVE.
                      -- Interface selection – Wi-Fi* and RS485 for more flexible configuration and system monitoring

                      Want me to do any more work for you on this subject, you need to set up a payment plan.

                      Contact the Mfg, or look on their website, and see if they have monitor software. (they have an android app.) http://www.samilpower.com/downloads.php
                      Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                      || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                      || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                      solar: http://tinyurl.com/LMR-Solar
                      gen: http://tinyurl.com/LMR-Lister

                      Comment

                      • boostinsteve
                        Member
                        • Aug 2013
                        • 36

                        #12
                        Originally posted by inetdog
                        Medium and high voltage CTs are very dangerous beasts.
                        But the CTs, especially split core, used for 120/240 volts are usually designed so that the core saturates, reducing the coupling between primary and secondary, well before a hazardous voltage is reached.
                        It is still a good practice to keep the secondary shorted though.
                        Lately, all I have been dealing with is 11.5kv and higher, so my mind draws to worst case scenario.