Try our solar cost and savings calculator
Most Popular Topics
Collapse
Is it possible to "island" Enphase inverters with generator
Collapse
X
-
Most automatic transfer switches will wait a minute or so when the grid comes back up to make sure it is stable before disconnecting and returning the power to the grid. The generator will run for about a minute of so to cool down before shutting down. -
Leave a comment:
-
Should that switchover not be instantaneous? Mine is - no solar involved.Leave a comment:
-
Leave a comment:
-
I hope you have a transfer switch.My generator is tied into the main break panel and there is a timer in the panel that will turn on the generator after 60 seconds or so after the power from the grid is disconnected. Above this switch doesn't get power and below will be powered from the generator.
The problem I have is though, when the power is provided from the electric company there is about a minute where the panel is in a in between state where half the power is coming from the grid and have from the generator until the switch that is open is closed again.
I would have about a 1 minute where the generator and electric grid could be providing some type of power to the main electric panel. Hopefully this will help with your suggestions! Thanks again for your commentsLeave a comment:
-
When power is restored the transfer switch will switch back after it senses stable grid power for a minute or so. When it does switch what you are hearing is the generator going through a cool down period. It is not connected to the grid at this time.Thanks for all the suggestions so far!
My generator is tied into the main break panel and there is a timer in the panel that will turn on the generator after 60 seconds or so after the power from the grid is disconnected. Above this switch doesn't get power and below will be powered from the generator.
The problem I have is though, when the power is provided from the electric company there is about a minute where the panel is in a in between state where half the power is coming from the grid and have from the generator until the switch that is open is closed again.
I would have about a 1 minute where the generator and electric grid could be providing some type of power to the main electric panel. Hopefully this will help with your suggestions! Thanks again for your comments
Secondly no grid tie inverter will start up immediately. There is a 5 minute start up sequence that it must go through before feeding anything to the grid.Leave a comment:
-
Thanks for all the suggestions so far!
My generator is tied into the main break panel and there is a timer in the panel that will turn on the generator after 60 seconds or so after the power from the grid is disconnected. Above this switch doesn't get power and below will be powered from the generator.
The problem I have is though, when the power is provided from the electric company there is about a minute where the panel is in a in between state where half the power is coming from the grid and have from the generator until the switch that is open is closed again.
I would have about a 1 minute where the generator and electric grid could be providing some type of power to the main electric panel. Hopefully this will help with your suggestions! Thanks again for your commentsLeave a comment:
-
Pardon? What do you intend to say?Originally posted by SchnappiYou must contact with the Enphase. That is a so bad quality!Leave a comment:
-
I totally agree. There are many systems out there that have slipped by inspection.You would have to do an AC coupled system which gets very complicated and potentially expensive. It will also void the warranty on the Enphase.
In your situation you would need to tie the solar into the portion of the house that is NOT powered by the generator. If you have a whole house generator that has one big transfer switch for all the house such as a GE symphony etc then the solar will tie in on the line side of the transfer switch to keep it isolated from the generator. Under no circumstances can you have a generator and a solar system feeding your house at the same time unless you are using a hybrid type inverter and the generator is used for battery charging.
Here is another opinon...
Solar Photovoltaic with Generator Backup
Question: Can a grid tied-inverter be connected to a system that also has back up generator power?
Answer: Since a grid-tied inverter does not regulate its power output based on the load requirements it would try to push as much power into the house and the generator as it could when the house is isolated from the grid and something would have to break, be it the inverter or the generator. Which would go has to do with the relative impedances of the two sources and how robust the controllers were. Connecting to a generator would also probably invalidate the warranty of the inverter since all the grid-tied inverter manufacturer's I know specifically say not to do this.
The correct way to back feed in this situation would be to interconnect on the utility side of the transfer switch. I did have one job where we could not connect to the utility side of the transfer switch so I had to design a control system that used the auxiliary contacts in the transfer switch to control a contactor connecting the inverter to the main panel. When the transfer switch was in any position but utility supply the contactor opened and the inverter was isolated.
Sometimes you run into a client that wants to use the PV system when the utility is down, not an unreasonable request I think, but they usually change their mind when I describe what is involved in building a hybrid PV system verses a simple grid-tied system.
shortcircuitLeave a comment:
-
You would have to do an AC coupled system which gets very complicated and potentially expensive. It will also void the warranty on the Enphase.
In your situation you would need to tie the solar into the portion of the house that is NOT powered by the generator. If you have a whole house generator that has one big transfer switch for all the house such as a GE symphony etc then the solar will tie in on the line side of the transfer switch to keep it isolated from the generator. Under no circumstances can you have a generator and a solar system feeding your house at the same time unless you are using a hybrid type inverter and the generator is used for battery charging.Leave a comment:
-
Thanks for the quick response!
So, in the scenario that I described, what will happen with the enphase inverters once the generator comes on?
Also, would you run your p.v. system with either the Sunny Island solution? OR would you try to run your system with the back-up generator providing power?
I'm aware the power will not be consistent as when coming from the grid compared to the generator.Leave a comment:
-
No there is not.Leave a comment:
-
Is it possible to "island" Enphase inverters with generator
I've read about Sunny island by SunnyBoy which supposed to allow a generator and solar to function if power from the grid is not available.
Is there a system like that with enphase.
For example, at my house I have a backup generator that will come on 60 seconds or so after the power from the grid is lost and I'm not sure how or what will happen when using Enphase inverters with the generator that starts after power from the grid is lost???
Copyright © 2014 SolarReviews All rights reserved.
Powered by vBulletin® Version 6.1.3
Copyright © 2026 MH Sub I, LLC dba vBulletin. All rights reserved.
Copyright © 2026 MH Sub I, LLC dba vBulletin. All rights reserved.
All times are GMT-5. This page was generated at 04:38 PM.
Leave a comment: