New PV+Batteries system underperforming

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • aluis
    Junior Member
    • Apr 2023
    • 8

    #1

    New PV+Batteries system underperforming

    I have just gotten a PV system with 5.46kW panels array and around 10kWh of battery storage, using a 6Kw inverter. It came online 2 days ago.

    The inverter is a SAJ H1 and 2 batteries SAJ B1 5.1kWH each.

    It's on a south west facing roof so it gets most direct sun in the afternoon.

    I think I selected a bad installer because, the first issue was that the batteries weren't being detected at all by the inverter. So the installer came over and fixed it. Now only one battery is detected but not the second.

    But the major issue is the under production of power. Yesterday it was a full sunny day and it only produced 1.6kWh the whole day, mainly before 10am, when the sun wasn't yet hitting the panels. During the day with direct sunlight on the panels, production was around 20w only!! I made the installer aware and he's very apologetic and said he'll come over soon.

    However I wonder what could cause this? What is it most likely, that this installer is just clueless or could it be bad parts?





    Last edited by aluis; 04-26-2023, 05:19 AM.
  • SunEagle
    Super Moderator
    • Oct 2012
    • 15199

    #2
    Sounds like the West facing panels are not wired properly into the inverter. And the issue with the second battery may be because it requires a Master/Slave set up.

    I think you are correct in getting the installer involved so they can correct the problems. Keep us informed on how your system performs. Thanks

    And welcome to Solar Panel Talk.

    Comment

    • Ampster
      Solar Fanatic
      • Jun 2017
      • 3658

      #3
      Originally posted by aluis
      .......

      However I wonder what could cause this? What is it most likely, that this installer is just clueless or could it be bad parts?
      If you are off grid, it could be caused by the one battery being full. If you are grid tied the only limit would be the output of the panels. How are you monitoring the output?
      9 kW solar, 42kWh LFP storage. EV owner since 2012

      Comment

      • aluis
        Junior Member
        • Apr 2023
        • 8

        #4
        Originally posted by Ampster
        If you are off grid, it could be caused by the one battery being full. If you are grid tied the only limit would be the output of the panels. How are you monitoring the output?
        I'm connected to the grid. Monitoring using the inverter manufacturers customer portal. Here's the most recent screenshot. The installer is currently at the house trying to get it working. There's some solar power now but it's very choppy. It's been a sunny day but the generation jumps from several kW to nearly zero.

        2023-04-26_15-48.png

        Comment

        • oregon_phil
          Solar Fanatic
          • Jan 2019
          • 501

          #5
          How many panels do you have, what kind are they and are they arranged in two strings connected to the two MPPT inputs? Do you have any shadows on the panels?

          Comment

          • aluis
            Junior Member
            • Apr 2023
            • 8

            #6
            Originally posted by oregon_phil
            How many panels do you have, what kind are they and are they arranged in two strings connected to the two MPPT inputs? Do you have any shadows on the panels?
            No shadows at all. There are 12 x 455w monocrystaline panels. I believe they're all in the same string.

            Comment

            • solardreamer
              Solar Fanatic
              • May 2015
              • 482

              #7
              Does the inverter show any errors? The PV string voltage may be too high.

              Comment

              • oregon_phil
                Solar Fanatic
                • Jan 2019
                • 501

                #8
                I agree. Inverter max voltage 600Vdc, MPPT range 90 to 550VDC.

                OP didn't panel specifics but guess 455 watt panel with half cut cells, Voc ~50 VDC = 600 VDC string voltage and maybe higher due to temperature coefficient depending on location.

                Panels with lower Voc might be OK.

                Disclaimer, I am not an installer.

                Comment

                • aluis
                  Junior Member
                  • Apr 2023
                  • 8

                  #9
                  Originally posted by solardreamer
                  Does the inverter show any errors? The PV string voltage may be too high.
                  I believe you're right. The installer is laying more cable from the roof down as I type, to create a second string. Shouldn't this have been done first time around?

                  Comment

                  • oregon_phil
                    Solar Fanatic
                    • Jan 2019
                    • 501

                    #10
                    One would assume the installer is making two strings of 6 but don't assume anything. Inverter has a start voltage of 120 vdc which would be a string of 3 or 4 panels depending on Voc. Just ask the installer what's going on.

                    Comment

                    • solardreamer
                      Solar Fanatic
                      • May 2015
                      • 482

                      #11
                      Originally posted by aluis

                      I believe you're right. The installer is laying more cable from the roof down as I type, to create a second string. Shouldn't this have been done first time around?
                      Are you talking about the same installer that didn't make sure the batteries were working fully before leaving? If so, I think you know the root problem cause.

                      Comment

                      • aluis
                        Junior Member
                        • Apr 2023
                        • 8

                        #12
                        Originally posted by oregon_phil
                        One would assume the installer is making two strings of 6 but don't assume anything. Inverter has a start voltage of 120 vdc which would be a string of 3 or 4 panels depending on Voc. Just ask the installer what's going on.
                        I confirmed and the strings were indeed split into 6 panels each.

                        The panels are now producing to full capacity but the problems don't end here.

                        The second battery was this morning all of the sudden recognized by the system, without any input from the installer. It's great that they now work but I would like to understand how it is possible that the system corrected itself.

                        The only problem remaining now is that the inverter is throwing 2 errors every couple of hours. They are "Grid Voltage 10 min. Average Overvoltage (energy storage)" and "Battery Open Circuit Warning".

                        When these are triggered the PV output is shut off and energy from the grid is used instead. After half an hour or so it goes back to producing solar.

                        The installer is blaming the unstable grid current that's triggering this. Is this true? I find it weird that the grid could shut down my solar production!

                        Comment

                        • SunEagle
                          Super Moderator
                          • Oct 2012
                          • 15199

                          #13
                          Originally posted by aluis

                          I confirmed and the strings were indeed split into 6 panels each.

                          The panels are now producing to full capacity but the problems don't end here.

                          The second battery was this morning all of the sudden recognized by the system, without any input from the installer. It's great that they now work but I would like to understand how it is possible that the system corrected itself.

                          The only problem remaining now is that the inverter is throwing 2 errors every couple of hours. They are "Grid Voltage 10 min. Average Overvoltage (energy storage)" and "Battery Open Circuit Warning".

                          When these are triggered the PV output is shut off and energy from the grid is used instead. After half an hour or so it goes back to producing solar.

                          The installer is blaming the unstable grid current that's triggering this. Is this true? I find it weird that the grid could shut down my solar production!
                          If your inverter has software that looks at the grid power and does not like what it sees it will turn off for a period of time. The issues could be voltage or frequency from the grid that falls outside the programmed parameters in the inverter. So yes the grid could be causing your inverter to stop.

                          You might have to contact your POCO and see what is happening on the grid and then your installer to see if the program in the inverter can be loosened up a little.

                          Comment

                          • oregon_phil
                            Solar Fanatic
                            • Jan 2019
                            • 501

                            #14
                            Originally posted by aluis

                            I confirmed and the strings were indeed split into 6 panels each.

                            The panels are now producing to full capacity but the problems don't end here.

                            The second battery was this morning all of the sudden recognized by the system, without any input from the installer. It's great that they now work but I would like to understand how it is possible that the system corrected itself.

                            The only problem remaining now is that the inverter is throwing 2 errors every couple of hours. They are "Grid Voltage 10 min. Average Overvoltage (energy storage)" and "Battery Open Circuit Warning".

                            When these are triggered the PV output is shut off and energy from the grid is used instead. After half an hour or so it goes back to producing solar.

                            The installer is blaming the unstable grid current that's triggering this. Is this true? I find it weird that the grid could shut down my solar production!
                            I don't think you said where you are located.

                            Australian example: "The grid voltage Australian standard AS 60038 is 230V +10% -6%, which is a range of 216V to 253V. The Australian standard for your inverter instructs that it must disconnect from the grid if voltage exceeds 255V for 10 minutes or exceeds 260V for any amount of time."

                            Try to search for your country grid's requirements. What specs are used?

                            Manuals and information on the internet regarding your inverter & battery's troubleshooting information are sparse.

                            Battery #2 should have DIP switches set different than battery #1. I have to assume your installer knows how to make and crimp communication cables correctly.

                            Good luck!

                            Attached Files

                            Comment

                            • aluis
                              Junior Member
                              • Apr 2023
                              • 8

                              #15
                              Originally posted by oregon_phil

                              I don't think you said where you are located.

                              Australian example: "The grid voltage Australian standard AS 60038 is 230V +10% -6%, which is a range of 216V to 253V. The Australian standard for your inverter instructs that it must disconnect from the grid if voltage exceeds 255V for 10 minutes or exceeds 260V for any amount of time."

                              Try to search for your country grid's requirements. What specs are used?

                              Manuals and information on the internet regarding your inverter & battery's troubleshooting information are sparse.

                              Battery #2 should have DIP switches set different than battery #1. I have to assume your installer knows how to make and crimp communication cables correctly.

                              Good luck!
                              Thanks, I appreciate the info.

                              I am in Portugal. I'm not sure of the exact specs of the grid voltage but it's definitely in the 200s. The installer said the inverter cutoff because it detected a grid voltage of 250, whic is too high. I have the inverter's manual which doesn't seem to contain parameters to set these limits. I guess these can't be set as they must be within the grids requirements.

                              Does this mean that I have to live with regular solar and battery cutoffs?

                              I also saw the DIP switches in the manual, when the second battery first didn't work, which I sent the installer. He just ignored me. He's probably fed up of my suggestions. I'm very disappointed with my choice of installer but too late to change now. And I'm not sure how to approach this without the communication deteriorating further. I still haven't paid for half of the costs. I'm holding on until everything is as up and running as possible. So I appreciate the feedback as I'm not aware of what he can or can't do about the cutting off issues.

                              Thank you.

                              Comment

                              Working...