What wiring needed 4Powerwall in detached garage 2 back up a house located 20' away?
Collapse
X
-
Tesla seems to have thought out the cookie cutter approach to drive costs down. I have heard of a few instances where the DC capacity was able to be tweaked based on site specifics. I have not heard how the new Tesla inverter choices may influence that flexibility. At those prices i would be in favor of using an agressive DC to AC ratio if I were to get a proposal from Tesla.Last edited by Ampster; 03-23-2021, 03:18 PM. -
Inverter sized to prevent 100amp and 200 amp panel upgrades totally makes sense. Thanks for the reminder.Leave a comment:
-
Tesla recommends both max DC and AC per Powerwall. Max AC power per Powerwall is 7.6kW
AndyLeave a comment:
-
It just says Powerwall, 13.5kWh capacity. I agree the generic query would recommend a low DC watts per powerwall to get sales up. Interestingly enough, the Tesla string inverters are sized 3.8 kw and 7.6 kw.Leave a comment:
-
Last edited by Ampster; 03-22-2021, 01:58 PM.Leave a comment:
-
Leave a comment:
-
I ran the tesla quote machine on the web. For every 4.05kW DC of panels, they recommended 1 Powerwall. Looks pretty basic. Nothing is said about inverters.Leave a comment:
-
Is the maximun capacity of AC coupled solar per Powerwall based on the AC inverter capacity or the DC solar panel capacity?Leave a comment:
-
The reason I brought up the need for 2 Powerwalls has to do with max solar that can be connected to a Powerwall. You could split up the micros and use some to charge Powerwall during a grid outage (connect to gateway) and connect some to line side of gateway so it turns off during grid outage.
AndyLeave a comment:
-
Leave a comment:
-
You and your customer could spend your time more productively thinking about which loads to back up and not worry about the topology of the wiring. Those would be the loads that are swung to the critical loads panel. For simplicity that location would most likely be near where those loads enter the panel.
The larger elements of gateway and Powerwall connection is what your customer is paying Sunrun or Tesla to do as part of the installation process. I am sure you will get a design to approve before construction starts if you want control over that element.
AndyLeave a comment:
-
You and your customer could spend your time more productively thinking about which loads to back up and not worry about the topology of the wiring. Those would be the loads that are swung to the critical loads panel. For simplicity that location would most likely be near where those loads enter the panel.
The larger elements of gateway and Powerwall connection is what your customer is paying Sunrun or Tesla to do as part of the installation process. I am sure you will get a design to approve before construction starts if you want control over that element.Last edited by Ampster; 03-21-2021, 03:45 PM.Leave a comment:
-
Leave a comment:
-
Leave a comment:
-
customer can only afford one power wall, might buy a 2nd latter on. what is the best way to wire up this situation?Leave a comment: