Great and inexpensive monitoring system and a problem to solve.

Collapse
X
 
  • Time
  • Show
Clear All
new posts

  • oregon_phil
    replied
    My point with the graph: In what appears to be random data, there are periods of time when the Darfon is making the correct power (like that flat spot from ~11:47 to 12:57). On either side of that flat spot is lower power and a much noisier signal. What changed?

    Leave a comment:


  • scrambler
    replied
    Originally posted by oregon_phil
    I understand you did have firmware updates that you knew about. Were there any pushed to you that you didn't know about? Sometimes companies think some firmware changes are house cleaning, but in the wild these changes might not be so minor.

    I'm with you, if the battery board blew and now I have troubles, I would be pushing to get a replacement inverter. How can Darfon prove your inverter problems are distinct from the battery board failure? Only by replacing the entire inverter. Your Darfon inverter is different and is not a factory version anymore. Darfon should want the inverter back in their factory so they can do all the testing they want.

    Your manual has voltage ride throughs to determine when to trip offline. 13 secs 264 to 288VAC; 0.166sec above 288VAC.

    I did take a closer look at one of your suspect graphs. If you look at it closely, there are times when the power output is correct (including one longer ~15 minute stretch); and a bunch of places that are wrong in between. Possibilities: Darfon and Tigo's have an interaction that needs to be addressed (Darfon firmware change); The Darfon is damaged from earlier battery board failure.

    I am not a EE and don't understand the inner workings of the Tigos and how that might interfere with inverter MPPT.

    Maybe an electrical type can explain all this stuff to us.
    * No there is no firmware push without my knowledge, I keep an eye on it, and the inverter has to shutdown and reboot for it.

    * I have not provided the full report to the integrator yet, so Darfon is likely not aware of it yet, so no need to jump the gun, I am just getting some feedback before I go to them with the latest info I am gathering

    * I am not sure what your point was about the Graph. The Graph is there to show the major production deviation of the Darfon while the Micro inverters keep producing normally, showing that what the Darfon is doing is not caused by a change in solar radiation, as all panels (18 connected to Darfon and 2 connected to Micro Inverters have the same exact exposure.

    * I have checked with both Darfon and Tigo and they both confirmed there was no interaction problem between them and they are compatible. Certification only applies to the Rapid Shutdown system and although they have not formerly Certified that aspect, it is known to work properly.

    I am continuing monitoring through this week to have at least 10 days of data on the new monitoring system, then I will submit all findings and we will take it form there

    Thanks all for the contributions.

    Leave a comment:


  • scrambler
    replied
    Originally posted by Ampster

    It is possible and worth seeing if there is a correlation. Also frequency changes can accompany changes in voltage. The typical scenerio is that lower voltage may be associated with lower frequency and higher voltages with higher frequency. My guess is the standard that determines the devices response is a range and that may explain different responses of devices to the same event. The standard may give you the answer about what voltage or frequency change light make a difference. I would start with UL 1741SA but there are others as well.
    If we are speaking about Voltage or frequency getting above or below the inverter threshold, the inverter has error codes for that, and it is not throwing any errors during the event, so that should not be the issue.
    It also has error code for derating caused by over temperature.

    Leave a comment:


  • oregon_phil
    replied
    I understand you did have firmware updates that you knew about. Were there any pushed to you that you didn't know about? Sometimes companies think some firmware changes are house cleaning, but in the wild these changes might not be so minor.

    I'm with you, if the battery board blew and now I have troubles, I would be pushing to get a replacement inverter. How can Darfon prove your inverter problems are distinct from the battery board failure? Only by replacing the entire inverter. Your Darfon inverter is different and is not a factory version anymore. Darfon should want the inverter back in their factory so they can do all the testing they want.

    Your manual has voltage ride throughs to determine when to trip offline. 13 secs 264 to 288VAC; 0.166sec above 288VAC.

    I did take a closer look at one of your suspect graphs. If you look at it closely, there are times when the power output is correct (including one longer ~15 minute stretch); and a bunch of places that are wrong in between. Possibilities: Darfon and Tigo's have an interaction that needs to be addressed (Darfon firmware change); The Darfon is damaged from earlier battery board failure.

    I am not a EE and don't understand the inner workings of the Tigos and how that might interfere with inverter MPPT.

    Maybe an electrical type can explain all this stuff to us.

    Darfon-modified.jpg
    Attached Files

    Leave a comment:


  • Ampster
    replied
    Originally posted by scrambler

    Wouldn't that also affect the Micro inverters?
    What Voltage are we speaking of? Given these events last quite long, I can check the voltage while they happen.
    It is possible and worth seeing if there is a correlation. Also frequency changes can accompany changes in voltage. The typical scenerio is that lower voltage may be associated with lower frequency and higher voltages with higher frequency. My guess is the standard that determines the devices response is a range and that may explain different responses of devices to the same event. The standard may give you the answer about what voltage or frequency change light make a difference. I would start with UL 1741SA but there are others as well.
    Last edited by Ampster; 02-10-2021, 01:39 PM.

    Leave a comment:


  • scrambler
    replied
    Originally posted by oregon_phil

    Has Darfon pushed firmware updates to you without you knowing it? maybe they pushed a firmware update at 5 months. They should have a log.
    We did have firmware updates, and the fact the symptom got less severe after another one a few month later, makes me think it is a strong possibility.
    The inverter also blew its battery board due to a flaw in the inverter a few weeks before it started and that was replaced, so there could be some leftover damage...

    Leave a comment:


  • scrambler
    replied
    Originally posted by Mike90250
    if your grid voltage rises from lots of solar pumping power into the grid, that can cause an inverter to either "throttle back" or shutdown for 5 min and restart when voltage is more normal
    Wouldn't that also affect the Micro inverters?
    What Voltage are we speaking of? Given these events last quite long, I can check the voltage while they happen.

    Leave a comment:


  • oregon_phil
    replied
    SMA acquired a minority stake in Tigo. SMA was going the Tigo optimizer route, but now they seem to be going Tigo rapid shutdown with SMA Shadefix MPPT algorithms. I noticed SMA America has removed all Tigo devices from their website except for the JMS-F rapid shutdown unit.

    I have an older -40 model that does not have the integrated Sunspec communication with the Tigo/SMA JMS-F rapid shutdown. My installer specifically told me that I needed a certain firmware version in order for the SMA inverter to operate correctly with the Tigo TS4-RO Optimizers.

    Last year I had my year old SMA inverter replaced due to peculiarities. I spent over six months documenting each fault by day, by event, by screen shot, by etc.

    One thing that happened a couple of months into my SMA inverter ownership is an auto firmware update. As we all know, if anything happens during a firmware update (like a power glitch) then all bets are off. The inverter may or may not work properly. My inverter happened to reboot on its own a random odd times.

    Has Darfon pushed firmware updates to you without you knowing it? maybe they pushed a firmware update at 5 months. They should have a log.

    If you are going to call Darfon, maybe they can tell you how their MPPT works in detail. I know my SMA optitrack used to look for a global MPPT point every 6 minutes, which is different than the local MPPT point. I could see power rhythms that had a 6 minutes intervals as shadows moved across my panels. That was before I had Tigo's installed. Now the power seems to be smoother over the time of day. I'm guessing SMA changed the optitrack MPPT algorithm once it figured out Tigo optimizers were in the mix.

    Leave a comment:


  • Mike90250
    replied
    if your grid voltage rises from lots of solar pumping power into the grid, that can cause an inverter to either "throttle back" or shutdown for 5 min and restart when voltage is more normal

    Leave a comment:


  • scrambler
    replied
    Originally posted by oregon_phil
    I have an SMA inverter that specifically requires a certain firmware upgrade to be commissioned before TIGO optimizer commissioning so it would recognize TIGO optimizers properly. I have no idea why this specific order of commissioning is required, but SMA is very specific about it being required.
    SMA acquired Tigo a while back, and my understanding is that the requirement you mention is so that their reporting can be integrated, not the functionality per say.

    Leave a comment:


  • scrambler
    replied
    Originally posted by scrambler

    I remember being told they were compatible, but let me recheck with Darfon and Tigo if there is formal Certification...
    But there is also the fact that the problem only started about 5 month after the installation. If that was an incompatibility, I would think it would have manifested earlier...

    Leave a comment:


  • scrambler
    replied
    Originally posted by oregon_phil
    "Could the MPPT algorithm of the TIGO optimizers and the Darfon MPPT algorithm be creating conflicts at certain times?"

    I was prepared to ask more detailed questions, but I looked up Darfon inverter compatibility with TIGO optimizers on the TIGO website and couldn't find a listing. Has Darfon been certified with TIGO optimizers?

    I have an SMA inverter that specifically requires a certain firmware upgrade to be commissioned before TIGO optimizer commissioning so it would recognize TIGO optimizers properly. I have no idea why this specific order of commissioning is required, but SMA is very specific about it being required.
    I remember being told they were compatible, but let me recheck with Darfon and Tigo if there is formal Certification...

    Leave a comment:


  • scrambler
    replied
    Originally posted by Ampster
    Good luck with that.
    Back to the topic that attracted my attention, what are the fees with the Emporia monitoring system?
    No Fees, $150 for a split phase plus 16 50A CTs, last 3h of second data download, 30 days of minutes downloads, and unlimited hourly downloads.
    This is a hell of a deal if you ask me

    Leave a comment:


  • oregon_phil
    replied
    "Could the MPPT algorithm of the TIGO optimizers and the Darfon MPPT algorithm be creating conflicts at certain times?"

    I was prepared to ask more detailed questions, but I looked up Darfon inverter compatibility with TIGO optimizers on the TIGO website and couldn't find a listing. Has Darfon been certified with TIGO optimizers?

    I have an SMA inverter that specifically requires a certain firmware upgrade to be commissioned before TIGO optimizer commissioning so it would recognize TIGO optimizers properly. I have no idea why this specific order of commissioning is required, but SMA is very specific about it being required.

    Leave a comment:


  • Ampster
    replied
    Good luck with that.
    Back to the topic that attracted my attention, what are the fees with the Emporia monitoring system?