Greetings! I've recently installed a power system. My inverter is a Sun Gold Power LPF series 5kw, controller is Epver tracer series 10415AN 5kw and running 8 Amerisolar 250w panels for 2kw with the option to upgrade to eight more for a total of 4kw, and my battery bank consists of 16 12v 150ah gel sealed batteries ran 48v series/parallel. Inverter has grid tie capability, but for now I just want to isolate my shop to cut energy costs. When my shop is disconnected from the main and I power up my system everything seems to work as I'm getting power and have no issues with controller or inverter, but when I turn on my air compressor it will not function and the overload warning on the inverter kicks in. Battery bank is is at 57-58v, so it's pretty much fully charged. My question is do I need to hook up to grid power even though I don't want to use that power? The inverter display does show an error message that it does not sense 240v input as it's not hooked up to it. I'm thinking that since inverter does not have any AC input as a baseline, it defaults to keep battery bank charge as primary and AC power out as secondary, thus minimizing amps. Inverter manual does state that it will run power tools including air compressors, and electric motors up to 5hp. Compressor motor is 5hp and the amps at 15. Thanks for any any all help!!!
Inverter dilemma
Collapse
X
-
-
The power factor (PF) of the motor will also increase the demand on the inverter
XWsurgeSpecs.gif
XWsurgeSpecs2.gifPowerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-Lister -
................
I'm thinking that since inverter does not have any AC input as a baseline, it defaults to keep battery bank charge as primary and AC power out as secondary, thus minimizing amps. Inverter manual does state that it will run power tools including air compressors, and electric motors up to 5hp. Compressor motor is 5hp and the amps at 15. Thanks for any any all help!!!
Mike summarized it well above.Last edited by Ampster; 04-19-2020, 03:33 PM.9 kW solar, 42kWh LFP storage. EV owner since 2012Comment
-
Thanks for the input. There is no "surge current" rating in the manual, just states that it can run up to 5hp motors. I figured that there needs to be an ac input for baseline. I'll hook up input, fire the system up and throw the breaker and see what happens. I'm hopin' that once the inverter initially senses ac input it will use that data and when I isolate my shop it will continue to base that initial data to keep peak load output.Comment
-
Forgot one thing... inverter specs do state that surge rating is 15kw for 20 secs, but nothing anywhere about amperage load capacity.Comment
-
At 240v that would be 60 Amps AC. I am sure that would work when on the grid. The issue I would want to explore is whether there a limit on battery Amperage. At 48 volts that same 15kW would be 300 Amps DC. Let us know how your experiment works out.9 kW solar, 42kWh LFP storage. EV owner since 2012Comment
-
Well... hopefully I'll never see the peak wattage, just stating what the inverter rating is. I have a 150 amp breaker on the bank. Just out of curiosity and ****z & giggles, what if the 240vac input comes from the inverter via sub panel that is powered 240 vac from the inverter via batteries? Most of the time the shop is idle so there would be minimum demand. Would the system along with solar keep itself charged, and when I'm pulling a higher demand working in the shop the inverter would sense an input voltage drop and then priority the batteries to take the load? Better to ask a stoopid question than make a stoopid mistake.Comment
-
OK, I replaced the 4000w/12000w peak inverter with a 12000w/36000x peak and viola, my 5hp compressor will start and restart when air pressure drops, and inverter demand is around 34-36% at that time. Now what happens is my 150a 12v dc circuit breaker pops off about a minute after the compressor restarts to top off . All of my cables are 2awg, but I bought some 4/0awg for the bank to inverter thinking the problem is the bottle neck there. The problem now is that the terminals on the 4/0 are way too big to attach to the breaker so I'm looking for any suggestions for a compatible breaker for 48vdc battery bank?Comment
-
Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-ListerComment
-
Comment
Comment