WOW! thanks for this info. I have a combox yes, bought on my own since the solar company didn't tell me it was an option.
So here are my settings
System Devices>XW>Settings>Charger Settings
Battery Type = AGM
Battery Bank Capacity = 220 Ah
Maximum Charge Rate = 100%
Maximum Bulk Charge Current = 140.0 A
Maximum Absorption Charge Current = 140.0 A
Maximum Float Charge Current = 140.0 A
Grid Support = Enabled
XW is set to 2-stage, both Charge Controllers set to 3-stage
Grid Support Voltage = 64.0 V
GVS = Disable
As for the gear I got, it was sold as a package and installed by the company. They are claiming the issue I am experiencing is a firmware issue, so I updated today, but it's been a crap cloudy day so I can't test.
As for your first line...
"With a 220ah bat. bank @ 48v = 10,560wh / 20 = 528w, never pull more than that from that 6.8k inverter!"
Could you elaborate on this, I don't speak electrician very well
I am not sure how I would control this, whether it is a setting within the system, or if you mean out of the panel?
And also, thanks again!!!
So here are my settings
System Devices>XW>Settings>Charger Settings
Battery Type = AGM
Battery Bank Capacity = 220 Ah
Maximum Charge Rate = 100%
Maximum Bulk Charge Current = 140.0 A
Maximum Absorption Charge Current = 140.0 A
Maximum Float Charge Current = 140.0 A
Grid Support = Enabled
XW is set to 2-stage, both Charge Controllers set to 3-stage
Grid Support Voltage = 64.0 V
GVS = Disable
As for the gear I got, it was sold as a package and installed by the company. They are claiming the issue I am experiencing is a firmware issue, so I updated today, but it's been a crap cloudy day so I can't test.
As for your first line...
"With a 220ah bat. bank @ 48v = 10,560wh / 20 = 528w, never pull more than that from that 6.8k inverter!"
Could you elaborate on this, I don't speak electrician very well

And also, thanks again!!!