Charge Controller Setting for battery

Collapse
X
 
  • Time
  • Show
Clear All
new posts

  • Sunking
    replied
    Originally posted by monogram
    My current setting for Boost voltage is already at 29.7V which is little high compared with MPPT default setting at 29.2V.
    • Should I continue increase the Boost voltage? If yes, then to What value?


    What about the Boost Duration, as it currently set at 120 mins (default value)
    • Should I increase it or leave it as is?

    I also noticed the last few days that my Gas Monitor Alarm went off when all doors in the house were closed, could it be the gas coming out from those batteries?

    Please let me know the correct setting as I don't want to explode my batteries.

    Regards,
    Key
    Your questions have been answered. Your battery hydrometer will tell you what the voltage should be. Go back and read the answers.

    Leave a comment:


  • Matrix
    replied
    If your Boost voltage is 29.7 volts and you did not reach a full charge, you either have the option of increasing the Boost time, or the Boost voltage. There is no other option. And since the sun doesn't give you enough time, you can only increase the voltage. As has already been stated why don't you try one half a volt increase to. 30.2 volts boost for a few days and check SG again?

    your manual is telling you that according to your manufacturer boost is what other people here are commenting as absorb.

    Right now at 1.240, IMHO, your SG is too low for a fully charged battery

    Leave a comment:


  • littleharbor
    replied
    I see they refer to the constant voltage, absorb stage as boost. Different mfg. have different words for these phases of charging. .

    Bulk, phase is where your controller allows all available power through to your batteries.

    The set point , 29.7 in your case, to transition from bulk to absorb (constant voltage) is where your controller holds the voltage steady and allows the current to slowly finish charging your batteries. If you have the ability to use % of ah. rating you can ensure your batteries are getting closer to full before you run out of sun for the day. Sunking has a much better explanation of this battery charging stuff. Have you already read the stickies at the top of the category list? I believe he has authored most of them.

    As far as your gas alarm, What kind of gas is it detecting? Aggressively charging batteries produce hydrogen gas, which is lighter than air. propane is heavier than air so the sniffer should be down low for propane. Not sure if a carbon monoxide alarm would detect Hydrogen gas. If your batteries are indoors they need to have some form of ventilation to the outdoors.
    Last edited by littleharbor; 04-09-2018, 06:11 PM.

    Leave a comment:


  • monogram
    replied
    According to MPPT manual, this controller has 3 stages battery charging algorithm:
    Untitled.jpg


    My current setting for Boost voltage is already at 29.7V which is little high compared with MPPT default setting at 29.2V.
    • Should I continue increase the Boost voltage? If yes, then to What value?

    What about the Boost Duration, as it currently set at 120 mins (default value)
    • Should I increase it or leave it as is?
    I also noticed the last few days that my Gas Monitor Alarm went off when all doors in the house were closed, could it be the gas coming out from those batteries?

    Please let me know the correct setting as I don't want to explode my batteries.

    Regards,
    Key
    Last edited by monogram; 04-09-2018, 05:41 PM.

    Leave a comment:


  • littleharbor
    replied
    The Boost voltage number is the point where your controller will transition to absorb. Until your battery reaches the set voltage point it is in boost mode. when it hits that voltage it should hold the voltage at that point until it determines the battery is full. That would be the absorb stage. If you can watch your controller you should see this. Hopefully it doesn't go straight to float as soon as it reaches the boost voltage set point.

    Leave a comment:


  • Matrix
    replied
    Boost

    Leave a comment:


  • monogram
    replied
    Originally posted by Mike90250
    Adding time is one method, but there is seldom enough sun hours, so try going up in voltage a bit, try adding half a volt, and increase Absorb time by an hour. Let that run a couple days and then see if you need more of either
    Am I adding the voltage to Float or BOOST?

    On my Epever MPPT, it does not have Absorb mode, are there any different term for it? (please see above for my setting)

    Leave a comment:


  • Mike90250
    replied
    Adding time is one method, but there is seldom enough sun hours, so try going up in voltage a bit, try adding half a volt, and increase Absorb time by an hour. Let that run a couple days and then see if you need more of either

    Leave a comment:


  • monogram
    replied
    I did not get the one with temperature (glass) as I broke one last time.

    This is the one I got:

    2018-04-09_112630.jpg


    Can I take the temperature by using this:

    2018-04-09_112921.jpg

    What adjustment do I need to make to bring it up to 100%

    Leave a comment:


  • Matrix
    replied
    did you read and look at the Temperature Compensation? Depending on the Temp, you either add or subtract point based on the temp. There is a temp thermometer on the hydrometer. So is the value of 1.240 a temperature compensated value? IF that is the Temp Comp value, I would think it is low. The chart I sent posted here indicates 1.240 is just over 80%. Too Low.

    Leave a comment:


  • monogram
    replied
    Hello All,

    Received the Hydrometer on Saturday, below are the readings:

    On Saturday:
    • At 5PM, the batteries at Float mode, MPPT display battery at 27.4V, SG reading at around 1240 (the needle about 3/7 between 1225 & 1250) (Load OFF)
    • At 11PM, 25.0V with SG=1245 (with LOAD)
    On Sunday:
    • At 7:30AM, 24.6V with SG=1240 (with LOAD)
    • At 10PM, 25.1V with SG=1240 (with LOAD)
    On Monday:
    • At 7AM, 24.6V with SG=1240 (with LOAD)

    Does my reading look normal?

    Do I need to increase the voltage to get SG to 1270?
    ​​​​​​​


    Here is my MPPT settings:
    SETTING User setting
    Over Voltage Disconnect Voltage 33
    Charging Limit Voltage 32.5
    Over Voltage Reconnect Voltage 32.5
    Equalize Charging Voltage 32.4
    Boost Charging Voltage (Bulk) 29.7
    Float Charging Voltage 27.4
    Boost Reconnect Charging Voltage 26.4
    Low Voltage Reconnect Voltage 25.2
    Under Voltage Warning Reconnect Voltage 24.4
    Under Volt. Warning Volt. 24.1
    Low Volt. Disconnect Volt. 24
    Discharging Limit Voltage 23.8
    Equalize Duration (min.) 120
    Boost Duration (min.) 120

    Leave a comment:


  • Sunking
    replied
    Originally posted by Matrix
    To the OP, I do not know if this helps, but I did just find this on another forum
    FWIW and clarification so no one misunderstands when you see a voltage setting like Bulk = 2.4 to 2.45 volts per cell is a window or range of voltages. Example for a 6 volt battery is 7.2 to 7.35 volts at 77 degree F.

    However the Temperature Compensation recommendation is incomplete making it gibberish.

    NOTE: TEMPERATURE COEFFICIENT IS -3mV / Cell
    Should read something like this:

    Add 3 mv for each degree below 77 F
    Subtract 3 mv each degree above 77 F





    Leave a comment:


  • Matrix
    replied
    To the OP, I do not know if this helps, but I did just find this on another forum

    Hard to find, but I got Info on...DEKA GC15 batteries from MFG...recommended charge info (bulk/absorb/equalize) for GC15 6volt 230AH wet cells that lots of us use.

    1. BULK STAGE = 30% of C20 (or 30% of 230Ah)
    - 69 amps (max.current) per series string.
    - Multiple the 69 amps x the parallel strings, if applicable.

    2. ABSORPTION STAGE = 2.40 - 2.45 vpc (x 3 cells) = 7.32 v x the # of batteries in your string

    3. FLOAT STAGE = 2.30 - 2.35 vpc (x 3 cells) = 6.96 v x the # of batteries in your string

    4. EQUALIZE STAGE = 2.50 x 2.55 vpc (x 3 cells) = 7.59 v x the # of batteries in your string

    NOTE: TEMPERATURE COEFFICIENT IS -3mV / Cell

    Leave a comment:


  • Sunking
    replied
    Originally posted by monogram
    I'm sorry to confuse you again. Yes, I understood what you mentioned. The reading is 24.2V not 14.2V as typo error, my fault, sorry.
    No apology needed.

    Originally posted by monogram
    Which mean it take about 2.5 hrs to to fully charge the battery again ? (assume I get 500W output from Charge Controller)
    On paper yes roughly, but not in practice. On a solar system with a MPPT Controller to put 1 usable watt hour into a battery requires the panel to generate 1.5 watt hours to overcome the inefficiencies. Understand?

    Second issue is 2.5 clock hours do not equal 2.5 Sun Hours. A solar panel does not generate it specified power when sun light strikes the panel. At solar noon gets close for a few brief minutes. If you were to look at a graph of Power vs Time from sunrise to sunset would be a Bell Curve? Understand?

    So depending on where you live, even though it may be light 14 hours will only yield you 4 to 6 sun hours in summer, and half that in winter. So in a design you need to know Sun Hours so you can determine panel wattage required. So if you need say 1000 watt hours, the panels must generate 1.5 times that much power of 1500 Watt Hours. You then look up your worse case Sun Hours in winter and lets say it is 3 Sun Hours. Now it is time to find Panel Wattage by factoring out hours so Panel Wattage = Watt Hours / Sun Hours, or 1500 Watt Hours / 3 Sun Hours = 500 watts. So it would take all day to equal 3 Sun Hours in Winter despite it being light 10 clock hours.

    Leave a comment:


  • Matrix
    replied
    Originally posted by monogram
    Hi Matrix,

    Yes, I did see the post from Sunking, found the spec but I could not find SG for the battery, did I missed it? If yes then I need a new glass.

    http://www.eastpennmanufacturing.com...nance-1932.pdf
    You are Correct Sir, not a lot to go on there, but there are many clues to testing and SG beginning in section 3.2 til the end of the document.

    They seem to indicate what I was telling you. EQ a fully charged battery (or at least a battery that is at 1.250 SG) until the SG stops rising. I would think that this point where your battery stops rising is the full SG reading. It will probably be somewhere in excess of 1.277 SG. While doing the EQ, monitor the SG, Cell water level and Battery Temp Regularly. The document gives you charging temps.

    I think your main concern with solar charging will rarely be over charging ... you will more have to be concerned with chronic and repeated under charging. Unless you are way over paneled.