What's a good way to switch charging of the battery-banks from PV to a Grid fed charger. when the batterybank is low and there is not much PV energy?
Automatic switch PV to Grid
Collapse
X
-
-
Get a charge controller with an aux output that can be used to start an external charger when battery voltage falls below a setpoint.
Get a battery monitor with an aux output that can be used to start an external charger when battery total energy falls below a setpoint.
-
The Outback does it all as listed above plus it will even start and stop a generator automatically to charge up the batteries.Comment
-
Comment
-
A Radian GS8048 will give you 8000 watts split phase, and handles generator start. It gives you two auxiliary outputs that you can use to start chargers, generators etc. The next size down is 4000 wattts (GS4048) but will surge to 6000 watts for 5 seconds.Comment
-
OutBack Power, headquartered in Bellingham, Washington and is the leading designer and manufacturer of advanced power electronics for renewable energy, back-up power and mobile applications. The Company is also a member of The Alpha Technologies -- a global alliance of companies that share a common philosophy: create world-class powering solutions for communication, commercial, industrial and renewable energy markets.
you would get it with two FXR3048 (sealed) or FXR3648 (vented) inverters.
OutBack Power, headquartered in Bellingham, Washington and is the leading designer and manufacturer of advanced power electronics for renewable energy, back-up power and mobile applications. The Company is also a member of The Alpha Technologies -- a global alliance of companies that share a common philosophy: create world-class powering solutions for communication, commercial, industrial and renewable energy markets.
Note that the Flexpower is the fully integrated which includes charge controllers, DC breakers, AC breakers etc.OutBack FP1 w/ CS6P-250P http://bit.ly/1Sg5VNHComment
-
Other inverter brands also do this. Schneider Conext XW series inverters, 240V split phase, no extra transformer needed, Some (including myself) state the generator support as implemented by the XW, is superior to the outback / radianPowerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-ListerComment