    Surge Protection Device (SPD) in Hybrid PV System

    Hi everyone,

    Where in a Hybrid PV System would you install SPD's ? AC and DC and how do you size them?

    I'm sure some experienced people over here are able to give the answer.

    Thx in advance

    Regards

    Johan




  • Sunking
    Solar Fanatic
    • Feb 2010
    • 23301

    #2
    At the output of the panels and at the AC service entrance. They are sized to match your wallet as large as you can afford. The real question should be do they do anything. Are you in a Lightning prone area and has your house been struck by Lightning.
    MSEE, PE

    Comment

    • Mike90250
      Moderator
      • May 2009
      • 16020

      #3
      I install both the Delta and the Midnight SPD's At the PV combiner box, input to charge controller and output of the Inverter and the several remote loads fed by the inverter, 1500' of underground AC cable could still pick up an induced surge.

      And it's all moot if you do get a direct hit, the wires in the conduit melt their insulation and need to be replaced even. The electronics will all be toast.
      Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
      || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
      || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

      solar: http://tinyurl.com/LMR-Solar
      gen: http://tinyurl.com/LMR-Lister

      Comment

      • Bendesa1962
        Solar Fanatic
        • Nov 2016
        • 104

        #4
        Originally posted by Sunking
        At the output of the panels and at the AC service entrance. They are sized to match your wallet as large as you can afford. The real question should be do they do anything. Are you in a Lightning prone area and has your house been struck by Lightning.
        So actually only between the inverter and the grid connection and between the inverter and the PV String (s). it makes no sence to install also between the AC inverter output and the House Load? And how about between the inverter and the battery bank?

        Comment

        • Mike90250
          Moderator
          • May 2009
          • 16020

          #5
          Originally posted by Bendesa1962
          ....... And how about between the inverter and the battery bank?
          The batteries are about the very best thing to absorb a blast of power, and anything that cooks an entire battery bank, will also fry any SPD you had on it. You gotta shunt it away while it's still outdoors, at the PV array, or the 120VAC feedlines.

          Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
          || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
          || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

          solar: http://tinyurl.com/LMR-Solar
          gen: http://tinyurl.com/LMR-Lister

          Comment

          • Sunking
            Solar Fanatic
            • Feb 2010
            • 23301

            #6
            Originally posted by Bendesa1962

            So actually only between the inverter and the grid connection and between the inverter and the PV String (s). it makes no sence to install also between the AC inverter output and the House Load?
            99% of all Transient Voltage Surges are from the utility making it the only place you should use one if at all.

            Originally posted by Bendesa1962
            And how about between the inverter and the battery bank?
            Like I said 99% of TVSS enters from the utility line side. That leaves 1% from a direct strike to the panels. Batteries have nothing to do with TVSS



            MSEE, PE