Battery Backup for a Grid-Tied system

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • ButchDeal
    Solar Fanatic
    • Apr 2014
    • 3802

    #31
    Originally posted by NetComrade
    Batteries are expensive, and do wear out. Fuel is expensive, and difficult to acquire during emergencies.

    To give you some context: I was thinking of prolonged outages and how much fuel I could save by having a good combination of generator and battery (and at this point I am assuming, bimodal does not care too much if it's connected to grid power or generator power).
    <SNIP>

    P.S. does bimodal also charge the battery from Grid/Generator?
    If you are just looking for backup then the batteries can lost a bit longer as they will be cycling much less.

    Most bimodal inverters have multiple AC inputs. OutBack Radian is a good example with several AC connections (3 in total).
    In a typical grid tie system with generator, you would use AC connection 1 for the gird, AC connection 2 for generator, and AC connection 3 for emergency panel (your loads that you want up all the time).

    Yes the bimodal inverter can charge from the grid as well as from the generator.
    You would also (in a DC coupled setup) have MPPT charge controller(s) which would allow the batteries to charge from solar as well as to power the inverter. from solar.
    OutBack FP1 w/ CS6P-250P http://bit.ly/1Sg5VNH

    Comment

    • NetComrade
      Member
      • Mar 2013
      • 74

      #32
      Found this guy using Ac Coupled Schneider SW to "fool" his SolarEdge Grid Tie inverter. Says it works, but grid disconnect is manual. Figured i'd share.. haven't looked too much into it, but seems like a fairly cheap solution


      Attached Files
      Last edited by NetComrade; 03-27-2019, 10:43 AM.

      Comment

      • bcroe
        Solar Fanatic
        • Jan 2012
        • 5198

        #33
        Originally posted by NetComrade
        Found this guy using Ac Coupled Schneider SW to "fool" his SolarEdge Grid Tie inverter. Says it works, but grid disconnect is manual. Figured i'd share.. haven't looked too much into it, but seems like a fairly cheap solution
        And where is the solar power going to go if it exceeds the home drain? What about balancing the 120V
        circuits? Why does he not just feed solar to the batteries? Bruce Roe

        Comment

        • NetComrade
          Member
          • Mar 2013
          • 74

          #34
          If you watch the video, he claims the Schneider raises frequency above 60Hz, which tells SolarEdge to send less power

          I am not sure about balancing, isn't that a separate topic ?

          Comment

          • bcroe
            Solar Fanatic
            • Jan 2012
            • 5198

            #35
            Originally posted by NetComrade
            If you watch the video, he claims the Schneider raises frequency above 60Hz, which tells SolarEdge to send less power

            I am not sure about balancing, isn't that a separate topic ?
            My neighbor messed up his neutral and lack of balance burned out the door opener transformer.
            I fixed it 15 feet in the air. Every 120V appliance could be smoked by this idea. Bruce Roe

            Comment

            • Ampster
              Solar Fanatic
              • Jun 2017
              • 3649

              #36
              Originally posted by bcroe

              And where is the solar power going to go if it exceeds the home drain? What about balancing the 120V
              circuits? Why does he not just feed solar to the batteries? Bruce Roe
              I am on the road and can't watch the entire video until later.
              My high level understanding of the concept is the hybrid inverter modulates the output of the grid tie inverter so that the output of the grid tie inverter matches the combined load of the house and charging load. The balancing would have to be done by the grid tie inverter, if not then an auto transformer would have to do that.
              My understanding of why he didnt feed solar to the batteries was that he would have needed to buy a 400v charge controller or rewire his panels for a lower voltage charge controller. I think ButchDeal explained some of that in an earlier post.
              Last edited by Ampster; 03-27-2019, 12:44 PM.
              9 kW solar, 42kWh LFP storage. EV owner since 2012

              Comment

              • ButchDeal
                Solar Fanatic
                • Apr 2014
                • 3802

                #37
                Originally posted by Ampster

                I am on the road and can't watch the entire video until later.
                My high level understanding of the concept is the hybrid inverter modulates the output of the grid tie inverter so that the output of the grid tie inverter matches the combined load of the house and charging load. The balancing would have to be done by the grid tie inverter, if not then an auto transformer would have to do that.
                My understanding of why he didnt feed solar to the batteries was that he would have needed to buy a 400v charge controller or rewire his panels for a lower voltage charge controller. I think ButchDeal explained some of that in an earlier post.
                Grid tie inverters do not generally have any way to balance the legs. Typically an auto-transformer is added to do that.

                It is concerning that he has a manual disconnect so that bimodal inverter is not connected during normal grid usage so how are the batteries maintained? or am I missing something?

                other than hacking this together it looks like a basic AC coupled system.
                OutBack FP1 w/ CS6P-250P http://bit.ly/1Sg5VNH

                Comment

                • Ampster
                  Solar Fanatic
                  • Jun 2017
                  • 3649

                  #38
                  Originally posted by ButchDeal
                  .......
                  It is concerning that he has a manual disconnect so that bimodal inverter is not connected during normal grid usage so how are the batteries maintained? or am I missing something?

                  other than hacking this together it looks like a basic AC coupled system.
                  Yes, I was wondering about the manual disconnect also. My Outback Skybox has an automatic transfer switch. For maintenance, I did install a manual transfer switch. I have the same question about charging batteries.
                  9 kW solar, 42kWh LFP storage. EV owner since 2012

                  Comment

                  • bcroe
                    Solar Fanatic
                    • Jan 2012
                    • 5198

                    #39
                    Originally posted by Ampster

                    I am on the road and can't watch the entire video until later.
                    My high level understanding of the concept is the hybrid inverter modulates the output of the grid tie inverter so that the output of the grid tie inverter matches the combined load of the house and charging load. The balancing would have to be done by the grid tie inverter, if not then an auto transformer would have to do that.
                    My understanding of why he didnt feed solar to the batteries was that he would have needed to buy a 400v charge controller or rewire his panels for a lower voltage charge controller. I think ButchDeal explained some of that in an earlier post.
                    I didn't go back to the beginning. But rewiring the panels is a trivial thing (which has happened to all
                    of mine), certainly a way better idea than this. 400 volt charge controller, fine buy it or rewire to 200V.

                    A grid tie inverter DOES NOT try to match the load, it matches the available solar power. Bruce Roe

                    Comment

                    • Ampster
                      Solar Fanatic
                      • Jun 2017
                      • 3649

                      #40
                      Originally posted by bcroe
                      ...........
                      A grid tie inverter DOES NOT try to match the load, it matches the available solar power. Bruce Roe
                      In this situation the hybrid inverter modulates the grid tie inverter by shifting the frequency that fools the grid tie inverter. In the case of a Solaredge inverter, it is the optimizers that drop off individually. Less panels providing power means less output from the grid tie inverter. My understanding of the concept comes from another forum where Tesla Powerwall users discuss how the Powerwall AC couples to other grid tie inverters. I could be mistaken. AC coupling is complex.
                      Last edited by Ampster; 03-27-2019, 11:21 PM.
                      9 kW solar, 42kWh LFP storage. EV owner since 2012

                      Comment

                      • bcroe
                        Solar Fanatic
                        • Jan 2012
                        • 5198

                        #41
                        Originally posted by Ampster

                        In this situation the hybrid inverter modulates the grid tie inverter by shifting the frequency that fools the grid tie inverter. In the case of a Solaredge inverter, it is the optimizers drop off individually. Less panel providing power means less output from the grid tie inverter.My understanding of the concept comes from another forum where Tesla Powerwall users discuss how the Powerwall AC couples to other grid tie inverters. I could be mistaken. AC coupling is complex.
                        You are completely out in left field. The issues here are the flow and control of energy. I know
                        little of optimizers, but the idea of trying to control a grid tie inverter from its output terminals is
                        quite contrary to the design intent. Even if somehow a design flaw allowed some of this to
                        happen, there is absolutely no assurance that this unintended mode will be a reliable operating
                        function. Soon as it is not, look for the smoke. Bruce Roe

                        Comment

                        • Ampster
                          Solar Fanatic
                          • Jun 2017
                          • 3649

                          #42
                          Originally posted by bcroe

                          You are completely out in left field. The issues here are the flow and control of energy. I know
                          little of optimizers, but the idea of trying to control a grid tie inverter from its output terminals is
                          quite contrary to the design intent. Even if somehow a design flaw allowed some of this to
                          happen, there is absolutely no assurance that this unintended mode will be a reliable operating
                          function. Soon as it is not, look for the smoke. Bruce Roe
                          I have been trying to answer your questions as best as I can. Perhaps my explanation did not make sense. You clearly have more background and technical knowledge than I do.

                          I have spent a great deal of time studying the issue as it is done with a Tesla Powerwall. What I can tell you about that interface is that it uses a separate gateway that acts as the transfer switch. It also uses CT clamps and a Neurio to sense the loads and outputs. It communicates with the Powerwall to shift the frequency of the sync signal. I am not advocating that anyone do that on their own. Various amateurs have tried to "fool" a grid tie inverter with a cheap inverter and the result is the inevitable smoke as you predict.

                          Perhaps the term "fool" is what is misleading? I know that there are tens of thousands of Tesla Powerwalls that have been installed and they allow a grid tie inverter to function when the grid is down. There are other hybrid inverters that can be AC coupled to do the same thing. I haven't watched the complete video that started this dialogue and need to understand what was meant by manual transfer switch. That raised a red flag because if that in any way defeats the safety features built into a grid tie inverter that would be very dangerous.

                          As I mentioned earlier, the high level concept is that the control of the grid tie inverter by the hybrid inverter is done by changing the frequency of the sync signal that the grid tie inverter uses. I dont know any other place on my grid tie inverter except the output terminals where the grid tie inverter would get the signal that it syncs with. Does that make sense?

                          Do you have another explanation of how AC coupling works to enable a grid tie inverter power the loads when the grid is down? ButchDeal described the system in the video as a "basic AC coupled system."
                          Last edited by Ampster; 03-28-2019, 12:01 AM.
                          9 kW solar, 42kWh LFP storage. EV owner since 2012

                          Comment

                          • bcroe
                            Solar Fanatic
                            • Jan 2012
                            • 5198

                            #43
                            Originally posted by Ampster
                            Do you have another explanation of how AC coupling works to enable a grid tie inverter power the loads when the grid is down?
                            I do not have anything else to add for now. Bruce Roe

                            Comment

                            • Ampster
                              Solar Fanatic
                              • Jun 2017
                              • 3649

                              #44
                              I started watching the video and the diagram at the beginning is not correct because it does not show the operation of the automatic transfer switch that isolates the hybrid inverter output from the meter. However his manual disconnect insures that the grid is disconected before he can connect the the hybrid inverter. The hybrid inverter transfer switch may not be able to handle all the loads of that electrical panel. Therefore he came up with the manual work around which may not satisfy the UL or local code requirements.

                              He does use the term frequency curtailment which is another way to describe the AC coupling process how the hybrid inverter uses to control the grid tie inverter.
                              Last edited by Ampster; 03-27-2019, 11:59 PM.
                              9 kW solar, 42kWh LFP storage. EV owner since 2012

                              Comment

                              • jflorey2
                                Solar Fanatic
                                • Aug 2015
                                • 2331

                                #45
                                Originally posted by Ampster
                                In this situation the hybrid inverter modulates the grid tie inverter by shifting the frequency that fools the grid tie inverter. In the case of a Solaredge inverter, it is the optimizers that drop off individually.
                                You may be thinking of the SMA Sunny Island system. The Sunny Island system does that (changes freq) and the microinverters throttle back their output. In a Solaredge system, all the optimizers see is DC so they don't "know" they have to throttle back; that's all under control of the master inverter, and AFAIK the SolarEdge inverter will NOT reduce output as frequency climbs.

                                However, after a certain point, any grid tie inverter will decide that the frequency is too far out of range and drop off completely. That, of course, is a little hard on the hybrid inverter, since it has to go from absorbing thousands of watts to sourcing thousands of watts within one AC cycle.

                                A lot of systems use relay(s) to disconnect the grid tie solar. If you have a microinverter system with a lot of strings of inverters, you can do this one string at a time, which is less stressful to the inverter. But it takes logic that most charge controllers/inverters do not have.