Get a genny and ATS. Everything works in your home while you kick back, relax, and watch your neighbors suffer. Lot less expensive than your way with extremely limited power.MSEE, PEComment
-
One of my requirements is to not have to rewire and thus have everything backed up. ThanksComment
-
City of Denver is not going to sign off on your plan. By code you must rewire your home for an emergency panel. With a Genny, no rewiring, no batteries to replace every few years, no expensive Hybrid inverter, and no limitations on power.MSEE, PEComment
-
A home-brew transfer switch is NOT acceptable. You can ONLY use a UL certified transfer switch, That switch is usually internal to the Solar GT inverter.
if not, that DIY switch is not an accepted device, There are " generator Lock-Out" gates that fit over 2 pairs of breakers in a panel, to switch a house from grid to generator power, but these are designed to only allow one or the other, with no chance of both happening.
Your "designer" (or your interpretation of his design) is flawed
Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
|| Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
|| VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A
solar: http://tinyurl.com/LMR-Solar
gen: http://tinyurl.com/LMR-ListerComment
-
You might seek a second opinion on the wiring up of a critical loads panel if you're bent on going the solar route. An electrician might have better ideas about such then a designer.Comment
-
Get another designer. Besides all the problems mentioned so far it will not work anyway. AC1 will go down if disconnected from the grid. You are finding it hard to do what you are trying to do because it can't be done.OutBack FP1 w/ CS6P-250P http://bit.ly/1Sg5VNHComment
-
You're killing yourself to get "everything backed up", but this isn't feasible unless budget and effort are both inexhaustible. With a hybrid inverter, batteries, generator, and pv, you can still get your whole house backed up but in a reasonable fashion. Several of us here are living with such systems.
Think about this... Why have your non-critical loads backed up with batteries? If you did so and decided to run your oven in a power outage - you'll beat your batteries senseless and one or more large inverters will be needed. That's just for the oven. You'll get far better options by finding alternative ways of accomplishing your non-critical functions without power than trying to run them off batteries. Example... Instead of getting 6 tons of batteries that cost $20k so you can run the oven in a power outage - get a wood or propane cook stove for $2k.Comment
-
I really really appreciate the comments and I'm sorry I have been muddy on my thoughts. I don't want to have everything backed up at all times. When my 13 kW system is bathed in sunshine and the grid is down I would like to have the option to use that power to run any of my normal needs. If my battery bank is full and it's daylight so I'm not running any lights it would be great to run my attic fan or my dishwasher or my laundry or my power saw.
What I seem to be reading here is I will only be allowed by my electrical inspector to have a critical load panel that can be supported just by my batteries regardless if I have 10kw coming out of my modules. So due to not wanting a gazillion batteries I'll just have to let a lot of electricity go to waste on a sunny day if the grid is down.
Is that right?Comment
-
And the bonus is that once you do this you don't even need a transfer switch. It's built in to the inverter.
Last edited by jflorey2; 03-21-2016, 10:53 PM.Comment
-
Some hybrid inverters support the loads all the time, and then direct the surplus toward the "grid". If the inverter is in a branch circuit from your main panel, then the "grid" includes the main panel and the surplus power is available to the demands on the main panel. After those demand are met (if) the power is fed to the utility. The only time the inverter cannot direct surplus power back to the main panel in this scenario is when there is a loss of grid power. This is a purposeful feature of hybrid inverters to prevent harming line workers.
You can self-consume all your pv power - except during a grid outage at which point you can only consume power for your critical loads.Comment
-
Some hybrid inverters support the loads all the time, and then direct the surplus toward the "grid". If the inverter is in a branch circuit from your main panel, then the "grid" includes the main panel and the surplus power is available to the demands on the main panel. After those demand are met (if) the power is fed to the utility. The only time the inverter cannot direct surplus power back to the main panel in this scenario is when there is a loss of grid power. This is a purposeful feature of hybrid inverters to prevent harming line workers.
You can self-consume all your pv power - except during a grid outage at which point you can only consume power for your critical loads.
This is an automatic function, unlike the manual switching the OP is proposing to use.SunnyBoy 3000 US, 18 BP Solar 175B panels.Comment
-
seems fairly naive. Although his goals seem lofty, to just wait it out is what most the population will do, till it doesn't come back for a day, a week, 2 weeks...... Been in two situations with no power, once for two weeks during an ice storm and a week after sandy. Better prepared than notComment
-
I really really appreciate the comments and I'm sorry I have been muddy on my thoughts. I don't want to have everything backed up at all times. When my 13 kW system is bathed in sunshine and the grid is down I would like to have the option to use that power to run any of my normal needs. If my battery bank is full and it's daylight so I'm not running any lights it would be great to run my attic fan or my dishwasher or my laundry or my power saw.
What I seem to be reading here is I will only be allowed by my electrical inspector to have a critical load panel that can be supported just by my batteries regardless if I have 10kw coming out of my modules. So due to not wanting a gazillion batteries I'll just have to let a lot of electricity go to waste on a sunny day if the grid is down.
Is that right?
Geez.Comment
-
seems fairly naive. Although his goals seem lofty, to just wait it out is what most the population will do, till it doesn't come back for a day, a week, 2 weeks...... Been in two situations with no power, once for two weeks during an ice storm and a week after sandy. Better prepared than not
I was only giving him a little guff because I've lived about 30 miles from his location most of the past 50 years and can't remember ever having the power out for more than a few hours once every 5 or 10 years or so. We have different pocos but live in almost identical climatic conditions except the wind here in Boulder county is probably a lot worse. Maybe kingofbanff's poco situation is bad though (I'd be surprised), or maybe he's just got cash burning a hole in his pocket. Doing what he's doing just seems extreme to me. I know of no one else around here who's worried about it. I was only suggesting that he reconsider how important it really is before charging down the path...Comment