Not a big thing, but some assume that the charger is doing the current limiting once reaching absorb.
What I would like to do is to find some good way to take the power not being used by the controller for battery charging, once the charger reaches it's absorption phase, and send this energy to a grid tied inverter.
AGM's, in reality, need to FINISH absorb, and get this - need to float at 13.6 - 13.8 for at least 8 hours to actually finish the job - otherwise you are walking them down in capacity. That little .1% that doesn't get recharged each cycle, eventually hard-sulfates, and just keeps on growing each and every cycle is part of the reason that agm's are widely murdered before their time. Continuous floating after that initial 8-12 hours is "maintenance", but that crucial first few hours after absorb are very hard to come by with solar. Sometimes just getting *to* absorb is a chore!
What is the absorb end-current for most for agm's? About 0.05C end current canonically - or no change in current for an hour or more due to age / drying out, etc. For you that would be about 14A with a battery capacity of 280Ah.
What I'm trying to say is that with your agm's, what you might view as inconsequential panel current at the end of absorb, or going into float is not wasted! Far from it - that is only extending the life of an agm that really truly needs to be fully charged as often as possible.