I have 10 panels to fit & would like to fit in 2 lots of 5 in series or should this be fitted as one series of 10. I like the 5 idea for any future fault finding, but not sure.
The inverter is a Growatt 6kw / 500v input & needs 150v to kick in.
So, if my understanding is correct ??? 40.25voc x 5 = 201.25v, or 40.25voc x 10 = 402.5v Am i ok either way? or do i need to add to the equation, like cold weather & anything else? Plus, would i be pushing the inverter at 6x2 or 12 = 241.5vx2 & 483v
Panel spec below.
Thanks for your help.