Try our solar cost and savings calculator
Apsystems DS3-L Tripping due to Grid Frequency
Collapse
X
-
-
If the inverter is producing power before and after the time-out, its unlikely its defective. If it were, it would just die. If 6-7 are showing the same thing, its likely its a grid profile mismatch or a grid issue. i would research more into it and maybe write in to the grid provider submitting the grid profile to them and asking them if it is correct.Comment
-
They only respond to queries from registered installers as priority.
DIY are not on their priority unfortunately simply because the support required is not cost effective and time consuming. They normally make installers buy large amounts of inverters so they can make them replace inverters under warranty and take all the hassle out of the consumers' hands. If 10,000 people wanted to install themselves and didnt know what they were doing, imagine the complaints they would receive and the negativity on reviews et al.
From what ive read in these forums, they do respond to DIY installers but on a much longer timeline.
Comment
-
When your voltage starts to exceed 254.4 VAC power start to ramp down and power goes to zero at 264 VAC. You only have access to data in 1 minute increments. Alot can happen in one minute. Your data shows quite a few inverters running in the 254/5 range, but none in the 260 range.
Thanks, so this would be expected behavior? Something happens 1-2 shut off and go to 0W and then 5 minutes later they are back on.
Here are the Rule 21 settings from APSystems
Screen Shot 2023-02-01 at 6.57.14 PM.pngScreen Shot 2023-02-01 at 6.57.27 PM.pngScreen Shot 2023-02-01 at 6.57.36 PM.png
Also, I would order the data in a physically not logically. In other words, closes inverter to Grid = #1, then next closes, ... and finally #ZZ is the farthest away. Theoretically the inverter farthest away should shut down first, but that's theory. Just a thought.Comment
-
Looks that way. If you check the grid profile you should see something like "start" or "reconnect" time set to 300s.
If you want, you could verify by changing the grid profile to disable volt-watt curtailment then the shut off should stop. However, the high voltage could be a sign that your PV branch wiring is too long/thin or your street transformer is not working properly.
Comment
-
It does sound like a problem with the inverters seeing too much voltage
into the grid. That happened here, not easy to fix.
Causes can be a combination of nominal line voltage being quite high
(as the PoCo tends to do), and additional voltage built up in the wiring
between your inverters and the grid.
Here I requested the PoCo bring down the voltage more to the legal
limit of 120/240 (was running 127/254), which helped but took a while.
But measurements revealed that the power lost in my 600 foot wiring
loop was some 9V at 60A, or 540W. Eventually I replaced all the wire
in that loop with rather oversized, to bring voltage loss to about 2V, or
120W loss. No more problems and better efficiency, even if the line
goes up again. Aluminum wire minimized the upgrade cost. Bruce RoeComment
-
The fastest reading is still the ECU. Installer accounts do not have faster readings. The service mode on the ECU will give the quickest updates of around 20-30s per update depending on the zigbee communication and non-service mode is every 8 mins to view but every 5 mins inverter updates.
It could be one of the inverters either has a different grid profile or is faulty. I recommend emailing APS.
PS only real difference between installer and non-installer is the ability to log data and having data like DC voltages and currents from each panel. Everything else is more or less the same.
Personally i prefer to use the ECU direct.
Screenshot 2023-02-02 at 10.39.51 AM.png
davidcheok how do i go about getting to the inverter data by itself my login does not show inverter data any help.
Screenshot 2023-06-29 163939.png
Comment
-
Only installers have inverter data. its a different account type. You should contact your installer.
davidcheok how do i go about getting to the inverter data by itself my login does not show inverter data any help.
Screenshot 2023-06-29 163939.pngComment
-
Testing if it is related to rule 21 is easy enough by temporarily turning that off.
But even if it is, if only two micro inverters are tripping because of it, they are likely defective (hardware or software), because all of them see the same grid and so they should all react to grid 21 or frequency limits in the same way.Comment
-
If this issue isn't fixed, you might try following the firmware update procedure in the manual. We had a similar trip-out mechanism with our new DS3-L's last year, and it had nothing to do with the grid. It was a firmware issue, and was corrected when the units updated by following the procedure.Comment