    Mixing panels

    What would be the best config for 2 X 265W and 2 X 270W (12V each)? 270's in series in parallel with the 265's in series OR 2 X 265+270 (S) in (P)? I know mixing power make you loose efficiency, but I own the 2 265 and someone offered me to give me the 270's. I'm using a 24V system (MPPT). What gauge of cable should I use for 80' of cable with this config? Thanks!
  • SunEagle
    Super Moderator
    • Oct 2012
    • 15125

    #2
    Check the Vmp and Imp of those panels. If they are within 5% of each other then you should be able to treat them as the same. How you wire them will be determined by the CC max input rating which is where you have to consider the Voc ratings. To high and your CC may burn up.

    The cable size is determine by the amount of amps they are carrying along with a voltage drop calculation. Until you provide more info on the panel specs and orientation then it would be difficult in providing a cable size for your system.

    Comment

    • bcroe
      Solar Fanatic
      • Jan 2012
      • 5199

      #3
      If the panels are as good a match as the ratings indicate, the arrangement
      will not be critical.

      You have 270W 12V panels, so with an MPPT of around 15V the current
      would be 18A, right? At 80 feet and a round trip loop length of near 180 ft,
      your most efficient arrangement is 4 panels in series. But that might present
      100V to your controller, check actual rating and temp range to avoid blowing
      it. With 60V from series panels at 18A , 2% loss would be 1.2V.
      Loop resistance needs to be limited to E/I or 1.2/18 equals 0.067 ohms, or
      0.00037 ohms per foot. That puts you around 6 gauge. Using a series-
      parallel panel arrangement gives twice the current at half the voltage, you
      would need 4 times as much copper to get the same efficiency. Bruce Roe

      Comment

      • littleharbor2
        Solar Fanatic
        • Jan 2016
        • 191

        #4
        Originally posted by Jambonjoebob
        What would be the best config for 2 X 265W and 2 X 270W (12V each)? 270's in series in parallel with the 265's in series OR 2 X 265+270 (S) in (P)? I know mixing power make you loose efficiency, but I own the 2 265 and someone offered me to give me the 270's. I'm using a 24V system (MPPT). What gauge of cable should I use for 80' of cable with this config? Thanks!
        I'm quite curious what panels you have that are 12 volts and that high od wattage. The only thing I have heard of similar to those are some dinosaurs made by Mobil Oil Co,