    Adding Solar to a -48VDC/Positive Ground/Telecom System?

    I previously worked in the telecom industry and I have a -48VDC (positive ground) battery back up system I built from surplus telecom equipment. I have about 40kwh of AGM batteries, a pair of old Xantrex XDI 2048 1.5kW rack mount inverters, and an undersized line powered charger that charges at around 3A. I mostly use this system for emergency backup power to run lights and furnace during weather problems.

    What I'd like to do is add solar power to my set up but from what I have researched positive ground doesn't seem to be very common with solar set ups, I'm mostly seeing negative ground or floating battery systems. I reached out to Morningstar and they gave me a link to their white paper on positive ground systems, so I know I have at least one decent option for charge controllers, but I'm open to other suggestions.

    I'm totally new to any sort of solar installation, so my biggest question is how can I tell which panels I can use with a positive ground system? Am I better off just redoing my existing setup and getting rid of my line power charger and inverters and switching to negative ground?

    Thanks in advance for any help.
  • bcroe
    Solar Fanatic
    • Jan 2012
    • 5213

    #2
    In more recent times, there is more telecom equipment with power circuitry
    isolated from ground. I would at least look at, if your equipment could operate
    with a negative ground. Bruce Roe

    Comment

    • Mike90250
      Moderator
      • May 2009
      • 16020

      #3
      Positive ground is used in comm centers because leakage currents don't erode the signal lines as much ( super short simple version ) So maybe your gear will work floating or - gnd.
      Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
      || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
      || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

      solar: http://tinyurl.com/LMR-Solar
      gen: http://tinyurl.com/LMR-Lister

      Comment

      • sdold
        Moderator
        • Jun 2014
        • 1470

        #4
        We're soon going to be trying a few Morningstar Tristar 60A controllers on some radio sites with -48V for the microwave, I think I saw the same white paper you did and their tech support confirmed that positive ground was no problem. I like that I can call them on the phone for easy tech support, unlike another company I won't name whose employees always seem to be "out back" and not answering the phone.

        Comment

        • Swervin
          Junior Member
          • Oct 2021
          • 3

          #5
          Originally posted by sdold
          We're soon going to be trying a few Morningstar Tristar 60A controllers on some radio sites with -48V for the microwave, I think I saw the same white paper you did and their tech support confirmed that positive ground was no problem. I like that I can call them on the phone for easy tech support, unlike another company I won't name whose employees always seem to be "out back" and not answering the phone.
          If you don't mind me asking, what solar panels are you planning on using? I emailed a few companies and was basically told they wouldn't confirm that their panels would work with positive ground. Makes me nervous when I can't get any assurance from a manufacturer about their products.

          Comment

          • sdold
            Moderator
            • Jun 2014
            • 1470

            #6
            LG LG410n2w, it's a 410 watt grid tie panel. They claim it's not a problem although we haven't actually tried one yet I also talked a bit about this with some tech support folks at Morningstar who have only heard of older Sunpowers having "some" problem with polarity, but it's best to check for yourself.

            Comment

            • Swervin
              Junior Member
              • Oct 2021
              • 3

              #7
              Originally posted by sdold
              LG LG410n2w, it's a 410 watt grid tie panel. They claim it's not a problem although we haven't actually tried one yet I also talked a bit about this with some tech support folks at Morningstar who have only heard of older Sunpowers having "some" problem with polarity, but it's best to check for yourself.
              Thanks for the information, much appreciated. I was really surprised there weren't more off the shelf equipment packages aimed at telecom setups, considering all the remote equipment.