    High voltage inverters

    Hi all

    sadly I can only have my panels a fair distance from my house +/- 400ft. So I need to do high voltage DC

    I found the Fronius Primo which allows for +/-600 VDC And they look like great inverters

    But what other inverters are there that can operate at 600VDC - 1000VDC ?

    thanks in advance
  • Mike90250
    Moderator
    • May 2009
    • 16020

    #2
    Is your house off-grid or on-grid ? Off-grid battery systems are generally 48V max, because of the HV DC hazard.

    Battery based systems have several options for a 600V MPPT battery charger (Morningstar, Schneider and Midnight )

    Grid tie systems regularly use 300 - 600V inverters, up to 10,000 watts, often with 2 strings into 2 independent MPPT channels.
    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister

    Comment

    • bcroe
      Solar Fanatic
      • Jan 2012
      • 5198

      #3
      Originally posted by TheBearF8
      Hi all
      sadly I can only have my panels a fair distance from my house +/- 400ft. So I need to do high voltage DC

      I found the Fronius Primo which allows for +/-600 VDC And they look like great inverters

      But what other inverters are there that can operate at 600VDC - 1000VDC ?
      I have 400VDC panel strings up to 700ft from the house, with AC & DC losses in the 1%
      range. There is some direct burial aluminum cable keeping losses down, cost no more
      than several panels. Bruce Roe

      Comment

      • nwdiver
        Solar Fanatic
        • Mar 2019
        • 422

        #4
        Originally posted by TheBearF8
        Hi all

        sadly I can only have my panels a fair distance from my house +/- 400ft. So I need to do high voltage DC

        I found the Fronius Primo which allows for +/-600 VDC And they look like great inverters

        But what other inverters are there that can operate at 600VDC - 1000VDC ?

        thanks in advance
        ~400' is nothing. I would use a SMA inverter, they're a bit more cost effective than Fronius unless you like the ability to see DC Voltage and current remotely. All 240v inverters have the same max operating DC voltage ~480v. Just run each string on an independent 10 or 8 AWG circuit. The line losses @ 8A would be < 2%... and if you oversize the array they're 'free' when the inverter is saturated, which is exactly when line losses would normally be highest. With panels as cheap as they are it may be more cost effective to add more watts than upsize the conductors from #10 to #8.

        Comment

        • TheBearF8
          Junior Member
          • Oct 2017
          • 7

          #5
          Originally posted by bcroe

          I have 400VDC panel strings up to 700ft from the house, with AC & DC losses in the 1%
          range. There is some direct burial aluminum cable keeping losses down, cost no more
          than several panels. Bruce Roe
          bcroe Thanks for the feedback, I'm interested to know more of the details, like what wire size and inverters you used, esp.

          Comment

          • TheBearF8
            Junior Member
            • Oct 2017
            • 7

            #6
            Originally posted by nwdiver

            ~400' is nothing. I would use a SMA inverter, they're a bit more cost effective than Fronius unless you like the ability to see DC Voltage and current remotely. All 240v inverters have the same max operating DC voltage ~480v. Just run each string on an independent 10 or 8 AWG circuit. The line losses @ 8A would be < 2%... and if you oversize the array they're 'free' when the inverter is saturated, which is exactly when line losses would normally be highest. With panels as cheap as they are it may be more cost effective to add more watts than upsize the conductors from #10 to #8.
            nwdiver Thanks for the feedback. Most wire sizing charts/calculators I have run across all mention 2 or 4 AWG for voltages around 480V. Thus I had to look at 600VDC+ to cater for the run length and remain within the 6 AWG range which is what I found is the max wire size specd on most of inverters I looked at. Could you please explain how you managed to use 8 or 10 AWG

            Thanks

            Comment

            • nwdiver
              Solar Fanatic
              • Mar 2019
              • 422

              #7
              Originally posted by TheBearF8

              nwdiver Thanks for the feedback. Most wire sizing charts/calculators I have run across all mention 2 or 4 AWG for voltages around 480V. Thus I had to look at 600VDC+ to cater for the run length and remain within the 6 AWG range which is what I found is the max wire size specd on most of inverters I looked at. Could you please explain how you managed to use 8 or 10 AWG

              Thanks
              Wire size has absolutely nothing to do with voltage as long as your wire is properly rated and THHN wire is rate to 600v. It's all about current. #10 is 'rated' for 30A but de-rating can reduce that to <15A. ~10A is fine.

              Most inverters either have independent MPP channels or terminals for up to 6 strings. Instead of investing in a combiner box and fuses it's more cost effective to just run a separate circuit for each string. If you have 3 strings then run 6 #10s.

              Comment

              • bcroe
                Solar Fanatic
                • Jan 2012
                • 5198

                #8
                Originally posted by TheBearF8
                . bcroe Thanks for the feedback, I'm interested to know more
                of the details, like what wire size and inverters you used, esp.
                Charts may cater to the most common situations, but will not cover the optimum
                solution for every situation. Most wire will handle 600V, it is not hard to find the
                resistance of a loop and calculate losses. My pair of 7.5KW inverters deliver about
                60A at 250VAC to the PoCo net metering. The installation originally used the existing
                600 foot loop of 4 gauge wire, which at 0.00025 ohm per foot, came to 0.150 ohms.
                60A through 0.15 ohm gives a 9VAC drop, or around 3.6%. I considered installing
                a 2/0 copper wire loop, which would have cost $2600. Instead I get the same
                performance by going to 4/0 aluminum wire, which cost only $650. The triplex
                direct burial wire included a 2/0 aluminum neutral, which does not effect efficiency
                since inverter current flows in the 240VAC wires.

                This reduced losses to less than 1/3 the previous. If you are running less than 15KW,
                you can easily do even better. My boxes at each end needed to be able to terminate
                the big aluminum wire, any house service 200A box can do that.

                The DC runs are mostly individual strings capable of 8A through 10 ga PV wire, up
                to a 400 foot loop. There the combiner box brings them into two 6 gauge loops, each
                near 500 feet to the pair of inverters. Losses vary, but can exceed 1 %.

                Feeds can be combined at the array or at the inverters. Combining them at the array
                gives the option of easily using as large wire as needed (or smaller if not), instead of
                continuing with PV wire to the inverter(s). Another thing, if your panels do not receive
                identical sun at all times (like shading), a combiner feed will gain some efficiency at
                reduced current. Individual feeds not shaded will remain just as lossy at full current
                while the next one carries no current.

                600V is a safety limit generally used in consumer situations. Since panel voltages
                are much higher in severe cold, and will hit open circuit voltage near 25% more
                than MPPT operation, working backwards from the limit and not risking blowing up
                my 7 year old FRONIUS inverters, panel MPPT operation comes to about 420VDC
                at 20F below zero, about 340VDC in hottest summer. Bruce Roe
                Last edited by bcroe; 10-13-2020, 10:43 PM.