Try our solar cost and savings calculator
Siemens QO breakers DC rating?
Collapse
X
-
Breakers make a handy switch for when you need to reboot the charge controller, but in real world, your 8A panels can't trip a 10A breaker, except for a Edge of Cloud lensing event. -
In my own situation I have 4 strings that run about 8.5A max so I used 10A breakers.Dead serious, I am a professional electrical engineer with 40 years of experience. A solar panel is a Current Source, not a voltage source. With one or two strings of panels, makes it impossible for a solar panel system to operate a fuse. A 250 watt panel with a dead bolt fault will only deliver roughly 8 to 10-amps of current. 8 to 10 amps of current on a 15 or 20 amps breaker or fuse is a normal load current and will never operate a fuse.That is why electrical codes do not require a fuse on solar panels unless you cross the line with 3 or more strings.
Look at any panel specification and look for the spec Isc and learn what it means. Isc = Current Short Circuit. A 200 watt panel Isc = roughly 8 to 10 amps. That is the absolute maximum current that panel can deliver with its output shorted out (two output wires twisted together tightly.) Please explain how 8 to 10 amps is going to operate a 15 or 20 amp fuse or breaker.
You can certainly use OCPD on the panels if you wish, but they are not required and an unnecessary expense.
Last edited by PNW_Steve; 11-12-2020, 11:58 PM.Leave a comment:
-
Dead serious, I am a professional electrical engineer with 40 years of experience. A solar panel is a Current Source, not a voltage source. With one or two strings of panels, makes it impossible for a solar panel system to operate a fuse. A 250 watt panel with a dead bolt fault will only deliver roughly 8 to 10-amps of current. 8 to 10 amps of current on a 15 or 20 amps breaker or fuse is a normal load current and will never operate a fuse.That is why electrical codes do not require a fuse on solar panels unless you cross the line with 3 or more strings.
Look at any panel specification and look for the spec Isc and learn what it means. Isc = Current Short Circuit. A 200 watt panel Isc = roughly 8 to 10 amps. That is the absolute maximum current that panel can deliver with its output shorted out (two output wires twisted together tightly.) Please explain how 8 to 10 amps is going to operate a 15 or 20 amp fuse or breaker.
You can certainly use OCPD on the panels if you wish, but they are not required and an unnecessary expense.Last edited by Sunking; 10-13-2020, 11:56 AM.Leave a comment:
-
I can't tell if you are joking or serious........
Apparently there are few to none when it comes "right designs". We use overcurrent protection on every circuit.Leave a comment:
-
Breakers are handy as a switch, for combiners to compare string performance as a quick sanity check. Also useful as a switch to disconnect PV from charge controller
Most fuse/holder combos are NOT rated for circuit interruption (meaning the contacts will fry if you pull a fuse while circuit is live) (only for the fuse to blow and interrupt)
And it's good practice to protect the cable from the battery to charge controller, in the odd chance the controller fails.
While sizing strings and only using 2 parallel PV strings, protection is not required, it's handyLeave a comment:
-
Why do you think you need breakers? You do know with the right design, no breakers or fuses are needed. Guess you want to spend the cash huh?Leave a comment:
-
My apologies, I somehow turned "Schneider" into "Siemens"
The breakers that I am looking for are actually Schneider.
Stuck on stupid......
Leave a comment:
-
I'm surprised/, Did you try calling them? I've bought them there many times
You an also try https://www.solar-electric.com/marin...akers.html?p=2
Andy
Leave a comment:
-
Doesn't look like they have them.
Thanks for trying.Leave a comment:
-
Leave a comment:
-
I don't know about the Siemens-QO
CARLING breakers rated for 150VDC
Carling may make a Load Center version , these are bolt on.
The C-Series hydraulic/magnetic circuit breakers are
ideal for applications that require higher amperage and
voltage handling capability in a smaller package. They are
available in 1-6 poles, 0.02-100amps, UL Recognized up to
480VAC or 150VDC, UL489 Listed up to 240VAC or 125VDC,
with choice of time delays, terminal options, actuator
styles and colors.
Carling Technologies, Inc.
60 Johnson Avenue • Plainville, CT 06062-1177
Phone: (860) 793-9281 • Fax: (860) 793-9231
Email: sales@carlingtech.com • www.carlingtech.com
Leave a comment:
-
Thanks.here - the 150VDC rated from Midnight, not sure who makes them.
http://www.midnitesolar.com/productP...Order=13&act=p
Any clue where I can find the breakers I am looking for?Leave a comment:
-
here - the 150VDC rated from Midnight, not sure who makes them.
Leave a comment:
-
According to the Schneider website they make breakers rated for both 48v and 125v. I have not had luck so far finding the 125v rated breakers. The 48v won't work for me as my Voc is going to be around 80v.I thought that QO was the Schneider SquareD breaker tradename. SquareD QO are only rated for 48VDC.
Schneider Electric USA. Browse our products and documents for Square D™ QO™ and QOB Miniature Circuit Breakers - QO and QOB miniature circuit breakers for QO systems
The important thing to remember is that interrupting DC is much more demanding than interrupting AC. That's why these 240V AC breakers are only rated for 48V DC.
The Midnight Solar breakers are rated for 150VDC. Sounds like you need them.Leave a comment:
-
I thought that QO was the Schneider SquareD breaker tradename. SquareD QO are only rated for 48VDC.
Schneider Electric USA. Browse our products and documents for Square D™ QO™ and QOB Miniature Circuit Breakers - QO and QOB miniature circuit breakers for QO systems
The important thing to remember is that interrupting DC is much more demanding than interrupting AC. That's why these 240V AC breakers are only rated for 48V DC.
The Midnight Solar breakers are rated for 150VDC. Sounds like you need them.Leave a comment:
Copyright © 2014 SolarReviews All rights reserved.
Powered by vBulletin® Version 6.1.3
Copyright © 2026 MH Sub I, LLC dba vBulletin. All rights reserved.
Copyright © 2026 MH Sub I, LLC dba vBulletin. All rights reserved.
All times are GMT-5. This page was generated at 07:02 AM.
Leave a comment: