I've always assumed that, since generally the panels themselves are where most of your money is going, that you would choose an inverter that is guaranteed to be able to handle the maximum DC power the panels can deliver.
However, looking at the "advanced" option in PVWatts, there is this confusing language describing the "DC to AC size ratio":
The DC to AC size ratio is the ratio of the inverter's AC rated size to the array's DC rated size. Increasing the ratio increases the system's output over the year, but also increases the array's cost. The default value is 1.20, which means that a 4 kW system size would be for an array with a 4 DC kW nameplate size at standard test conditions (STC) and an inverter with a 4 DC kW / 1.2 = 3.33 AC kW nameplate size.
For a system with a high DC to AC size ratio, during times when the array's DC power output exceeds the inverter's rated DC input size, the inverter limits the array's power output by increasing the DC operating voltage, which moves the array's operating point down its current-voltage (I-V) curve. PVWatts® models this effect by limiting the inverter's power output to its rated AC size.
Confusing, because in the first sentence it appears they're talking about AC-to-DC ratio, but they call the input DC-to-AC ratio ("X-to-Y ratio" means X/Y, not Y/X); the then in the example, it again appears they're talking DC-to-AC ratio.
Anyhow, if you figure you have the space and money to install a certain number of watts of panels, WHY would you choose an inverter which might clip the output of those panels under maximum power output conditions ? Why would you choose a DC-to-AC ratio greater than 1 ?
The language suggests cost of the inverter is the reason. In my situation, I'm going to install 4860 watts of panels, and use an SMA SunnyBoy inverter. PVWatts seems to suggest I'd want to choose their 3.8kw model, but my inclination would be to choose the 5.0kw model. The price difference is a whopping $70 (out of about $1000). Plus the larger one gives me 3 MPPTs, which might be nice for my 18 panels.
Am I missing something, is there some other downside in choosing the 5.0kw unit ?
However, looking at the "advanced" option in PVWatts, there is this confusing language describing the "DC to AC size ratio":
The DC to AC size ratio is the ratio of the inverter's AC rated size to the array's DC rated size. Increasing the ratio increases the system's output over the year, but also increases the array's cost. The default value is 1.20, which means that a 4 kW system size would be for an array with a 4 DC kW nameplate size at standard test conditions (STC) and an inverter with a 4 DC kW / 1.2 = 3.33 AC kW nameplate size.
For a system with a high DC to AC size ratio, during times when the array's DC power output exceeds the inverter's rated DC input size, the inverter limits the array's power output by increasing the DC operating voltage, which moves the array's operating point down its current-voltage (I-V) curve. PVWatts® models this effect by limiting the inverter's power output to its rated AC size.
Confusing, because in the first sentence it appears they're talking about AC-to-DC ratio, but they call the input DC-to-AC ratio ("X-to-Y ratio" means X/Y, not Y/X); the then in the example, it again appears they're talking DC-to-AC ratio.
Anyhow, if you figure you have the space and money to install a certain number of watts of panels, WHY would you choose an inverter which might clip the output of those panels under maximum power output conditions ? Why would you choose a DC-to-AC ratio greater than 1 ?
The language suggests cost of the inverter is the reason. In my situation, I'm going to install 4860 watts of panels, and use an SMA SunnyBoy inverter. PVWatts seems to suggest I'd want to choose their 3.8kw model, but my inclination would be to choose the 5.0kw model. The price difference is a whopping $70 (out of about $1000). Plus the larger one gives me 3 MPPTs, which might be nice for my 18 panels.
Am I missing something, is there some other downside in choosing the 5.0kw unit ?