Hi guys. Drama brings me here to inquire about wiring my panels into 3 strings on a SE11400A inverter. But first a little backstory.
So my contractor outsourced the installation of my system who installed 36 Hanwha 295w panels in two strings. 18 on string 1 and 18 on string 2. This apparently exceeds the max watts per string the inverter can handle and of course we find out after the company has replaced the inverter now for a third time and currently waiting for the company to come and "re-string" the panels to all three strings.
So my question is this. Would it be possible to "re-string" my panels with 14-string1/14-string2/8-string3? I ask because I've seen a spec sheet on other Solaredge inverters that state there should not be more that a 1kw difference between strings. I simply want to leave the third string open to add more panels down the road without having to restring everything again.
So my contractor outsourced the installation of my system who installed 36 Hanwha 295w panels in two strings. 18 on string 1 and 18 on string 2. This apparently exceeds the max watts per string the inverter can handle and of course we find out after the company has replaced the inverter now for a third time and currently waiting for the company to come and "re-string" the panels to all three strings.
So my question is this. Would it be possible to "re-string" my panels with 14-string1/14-string2/8-string3? I ask because I've seen a spec sheet on other Solaredge inverters that state there should not be more that a 1kw difference between strings. I simply want to leave the third string open to add more panels down the road without having to restring everything again.