  • PNPmacnab
    replied
    Originally posted by bcroe

    Once again Nyle announced the e8 water heating heat pump adapter,
    might soon be available. It is still in the process of being Energy Star
    certified, UEF tested, UL tested, and other things. If I ever get one,
    the energy reserve might be exhausted, better than giving it away.

    IMGP2436.jpg
    A friend of mine just got a e8 end of May and finally got around to installing it. He is quite impressed. He got build #4, just after the ones sent off for regulatory testing. So, I guess that is still experimental as it has no certification. Surprised it is a 120V unit with the market being primarily commercial. He uses it in singe pass full temperature output.

    Leave a comment:


  • bcroe
    replied
    Originally posted by DanS26
    Bruce, I use silver conductive grease on every connection and a torque screwdriver or wrench. Not to be confused with dielectric grease. It’s expensive but we’ll worth it IMO. Use very sparingly as excess will short a circuit. If + and - are near each other.
    Never had a connection failure in my system.
    I am again bringing the main PV wiring into a more regular review,
    even using a temp gauge to check for a box heating up after a
    few hours at max power. I will be using some kind of terminal
    protection on everything now. And spare shutdown assemblies
    are prepared and sealed, just in case. The post mortum hints to
    me, the issue has been the aluminum terminal block that came
    bolted to the DC shutdown switch assembly. I am replacing all
    of these with copper terminal blocks + anti corrosion stuff.

    This year the big solar item is the smoke. Usually not so common
    here in nothern IL. Even smoke not looking so thick, has a big
    impact on solar energy. I am used to seeing the 15KW system
    peaked out for nearly 8 hours a day many times. But recently it
    has trouble getting up to the full 15KW capacity. Even when the
    sky is not cloudy, production might be down 20% or more. Still
    the array is fighting it, energy reserve is about 7.8MWh vs 8MWh
    best at this date.

    Then there is air quality, worst numbers I have ever seen. But
    smoke containts physical particulate, which my electronic air filter
    can remove no matter how small. The furnace blower operates it
    around 20 minutes every hour. This really works, even before the
    smoke, I could see that the dust particles in a beam of sun were
    way down. The overall PV system produces enough energy to
    allow this luxury (?) at no extra cost beyond cleaning the filter.
    The blower motor (a standardized direct drive) was recently
    replaced as the original was about to fail. All motor wires were
    the same, though I did need to touch up the impeller balance.

    Bruce Roe

    Leave a comment:


  • DanS26
    replied
    Bruce, I use silver conductive grease on every connection and a torque screwdriver or wrench. Not to be confused with dielectric grease. It’s expensive but we’ll worth it IMO. Use very sparingly as excess will short a circuit. If + and - are near each other.

    Never had a connection failure in my system.

    Leave a comment:


  • Mike 134
    replied
    Originally posted by bcroe
    After a decade the 15KW system here has again developed
    wiring problems. The twin 7.5KW inverters normally are a
    match to around 1%, but lately EAST was lagging some. A
    quick check with the clamp on DC ammeter indicated all
    strings were close to a match. More checking, after half a
    day running full power (that is up to 8 hours with this
    configuration) the EAST DC disconnect box was getting pretty
    warm.

    As usual I set up a night work light and waited for the darkness.
    Inside the Square D 361 box a 6 gauge wire looked like it
    was cooking its insulation. The 361 is rated 30A against
    the 22 I run, and 600VDC against my 400, 3 contact positions.
    Something about the plus array wire was making poor contact
    and getting ready to burn out. It was not my wire clamp screw.

    I had this same failure on another contact years ago, I had
    just moved the wires to the spare position. Something was
    not making good contact, not sure if it was the bolts holding
    metal together, or the switch contact. Is there a contact lube
    that should be used on these?

    Fortunately I have a lot of spare parts, and these boxes are
    designed so a few screws from the open door side allow
    replacing whole units. I found a nice switch section, made
    sure all its screws were pretty tight, and soon had it installed.
    Hand test today indicated proper cool operation.

    There are plenty of the 361 outdoor boxes on Evil Bay, some
    with 600V fuses (that I do not need), and some with just a
    switch. Bruce Roe PVburnedDC.jpg
    Is that brownish color light rust on the rivets? Perhaps some condensation over the past 10 years leading to the poor connection.

    Leave a comment:


  • bcroe
    replied
    After a decade the 15KW system here has again developed
    wiring problems. The twin 7.5KW inverters normally are a
    match to around 1%, but lately EAST was lagging some. A
    quick check with the clamp on DC ammeter indicated all
    strings were close to a match. More checking, after half a
    day running full power (that is up to 8 hours with this
    configuration) the EAST DC disconnect box was getting pretty
    warm.

    As usual I set up a night work light and waited for the darkness.
    Inside the Square D 361 box a 6 gauge wire looked like it
    was cooking its insulation. The 361 is rated 30A against
    the 22 I run, and 600VDC against my 400, 3 contact positions.
    Something about the plus array wire was making poor contact
    and getting ready to burn out. It was not my wire clamp screw.

    I had this same failure on another contact years ago, I had
    just moved the wires to the spare position. Something was
    not making good contact, not sure if it was the bolts holding
    metal together, or the switch contact. Is there a contact lube
    that should be used on these?

    Fortunately I have a lot of spare parts, and these boxes are
    designed so a few screws from the open door side allow
    replacing whole units. I found a nice switch section, made
    sure all its screws were pretty tight, and soon had it installed.
    Hand test today indicated proper cool operation.

    There are plenty of the 361 outdoor boxes on Evil Bay, some
    with 600V fuses (that I do not need), and some with just a
    switch. Bruce Roe PVburnedDC.jpg

    Leave a comment:


  • bcroe
    replied
    Here I am again, smoke from wild fires in the NW is sending haze over
    the IL area again. While not terribly severe, it is enough to cause the
    inverters to drop out of clipping (about 7600W each), to more like 7300
    or 7400W. Bruce Roe

    Leave a comment:


  • DanS26
    replied
    I recently added an antenna to my mid-1800's barn with a very slick metal roof.........

    IMG-0756.jpg

    Leave a comment:


  • bcroe
    replied
    The pair of Fronius IG 7.5 are just doing their thing after 10 years.
    The new-out-of-the-box spare is mounted next to them, just need
    to move 2 wires and throw a breaker if backup is needed. Guess
    it might be a good idea to actually try that some day, might take
    commissioning to get it going. No more worries about high line
    voltage programming since the heavy feed was installed in 2020.

    Looking good so far this year, the 15KW inverter plant delivered
    150KWh today. The previous year was rather poor sun, generation
    was a bit under 28,000 KWh. I got to keep more of that, the 2020
    heavy feed is delivering close to an extra 1000KWh of generation
    to the meter for credit. I made it past 1 April reset with a 1700 KWh
    in the black surplus (given to the PoCo). Most stuff here just ran,
    one of the 6 heat pumps needs attention.

    Some energy ideas, new mounts could boost output and reduce snow
    accumulation. And more house insulation, windows and in attic.
    Observation of loads is ongoing, but Energy Star and some mods
    have brought efficiency to a high level. Design a clipping level monitor.

    However most attention today is catch up on stuff ignored for the
    first PV decade. Need to get a new antenna up before the old one
    falls down, still considering J.P.M.s advice how to (not) do that on
    the steel roof. Some really big chunks of snow slid down this winter,
    I am building some clamp on slide restrictors using the same 6061
    aluminum and 18-8 SS bolts that have worked so well holding panels.
    Bruce Roe

    Leave a comment:


  • DanS26
    replied
    hey Bruce...just wondering how those 7.5 Fronius inverters are holding up?

    I wake up every morning and think I'm glad to see another day. My eleven year old Fronius transformer inverters must think the same thing........well maybe if they were AI.

    Leave a comment:


  • bcroe
    replied
    Originally posted by bcroe
    So another year, Nyle periodically says the unit will
    be available, but once again failed to deliver it. Bruce Roe
    Once again Nyle announced the e8 water heating heat pump adapter,
    might soon be available. It is still in the process of being Energy Star
    certified, UEF tested, UL tested, and other things. If I ever get one,
    the energy reserve might be exhausted, better than giving it away.

    Although this property was purchased with an eye to eliminating the
    building maintenance (painting, etc), there was one standard roof on
    the house. The shingles, facia, and rain gutters got replaced in 2021,
    but now it was so slippery I could hardly go up there. As discussed
    earlier, clamps to attach are quite expensive, $5 and up each. After
    a bit of experimentation, I came up with this DIY version, using the
    same 6061 aluminum and 18-8 hardware as the ground mounts. I
    put some special conductive tape over the roof ridge first, to avoid
    scratching the paint too much.

    This is not normally under much stress, it just gives me a handhold
    and a place to connect a safety strap. Note the foot friction strips
    which stick to the roof. Bruce Roe

    IMGP2436.jpg
    Last edited by bcroe; 05-04-2023, 12:14 AM.

    Leave a comment:


  • J.P.M.
    replied
    Originally posted by bcroe
    This area usually dodges most of that, but we
    did get hit with -10F temps and wind giving a chill of -30F (how much
    of that applies to buildings?).
    Bruce Roe
    Bruce:

    Strictly speaking, since wind chill is defined as what the air temp. feels like to exposed human skin, not much, that is, zero.

    However, dwelling heat loss (or gain) is affected by dry bulb temp. difference inside to outside a dwelling and wind velocity as well as solar input and the radiant effects of the surroundings (including the effective sky temp.)
    The higher the wind velocity is on a building element (with effects for wind direction relative to the building element under consideration thrown in), the greater the heat transfer component due to wind vector will be.

    I believe I understand the physiological concepts involved with the concept of wind chill, but I always thought wind chill was mostly a bunch of B.S. hype whose only use was/is to make people feel more catastrophic.

    If I was out shoveling my driveway in Buffalo w/10F. air temp. and 30 MPH wind (which was pretty common), about the only parts of my body exposed to the air was my nose and eyes. Kind of like who in their right mind opens a window in a blizzard, who's out running around outside butt naked in the cold anyway ?

    Give me the dry bulb temp. and the wind vector and I'll dress appropriately for the circumstances.

    Leave a comment:


  • Mike 134
    replied
    Originally posted by bcroe
    This area usually dodges most of that, but we
    did get hit with -10F temps and wind giving a chill of -30F (how much
    of that applies to buildings?). This does take a slug of energy, with
    my HVAC COP not much better than 1.


    Bruce Roe
    The strong winds remove heat faster from an object outdoors, but the final temperature still is -10.
    Same with your building, if it's fairly airtight the winds won't find ever crack and crevasse to leak in. A tent can feel ok at -10 outside with no wind disturbing the trapped air but have some 30 mph winds pushing into it and it gets pretty cold inside.

    Leave a comment:


  • bcroe
    replied
    Although energy reserve built up was not very high this net metering
    year, warmer weather and some sun allowed it hold for several weeks
    past the usual 1 Nov starting decline. I am hopeful to make it thru with
    some to spare again this winter. This week weather has been really
    tough for the country. This area usually dodges most of that, but we
    did get hit with -10F temps and wind giving a chill of -30F (how much
    of that applies to buildings?). This does take a slug of energy, with
    my HVAC COP not much better than 1.

    One consequence, for my first memory in northern IL, the PoCo ask
    nicely that customers in a dozen states from the E coast to IL try to
    conserve electricity. I do not see much I can do to help. All the
    appliances we should avoid using, are not being used just now. With
    the all electric conversion, almost all my KWh go to heating these
    winter months. But today we did get some real sun, unusual here in
    Dec, so I did clear the panels and contributed some 60KWh to the
    situation.

    With the nuke plant doing nicely, within sight of the property, I doubt
    we will get hit with a rolling blackout. If we do, I will be burning fossil
    fuels in the gen set and the propane furnace to get by, not very green.
    Bruce Roe

    Leave a comment:


  • bcroe
    replied
    I am entering into my 5th winter of using 6 air to air mini
    split heat pumps, to avoid any fossile fuel use, for 2 buildings.
    I plan to report on the experience about fall 23, of a lot of
    details you will not find on YouTu-e. Service incidents have
    been very minimal, less than annual, essentailly all related
    to installer lack of experience. However this DIYer has
    saved a fortune on the work. Bruce Roe
    OcHpN.JPG

    Leave a comment:


  • bcroe
    replied
    A paramont way to manage on less energy here, is to avoid
    wasting it. Any electrical loads continuously on, are subject
    to periodic review. Those located outside the living space are
    especially of interest, since the energy they waste as heat does
    not even contribute (at a low COP) to keeping me warm. These
    include GFIs, gas detector alarms, security devices such as motion
    detector lights, cameras and controls, central vacuum, garage door
    opener controls, TV etc remote control receivers, computer DC
    conversion power packs, and battery maintainers for infrequently
    used IC engines. Some of these were addressed by plugging into
    room circuits that were only on with the lights. Many were hugely
    improved with the purchase of Energy Star appliances. Of those
    remaining, any Wall Wart powered device aquired is suspect.

    There are about 6 Battery Maintainers serving here, for electric
    start IC engines. Recently I went thru the maintainers, noting that
    they tended to draw maximum over 4W, and not much less even
    when battery current was far less power.

    It is not so easy to build a really efficient, economical, line frequency,
    small line isolation/conversion transformer. There is technology to
    get around this using high frequency switching. These may be
    recognized by their heft, or rather lack of it.

    SwitchMaint.png

    I bought a couple of 12V battery maintainers using this technology.
    They were set up with my standrd 12V maintainer EC3 connectors,
    mating to the EC3 connectors on all my IC engine batteries which
    are battery current protected by fusable links. These cannot be
    connected backwards or easily come loose, I do not normally use
    the supplied clip leads.

    CAR WIRE 2.JPGCAR WIRE 1.JPG

    This is the battery end wiring with pins ready to insert into the EC3
    connector. Note the fusible link in the hot, red positivs lead. For
    some wire strain relief a big piece of heat shrink tubing can be used.
    I usually make a dummy mating dust cap.

    I plugged the new tech maintainer into my Kill-A-Watt, and the no
    load draw was 0.0 Watt! My maintainer test unit showed, drain was
    very minimal, tracking needed battery current. Voltage regulation was
    very good, around 13.85 VDC. Looks like this ap might save me a
    couple hundred KWhours a year.

    So I will be checking these units for reliability and EMI. If they prove
    out over time, all the rest of the control transformers here will get
    another look. Bruce Roe

    Leave a comment: