Try our solar cost and savings calculator
solar problems/need guidance
Collapse
X
-
I don't know but I think cats and hawks are pretty good at eliminating squirrels.
you need to get rid of them completely- they tend to populate attics and in order to do that they must make holes in your roof. You can buy special trap cage for them and after they got caught drive them out of town to nearby forest / whatever where they belong. In terms of climbing I saw them hanging comfortably on a vertical brick wall or climbing upper part of the roof under negative angle. I don't think anything less than electric fence will deter them
.Leave a comment:
-
you need to get rid of them completely- they tend to populate attics and in order to do that they must make holes in your roof. You can buy special trap cage for them and after they got caught drive them out of town to nearby forest / whatever where they belong. In terms of climbing I saw them hanging comfortably on a vertical brick wall or climbing upper part of the roof under negative angle. I don't think anything less than electric fence will deter them
.
Leave a comment:
-
thank you for the information. I will use it. I found another group of bare wires today already. and yes every panel and wire leading to them will be checked. is it worth to put up a squirrel cage around the array?
OK, thanks for confirming you did track down wiring problems; from your description above, it
would be advised to check 100% of your wiring for damage. Again keep in mind, these voltages
are far more dangerous than the sort of potential we in the phone and related bus encountered.
Critters can be a problem, I have been lucky to suffer no damage with a ground mount; raccoons,
turkeys, ground squirrels, and many others inhabiting the area. It will not be a surprise the day I
find a cooked deer in my array.
Once your wiring is fully repaired and still isolated from inverters, you should not be able to draw
any kind of voltage from any array lead to ground. My low impedance tester is several 75 bulbs in
series, which draws off any static charges. And draws a nice (controlled) arc when current flows.
Your MC4s are low quality, non precious metal connectors which will not tolerate much abuse.
Don't leave them exposed to the elements, they quickly oxidize. Don't interrupt current with
them, not even for a single low voltage panel. Instead make a test circuit with your meter and
a switch. Plug this into the panel AND THEN close the switch to make a current reading. Open
the switch and move on. This will allow you to grind off the latches on your MC4 test connectors
to save a lot of test time.
Don't try this for multiple panels in series, as it will arc the switch to destruction. Only a large
high voltage DC disconnect can handle this, and doing it very many times will soon wear
it out; I consider it for emergency or nighttime use only.
As for measuring current, inserting a meter in a high current DC circuit is a lot more difficult
than it appears on the blackboard. My advice is get a nice DC clamp on ammeter, a very
useful tool around PV. Otherwise put a shunt resistor in the circuit (could be permanent)
and use your sensitive DVM to measure the voltage across the shunt. You can measure
the current of an entire string as well as one panel, but you will only be able to make one
measurement a day, moving the test connection at night. Bruce RoeLeave a comment:
-
I will mike, thanksLeave a comment:
-
Please be careful about connecting your series ampmeter, even to a single panel. 40V is a really stout arc welding voltage and will easily damage the MC connectors
Leave a comment:
-
that worked thanksLeave a comment:
-
panel normally is source of current so it tolerates being shorted very well. bcroe even recommends to do this on outside installations to keep connectors protected from weather. If you think about it panel doesn't 'produce' the energy it can only 'shorten' less than 20% of what already fell on it anyway.
Something is up with your meter- can you connect it to 1.5V AA battery for a second? It should give you 1-3 A current.Last edited by max2k; 08-02-2017, 06:00 PM.Leave a comment:
-
OK, thanks for confirming you did track down wiring problems; from your description above, itbcroe you are correct with your advice and I thank you for it. i as far as thr gfi fault i followed it, that's how i found the 3 problems so far.have worked on dc power plants from -48v, +24v, up to 10,000 amps for last 37 years. I might not know the system but I do know caution. i found 3 faults so far, one bad connector and looks like some animal ate the insulation off the other 2. and that's only after going through 20% I'm thinking about a cage around all the panels to stop the critters
would be advised to check 100% of your wiring for damage. Again keep in mind, these voltages
are far more dangerous than the sort of potential we in the phone and related bus encountered.
Critters can be a problem, I have been lucky to suffer no damage with a ground mount; raccoons,
turkeys, ground squirrels, and many others inhabiting the area. It will not be a surprise the day I
find a cooked deer in my array.
Once your wiring is fully repaired and still isolated from inverters, you should not be able to draw
any kind of voltage from any array lead to ground. My low impedance tester is several 75 bulbs in
series, which draws off any static charges. And draws a nice (controlled) arc when current flows.
Your MC4s are low quality, non precious metal connectors which will not tolerate much abuse.
Don't leave them exposed to the elements, they quickly oxidize. Don't interrupt current with
them, not even for a single low voltage panel. Instead make a test circuit with your meter and
a switch. Plug this into the panel AND THEN close the switch to make a current reading. Open
the switch and move on. This will allow you to grind off the latches on your MC4 test connectors
to save a lot of test time.
Don't try this for multiple panels in series, as it will arc the switch to destruction. Only a large
high voltage DC disconnect can handle this, and doing it very many times will soon wear
it out; I consider it for emergency or nighttime use only.
As for measuring current, inserting a meter in a high current DC circuit is a lot more difficult
than it appears on the blackboard. My advice is get a nice DC clamp on ammeter, a very
useful tool around PV. Otherwise put a shunt resistor in the circuit (could be permanent)
and use your sensitive DVM to measure the voltage across the shunt. You can measure
the current of an entire string as well as one panel, but you will only be able to make one
measurement a day, moving the test connection at night. Bruce RoeLast edited by bcroe; 08-02-2017, 04:43 PM.Leave a comment:
-
Leave a comment:
-
yeah I have a rms clamp meter. so I didn't know you could short the panel. that's the way ill go then. thanksLeave a comment:
-
Yeah, sounds like you need to double check your meter against a known current, or double check the fuse inside isn't blown. Do you have access to a clamp on meter? Then you could just directly short the panel's DC- and DC+ leads, and measure with the clamp.
yes and it has the 10a jack. same on all the panels I checked so far. now the panels I checked so far are all on the same two strings that went to the inverter that had the blown gfi fuse. could they all be bad? but yet the voltages are fine. it could be the meter but long shot.Leave a comment:
-
yes and it has the 10a jack. same on all the panels I checked so far. now the panels I checked so far are all on the same two strings that went to the inverter that had the blown gfi fuse. could they all be bad? but yet the voltages are fine. it could be the meter but long shot.Last edited by tim a; 08-02-2017, 03:41 PM.Leave a comment:
-
Leave a comment:
-
yeah I did that to one panel, 40 vdc but 0 amps, these are 12 year old panels. its suppose to be 40v and 5.25 amp per panel
of course- you just connect amperemeter to it (or multimeter in amperemeter mode) with sufficient range. Since this is DC there will be a little arching from single panel so try not to play with this for too long and connect/disconnect quickly. Modern >300W panel in full sun can produce up to 10A current. Please don't try to do this for more than single panel- while current will be the same arching due to higher voltage will damage connectors.Last edited by tim a; 08-02-2017, 03:24 PM.Leave a comment:
Copyright © 2014 SolarReviews All rights reserved.
Powered by vBulletin® Version 6.1.3
Copyright © 2026 MH Sub I, LLC dba vBulletin. All rights reserved.
Copyright © 2026 MH Sub I, LLC dba vBulletin. All rights reserved.
All times are GMT-5. This page was generated at 11:23 AM.
Leave a comment: