Can you stack hybrid inverters in a large PV system?

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • TheMechE
    Junior Member
    • Jun 2017
    • 19

    #16
    Originally posted by ButchDeal
    Why do people try so hard to over complicate things

    my system and all D.C. Coupled systems have

    Code:
    Backup load
    I
    solar ------- CC------- DC bus-------inverter-------grid
    I
    Battery


    the inverter can regulate how much int inverts and if it is a charger or inverter, thus it controls the flow of power
    you can have multiple inverters and multiple CC on the system
    ouback inverters can sync with each other and the grid
    they can sync either in phase or opposite phase or with three of them for 3 phase.
    if they are configured for in phase or out of phase with an auto-transformer then one can shut down if the load is less than the other can handle by itself.
    That is cool. Thank you for the information. I will look into outback inverters since they can sync with each other. My concern was just that the system I was thinking about was really large and I don't know if there are limits for how many inverters can sync. I assume you meant that your system looks like this from what you told me before though.


    Code:
    ...........................Backup load
    ...................................I
    solar ------- CC------- DC bus-------inverter-------grid
    ...................................I
    ................................Battery

    Comment

    • ButchDeal
      Solar Fanatic
      • Apr 2014
      • 3802

      #17
      Originally posted by TheMechE

      That is cool. Thank you for the information. I will look into outback inverters since they can sync with each other. My concern was just that the system I was thinking about was really large and I don't know if there are limits for how many inverters can sync. I assume you meant that your system looks like this from what you told me before though.

      ..............................................Back up load
      .................................................. .........I
      solar ------- CC------- DC bus-------inverter-------grid
      ...................................I
      ................................Battery

      it is like this
      nearly all DC coupled bimodal systems are simlar

      There are stacking limitations on the count of inverters that vary by model.

      OutBack FP1 w/ CS6P-250P http://bit.ly/1Sg5VNH

      Comment

      • TheMechE
        Junior Member
        • Jun 2017
        • 19

        #18
        Originally posted by ButchDeal


        ..............................................Back up load
        .................................................. .........I
        solar ------- CC------- DC bus-------inverter-------grid
        ...................................I
        ................................Battery

        it is like this
        nearly all DC coupled bimodal systems are simlar

        There are stacking limitations on the count of inverters that vary by model.
        Is there a known way to get past stacking limitations? Like with a very large system? Is there a controller that can accept many AC input signals and sync them all to output a single AC signal?
        Last edited by TheMechE; 06-28-2017, 10:26 AM.

        Comment

        • ButchDeal
          Solar Fanatic
          • Apr 2014
          • 3802

          #19
          Originally posted by TheMechE

          Is there a known way to get past stacking limitations? Like with a very large system? Is there a controller that can accept many AC input signals and sync them all to output a single AC signal?
          you can talk to outback or Schneider etc. on setting up a large system. It looks like the Radian is limited to 10 which would get you to 80kw of inverter. That would be enough for a 100kw array.

          OutBack FP1 w/ CS6P-250P http://bit.ly/1Sg5VNH

          Comment

          • TheMechE
            Junior Member
            • Jun 2017
            • 19

            #20
            Originally posted by ButchDeal

            you can talk to outback or Schneider etc. on setting up a large system. It looks like the Radian is limited to 10 which would get you to 80kw of inverter. That would be enough for a 100kw array.

            http://www.outbackpower.com/download..._specsheet.pdf
            Thanks, just to make sure, something like that wouldn't convert the solar power to AC before converting it back to DC to put in the batteries right? It chooses either to convert it to AC or leave it as DC and charge the batteries. Or is this the one you use where the inverter and the CC aren't combined into one unit, so it can go to DC first then to the inverter?

            Comment

            • ButchDeal
              Solar Fanatic
              • Apr 2014
              • 3802

              #21
              Originally posted by TheMechE
              Thanks, just to make sure, something like that wouldn't convert the solar power to AC before converting it back to DC to put in the batteries right?
              That would be AC coupled

              Originally posted by TheMechE
              It chooses either to convert it to AC or leave it as DC and charge the batteries.
              DC coupled.


              Originally posted by TheMechE
              Or is this the one you use where the inverter and the CC aren't combined into one unit, so it can go to DC first then to the inverter?
              Outback and Schneider use separate charge controllers.

              Normally Outback would be DC coupled for a system like this but you could configure it any way you like. If you wanted AC coupled you would have to add on grid tie inverters and skip the charge controllers. I would recommend going DC coupled using Charge Controllers though.

              OutBack FP1 w/ CS6P-250P http://bit.ly/1Sg5VNH

              Comment

              • TheMechE
                Junior Member
                • Jun 2017
                • 19

                #22
                Originally posted by ButchDeal
                That would be AC coupled


                DC coupled.



                Outback and Schneider use separate charge controllers.

                Normally Outback would be DC coupled for a system like this but you could configure it any way you like. If you wanted AC coupled you would have to add on grid tie inverters and skip the charge controllers. I would recommend going DC coupled using Charge Controllers though.
                Yeah, converting the DC to AC (AC coupled system) doesn't make sense to me because you lose efficiency when you convert back to DC. Definitely would want a DC coupled system.

                Comment

                • Mike90250
                  Moderator
                  • May 2009
                  • 16020

                  #23
                  Originally posted by TheMechE
                  ....Is it a large zener diode to ensure energy only goes into the batteries and not out unless the grid goes offline? .......
                  I'm going to kneecap the person responsible for implanting in folks minds you need diodes in solar systems.

                  Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                  || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                  || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                  solar: http://tinyurl.com/LMR-Solar
                  gen: http://tinyurl.com/LMR-Lister

                  Comment

                  • ButchDeal
                    Solar Fanatic
                    • Apr 2014
                    • 3802

                    #24
                    Originally posted by Mike90250

                    I'm going to kneecap the person responsible for implanting in folks minds you need diodes in solar systems.
                    but if you don't have them then the power will flow backwards and the PV modules will glow light light bulbs...
                    OutBack FP1 w/ CS6P-250P http://bit.ly/1Sg5VNH

                    Comment

                    • TheMechE
                      Junior Member
                      • Jun 2017
                      • 19

                      #25
                      Originally posted by Mike90250

                      I'm going to kneecap the person responsible for implanting in folks minds you need diodes in solar systems.
                      Originally posted by ButchDeal

                      but if you don't have them then the power will flow backwards and the PV modules will glow light light bulbs...

                      I was talking about something like this. I mean, how else do you stop the batteries from being drained unless the equipment communicates which it sounds like it does?

                      Last edited by TheMechE; 06-28-2017, 03:30 PM.

                      Comment

                      • ButchDeal
                        Solar Fanatic
                        • Apr 2014
                        • 3802

                        #26
                        there is so much wrong with that drawing.
                        What is the grid tie inverter doing?
                        you don't connect batteries to the input on a grid tie inverter and you don't connect a charge controller to a grid tie inverter input.
                        OutBack FP1 w/ CS6P-250P http://bit.ly/1Sg5VNH

                        Comment

                        • TheMechE
                          Junior Member
                          • Jun 2017
                          • 19

                          #27
                          Originally posted by ButchDeal
                          there is so much wrong with that drawing.
                          What is the grid tie inverter doing?
                          you don't connect batteries to the input on a grid tie inverter and you don't connect a charge controller to a grid tie inverter input.
                          Thank you. I see what you mean. I revised the image. The problem is I need inverters that can handle a very large PV system (probably too large for hybrid inverters?) yet I also want to be able to function independently of the grid.

                          So I am seeing three scenarios here:
                          1. Grid-tie only (no batteries nor hybrid inverter needed. I can remove those from the image)
                          2. Hybrid system (all components in the image remain, including the zener diode?)
                          3. Pure off-grid system (remove grid-tie inverters from system)

                          I hate switches because they can fail and cause a lot of problems, but maybe this shows why I think I need the zener diodes so the hybrid inverter can choose whether to draw from the batteries or not.

                          I need to do more reading on MPPT charge controllers though. Can they always put 100% of the PV power into the batteries if the batteries aren't fully charged? Or are batteries picky and can only accept so much energy at once depending on their state on charge?
                          Last edited by TheMechE; 06-28-2017, 02:34 PM.

                          Comment

                          • ButchDeal
                            Solar Fanatic
                            • Apr 2014
                            • 3802

                            #28
                            I don't see a new image but also don't really understand they the zener diodes.

                            The hybrid inverter is going to draw the power it needs for the loads when off grid from the DC bus. In off grid it is either this or shut down. The power comes from Grid and/or battery but there is no choice the power is needed.

                            In grid tie mode the inverter inverters what is left over after any charging from the charge controllers. There is no need to "Control" the flow just regulate how much it inverters.
                            So if you are getting 5kw from solar and using 3 to charge the battery then the inverter can invert 2kw, problem solved no need for any diodes or switches.

                            OutBack FP1 w/ CS6P-250P http://bit.ly/1Sg5VNH

                            Comment

                            • TheMechE
                              Junior Member
                              • Jun 2017
                              • 19

                              #29
                              Originally posted by ButchDeal
                              I don't see a new image but also don't really understand they the zener diodes.

                              The hybrid inverter is going to draw the power it needs for the loads when off grid from the DC bus. In off grid it is either this or shut down. The power comes from Grid and/or battery but there is no choice the power is needed.

                              In grid tie mode the inverter inverters what is left over after any charging from the charge controllers. There is no need to "Control" the flow just regulate how much it inverters.
                              So if you are getting 5kw from solar and using 3 to charge the battery then the inverter can invert 2kw, problem solved no need for any diodes or switches.
                              The new image is in the old post. I just ended up replacing the old image with the new one. What you said makes sense. The inverter only inverts what it needs. The rest goes to the batteries.

                              What is to stop some of the energy from leaking out of the batteries and flowing unneeded into the inverter though (and then the batteries getting recharged from the output of the solar panel)? Wouldn't that be an efficiency loss and bad for the batteries? Here's an image of what I mean. I know the NET flow to the batteries is zero in this case, but couldn't there still be flow to and from the batteries?



                              What I'm trying to ask here is how do you know the inverter's source of power is 100% the PV panels and 0% battery energy? The way I see it, either the battery or the PV panel could supply energy to the inverter.

                              Comment

                              • Mike90250
                                Moderator
                                • May 2009
                                • 16020

                                #30
                                Originally posted by TheMechE
                                .......
                                What is to stop some of the energy from leaking out of the batteries and flowing unneeded into the inverter though (and then the batteries getting recharged from the output of the solar panel)? Wouldn't that be an efficiency loss and bad for the batteries? Here's an image of what I mean. I know the NET flow to the batteries is zero in this case, but couldn't there still be flow to and from the batteries?.....
                                Same thing that keeps your 100w light bulb from consuming 1800w when it's plugged into the grid.
                                Simple electrical theory, parts that are operating properly, consume a limited amount of power, not unlimited power.

                                Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                                || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                                || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A