That is somewhat contradictory.
Unlike voltage drop in conductors to a load, the voltage drop caused by current in the wires adds to the voltage seen by the inverter, making it higher than the grid voltage.
So what you really need are shorter wires and larger wires to reduce that voltage difference as much as possible.
But if the grid voltage itself goes higher than the inverter's threshold setting even a zero ohm wire would not be good enough.
If POCO won't correct it and the inverter manufacturer will not release the setting codes, you could be forced to use a buck/boost transformer to lower the voltage at the inverter.
FWIW, 260/130 on a residential service will burn out incandescent light bulbs pretty fast, so I guess it if fortunate that they are not used much anymore.
Unlike voltage drop in conductors to a load, the voltage drop caused by current in the wires adds to the voltage seen by the inverter, making it higher than the grid voltage.
So what you really need are shorter wires and larger wires to reduce that voltage difference as much as possible.
But if the grid voltage itself goes higher than the inverter's threshold setting even a zero ohm wire would not be good enough.
If POCO won't correct it and the inverter manufacturer will not release the setting codes, you could be forced to use a buck/boost transformer to lower the voltage at the inverter.
FWIW, 260/130 on a residential service will burn out incandescent light bulbs pretty fast, so I guess it if fortunate that they are not used much anymore.