I'm looking at Sunny Boy specs and came across the following for their 7700TL-US:
Maximum system voltage 600 V
Rated MPP tracking voltage range at 240 V AC 270 V to 480 V
Rated operating voltage 400 V
Correct me if I'm wrong; I assume the 600V relates to the array open circuit voltage.
Assuming the array is very near Voc as configured, what am I to make of the 400V rated operating voltage and the MPP range? Am I supposed to stay at or below 400V as the strings Vmp? If I go above 400V is it clipped - what ? If Voc is 590 is the MPP normally near their 480 given the average panel and therefore I don't have to worry about it? The graphs trying to display where the max power point is located appears very near Voc so I can't believe that its over 100 volts below it in an actual situation. I have no experience in this - how do you interpret this stuff?
I'm using a spreadsheet I downloaded from SMA's web site to try some configurations and keep getting a warning about
"Module Isc exceeds allowable for 2 strings per input" . Reading their installation manual on how strings are physically connected gives me the impression that two strings are placed in parallel per either the A or B sections of the inverter. The connectors inside their DC disconnect are just a convenience to allow 4 wires to become 2 wires electrically.
Their spec says :
Maximum short-circuit current per MPP tracking input 19 A
but with my test input set for Isc @ 7 amps I still get the warning. Last time I checked 2 * 7 = 14.
Spreadsheet bug?
Maximum system voltage 600 V
Rated MPP tracking voltage range at 240 V AC 270 V to 480 V
Rated operating voltage 400 V
Correct me if I'm wrong; I assume the 600V relates to the array open circuit voltage.
Assuming the array is very near Voc as configured, what am I to make of the 400V rated operating voltage and the MPP range? Am I supposed to stay at or below 400V as the strings Vmp? If I go above 400V is it clipped - what ? If Voc is 590 is the MPP normally near their 480 given the average panel and therefore I don't have to worry about it? The graphs trying to display where the max power point is located appears very near Voc so I can't believe that its over 100 volts below it in an actual situation. I have no experience in this - how do you interpret this stuff?
I'm using a spreadsheet I downloaded from SMA's web site to try some configurations and keep getting a warning about
"Module Isc exceeds allowable for 2 strings per input" . Reading their installation manual on how strings are physically connected gives me the impression that two strings are placed in parallel per either the A or B sections of the inverter. The connectors inside their DC disconnect are just a convenience to allow 4 wires to become 2 wires electrically.
Their spec says :
Maximum short-circuit current per MPP tracking input 19 A
but with my test input set for Isc @ 7 amps I still get the warning. Last time I checked 2 * 7 = 14.
Spreadsheet bug?
Comment