Adding panels to an existing array

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • Kerry
    Junior Member
    • May 2010
    • 1

    #1

    Adding panels to an existing array

    I hope this is not too simple, but I can't fins the answer with google...

    I have 24 Aleo s-18 225 watt panels hooked to a SMA SB 7000 in 3 8 panel strings. I would like to add more panels, but the original supplier/installer is not an option. The question is: If I buy 225 watt panels from a different manufacturer, are they going to be compatible if they have there own string? Are they going to drag down the rest of the system because of voltage differences?

    I understand that I can add more panels if I add a new inverter, but the inverter that I have has alot of capacity to spare. And I would rather not spend the money on a separate one if I can get away with it.

    Thanks for reading
  • Mike90250
    Moderator
    • May 2009
    • 16020

    #2
    Depends. If the inverter has SEPERATE MPPT controllers, then you can hook any compatible string to the other input. If there is only a single MPPT controller, then all the strings should be matched, or performance will suffer as the inverter hunts for a sweet spot that does not exist.
    The closer you can match the string voltages, then the less loss you will have.
    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister

    Comment

    • solar_geoff
      Member
      • Jan 2009
      • 49

      #3
      If you can find modules with a very similar I-V curve it would work OK... But if not its pretty much its not going to work even if you have an entire string of the new mod. By having a different type of module you will be outputting a completely different voltage which will not allow the invereter to find a consistent max power point. Production would suffer heavily.