    Originally posted by bcroe
    Yea, yea, I know. I rewired the breakers myself, using 6 ga where 10 ga would have worked.
    I torque things pretty well, but perhaps rechecking them a few times the first year is good.
    Although, I believe the first trips were observed before the smaller wire was replaced. Guess
    I'd have to prove a bad breaker, to defend my honor. Later, Bruce
    I would never deliberately impugn your honor, just make fun of you behind your back.

    Leave a comment:


  • bcroe
    replied
    Loose Terminal

    Originally posted by inetdog
    It is also possible that the connection was never correctly torqued or just loosened up from thermal cycling.
    Once the breaker has spend too much time with a hot terminal or has gone through a few trips from that heat source it may be permanently damaged and its set point effectively lowered.
    Yea, yea, I know. I rewired the breakers myself, using 6 ga where 10 ga would have worked.
    I torque things pretty well, but perhaps rechecking them a few times the first year is good.
    Although, I believe the first trips were observed before the smaller wire was replaced. Guess
    I'd have to prove a bad breaker, to defend my honor. Later, Bruce

    Leave a comment:


  • inetdog
    replied
    Originally posted by bcroe
    A close
    exam revealed one wire from the inverter was discolored from heat at the breaker terminal.
    Maybe it was one of those counterfeit Squ*re D breakers from Asia. I replaced the breaker and
    had no more problems. Bruce Roe
    It is also possible that the connection was never correctly torqued or just loosened up from thermal cycling.
    Once the breaker has spend too much time with a hot terminal or has gone through a few trips from that heat source it may be permanently damaged and its set point effectively lowered.

    Leave a comment:


  • bcroe
    replied
    Inverter trip

    Originally posted by inetdog
    AHA! Yes, one of the things often forgotten is that high resistance in the connection between POCO and GTI can cause the GTI output to go too high.
    But if the resistance were that high, I would also expect some other part of the anti-islanding circuitry to have tripped too.
    Was the problem just on one side of the 240 circuit, causing a trip based on L1-N to L2-N imbalance?
    I believe the trip code was a little vague, but caused by excessive voltage. With 60A into a
    600' loop of 4 gauge, drop is higher than ideal. But that extra percent loss only occurs in the
    limited time the inverters peak; I won't be digging up all that wire installed decades ago.

    At first the inverter would trip at high power, I thought it was programmed wrong since its twin
    never tripped. Then the 40A breaker started tripping (the other breaker never tripped). A close
    exam revealed one wire from the inverter was discolored from heat at the breaker terminal.
    Maybe it was one of those counterfeit Squ*re D breakers from Asia. I replaced the breaker and
    had no more problems. Bruce Roe

    Leave a comment:


  • inetdog
    replied
    Originally posted by bcroe
    Forgot to mention, I had one of my inverters tripping with a high line voltage code. In
    time it turned out to be a failing 40A circuit breaker into the 240VAC line. Replaced
    that and had no more trouble. Bruce Roe
    AHA! Yes, one of the things often forgotten is that high resistance in the connection between POCO and GTI can cause the GTI output to go too high.
    But if the resistance were that high, I would also expect some other part of the anti-islanding circuitry to have tripped too.
    Was the problem just on one side of the 240 circuit, causing a trip based on L1-N to L2-N imbalance?

    Leave a comment:


  • bcroe
    replied
    Over Voltage

    Forgot to mention, I had one of my inverters tripping with a high line voltage code. In
    time it turned out to be a failing 40A circuit breaker into the 240VAC line. Replaced
    that and had no more trouble. Bruce Roe

    Leave a comment:


  • Naptown
    replied
    Call tech support I have found them to be very helpful and quick with an answer.
    The inverter you have is limited in max voltage and is for a European application. The IG+ UNI can be field programmed for varying voltages (208 240 277)
    Not sure about the one you have.

    Leave a comment:


  • bcroe
    replied
    Programming

    Originally posted by nrsilva
    Hi there,
    I have a fronius IG20 that shutdown with 250Vca.
    I would like to raise this Value to 260Vca. Have you any idea how to do this?
    Is there a secret password or menu to do this? Regards, Silva
    My Fronius converters definitely have a programmable voltage limit, as well
    as an absolute design limit. And there is a password. Since i am running 240VAC
    into a pretty long loop (only slightly over gauge), they were programmed to much
    higher than the default limit. No problem, as the inverters could also feed 277VAC.

    Bruce Roe

    Leave a comment:


  • latitude500
    replied
    I'm sorry I really don't know, You could always give Fronius a call, but the tech support isn't very helpful. I ended up junking mine, and swapping it out with a SMA inverter.
    Good luck,


    Originally posted by nrsilva
    Hi there,
    I have a fronius IG20 that shutdown with 250Vca.
    I would like to raise this Value to 260Vca. Have you any idea how to do this?
    Is there a secret password or menu to do this?
    Regards,
    Silva

    Leave a comment:


  • nrsilva
    replied
    Originally posted by peakbagger
    If the voltage is out of range it could be the utility. Local grid conditions can lead to higher or lower utility voltage or something as simple as someone ran into a light pole down the road and they tapped the wrong tap on a replacement light pole. The voltages can and do change during the day depending on grid loads. My friend had issues like these and Fronius gave him the super secret code to change his voltage range a little wider. He complained to the power company and they ended up installing a recording volt meter and it proved that their system was at fault and eventually fixed it.
    Hi there,
    I have a fronius IG20 that shutdown with 250Vca.
    I would like to raise this Value to 260Vca. Have you any idea how to do this?
    Is there a secret password or menu to do this?
    Regards,
    Silva

    Leave a comment:


  • latitude500
    replied
    I've had the Austin Energy company come out and check the electrical amount, and they said it was in the correct range. And the Solar Panel company that came out and checked the inverter also stated it was bad. So I'm at a lost on what to do.

    peakbagger I didn't know you could change the electric range of the system. Can you tell me more of that? I've called Fronius and because it is 2 MONTHS out of warranty they couldn't care less. The help desk support guy Dan even stated that I would be better off with another inverter. What a joke. But I'm hoping that I don't have to replace this one because paying out for another one is going to be hard.

    Leave a comment:


  • peakbagger
    replied
    If the voltage is out of range it could be the utility. Local grid conditions can lead to higher or lower utility voltage or something as simple as someone ran into a light pole down the road and they tapped the wrong tap on a replacement light pole. The voltages can and do change during the day depending on grid loads. My friend had issues like these and Fronius gave him the super secret code to change his voltage range a little wider. He complained to the power company and they ended up installing a recording volt meter and it proved that their system was at fault and eventually fixed it.

    Leave a comment:


  • Naptown
    replied
    Also call tech support it may not be a bad inverter but many are programable for the voltage of the grid.
    If for some reason the programming was changed this may be causing the error.
    (had this happen once)

    Leave a comment:


  • Mike90250
    replied
    you might want to get a volt meter and check the voltages yourself, before assuming the inverter is bad. I don't know what the error codes mean.

    Leave a comment:


  • danboy
    replied
    google best high efficient inverters.
    some inverters are at 98.5% now so u can gain an extra 2%+ in output.
    i think it should cost no more then 1500.00 as i can get the power one 5000 TL for 2k.