I have 6 x 180 Watt Solar-Panels and 4 x 200 Ah 12V Batteries. The Batteries are connected parallel, so that the input/output is 24V. Now I want to buy a "Best-Quality" Controller to charge the Batteries. Which Controller is the best for my requirements?
Try our solar cost and savings calculator
Which Controller for 1KW-Solarpanel-Array and 800Ah Batteries is the best?
Collapse
This topic is closed.
X
X
-
-
Next eye opener for you is if wired at 24 volts you only need a 40 amp MPPT controller and much smaller copper wire, take it up to 48 volts and all you need is a 20 amp MPPT controller and even smaller wire. You are talking thousands of dollars in savings and a much more efficient system.
Anyway you are looking for Morningstar and Midnight Solar MPPT controllers. Do not even think about PWM.MSEE, PE -
Thank you for your answer
Next eye opener for you is if wired at 24 volts you only need a 40 amp MPPT controller and much smaller copper wire, take it up to 48 volts and all you need is a 20 amp MPPT controller and even smaller wire. You are talking thousands of dollars in savings and a much more efficient system.Anyway you are looking for Morningstar and Midnight Solar MPPT controllers. Do not even think about PWM.Comment
-
For Morningstar product line you are looking for a Morningstar TriStar MPPT 45 Amp controller. If you see expansion in your future go with the 60 amp model. With the 40 amp model at 24 volts 1200 is the maximum input you can run. Or you can upgrade to 48 volts which gets you up to 2400 watts input.
I do not know how you have the panels configured or the specs of your panels but you will most likely want them in a 2 x 3 configuration meaning 2 strings in parallel with each string having 3 panels in series. If you have high voltage Grid Tied panels you may need to go with 3 x 2.
- What are the panel specs so I can give you the most optimum config? (Voc Vmp, and Isc)
- In addition what is the 1-way cable distance between panels and controller?
MSEE, PEComment
- What are the panel specs so I can give you the most optimum config? (Voc Vmp, and Isc)
-
> OK that raises some concern. Is it because the charger is faulty, or you are using more power than the panels can replace?
I can not change the 24V system because I am not a big expert in electricity and I have already an inverter which works with 24V.
> What are the panel specs so I can give you the most optimum config?
The solar panels are already installed on the roof, so I can not see the exact technical details. But each solar panel have 180W @ 17V
I also do not know how the solar panels are wired, but I checked the voltage of solar panel cable (at my home) - there is about 45V in a peek-time when the cable is not connected to the controller.
> In addition what is the 1-way cable distance between panels and controller?
Between solar panels and the controller is about 40m cable.
> For Morningstar product line you are looking for a Morningstar TriStar MPPT 45 Amp controller.
This Morningstar controller looks really good, thank you for this recommendation. I think that I will buy this controller.Comment
-
> What are the panel specs so I can give you the most optimum config?
The solar panels are already installed on the roof, so I can not see the exact technical details. But each solar panel have 180W @ 17V
I also do not know how the solar panels are wired, but I checked the voltage of solar panel cable (at my home) - there is about 45V in a peek-time when the cable is not connected to the controller.
Can you tell me what size wire is between the panels and controller?MSEE, PEComment
-
Another question
We would need to know the panel specs manufacturer and open circuit voltage and location for coldest recorded temperature.
There may be a possibility of wiring all panels in series reducing your losses even further
You may at that point need to go to a midnight 250v controller which would work in any case.
Don't buy anything yetLast edited by Naptown; 09-17-2013, 09:57 AM.NABCEP certified Technical Sales Professional
[URL="http://www.solarpaneltalk.com/showthread.php?5334-Solar-Off-Grid-Battery-Design"]http://www.solarpaneltalk.com/showth...Battery-Design[/URL]
[URL]http://www.calculator.net/voltage-drop-calculator.html[/URL] (Voltage drop Calculator among others)
[URL="http://www.gaisma.com"]www.gaisma.com[/URL]Comment
-
Rich it sounds like he has standard battery panels with a Voc of 23 volts. Pretty much can go with NEC 125% rating of 6 panels x 23 volts x 1.25 = 173 volts. Classic 200 would make a good fit, but I suspect price might be an issue for him since he is not in the USA. Us price for a Midnite Solar Classic 200 is around $600 to $700 USDMSEE, PEComment
-
That's why I asked for coldest temp and panel specs.
Can't do much on costNABCEP certified Technical Sales Professional
[URL="http://www.solarpaneltalk.com/showthread.php?5334-Solar-Off-Grid-Battery-Design"]http://www.solarpaneltalk.com/showth...Battery-Design[/URL]
[URL]http://www.calculator.net/voltage-drop-calculator.html[/URL] (Voltage drop Calculator among others)
[URL="http://www.gaisma.com"]www.gaisma.com[/URL]Comment
-
Get a Midnite Classic 200, wire all the panels in series, get some stranded 10Ga copper wire for the panel to CC run. Then eventually, wire those same batteries into a 48V single series string and switch the inverter out to a 48V one.
someone check me...1150W, Midnite Classic 200, Cotek PSW, 8 T-605sComment
-
Well if you take worse case of NEC 125% you eliminate the need for derating as it is already overkill @ 125%. 6 battery panels in series are not going to go over 200 Voc anywhere on earth to my knowledge. I agree about the cost.MSEE, PEComment
-
I suspect he also is in defecit charging which means either cut power usage or upsize everything.MSEE, PEComment
-
My bad, I thought the run was 40Ft, still, 6Ga would be alot cheaper wire than 2/01150W, Midnite Classic 200, Cotek PSW, 8 T-605sComment
-
I suspect maybe a # 8 wire from panels to CC and he currently has a PWM controller.
This is a recipe for deficient charging.
But let's see what he comes back with.NABCEP certified Technical Sales Professional
[URL="http://www.solarpaneltalk.com/showthread.php?5334-Solar-Off-Grid-Battery-Design"]http://www.solarpaneltalk.com/showth...Battery-Design[/URL]
[URL]http://www.calculator.net/voltage-drop-calculator.html[/URL] (Voltage drop Calculator among others)
[URL="http://www.gaisma.com"]www.gaisma.com[/URL]Comment
-