    Inverter sizing and unequal strings

    New member. San Diego County, CA. Signed for 15 panel Sunpower 327's w/Sunpower SPR5000m inverter (at $4.50/N.P.Watt BTW). 2 month signup to startup baring gross permitting delays or vendor picks up elec. bill after 60 days until startup
    Roof azimuth 15.8 deg. west of due south. Roof el. 18.8 deg. No shade any day between 0800 and 1600 hrs. solar time. 16 panels possible but tight and somewhat funky looking pretty much regardless of how I do it. If I had more room It wouldn't be Sunpower.
    A few questions about the choice of inverter and stringing if I might:

    1.) Is the inverter oversized ?
    2.) Is the inverter transformerless ?
    3.) Is it possible/adviseable using this inverter to have 2 strings of unequal size, 7 on one string and 8 on the next ? OR,

    4.)Have 3 strings of 5 panels/string ?

    Regards,

    J.P.M.
  • Mike90250
    Moderator
    • May 2009
    • 16020

    #2
    Inverter might be a little oversize, but it only hurts the pocketbook. Maybe the next size down is too small.

    If it's heavy, it has a transformer - or read the fine print.

    Strings MUST be equal panels, 3 strings of 5 might work, but 7 & 8 will not be good.

    You must look for 2 specs in the inverter, it's MPPT range (not the same as operating range) and the Max input voltage. Then you see if 5 series panels approaches the Max voltage, and if it is nicely inside the MPPT range.
    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister

    Comment

    • J.P.M.
      Solar Fanatic
      • Aug 2013
      • 15038

      #3
      Originally posted by Mike90250
      Inverter might be a little oversize, but it only hurts the pocketbook. Maybe the next size down is too small.

      If it's heavy, it has a transformer - or read the fine print.

      Strings MUST be equal panels, 3 strings of 5 might work, but 7 & 8 will not be good.

      You must look for 2 specs in the inverter, it's MPPT range (not the same as operating range) and the Max input voltage. Then you see if 5 series panels approaches the Max voltage, and if it is nicely inside the MPPT range.
      Funky or not, I went to 16 327's, 25 strings of 8. I think this will fit inverter parameters.

      Thanks for the help.

      J.P.M.

      Comment

      • J.P.M.
        Solar Fanatic
        • Aug 2013
        • 15038

        #4
        Originally posted by J.P.M.
        Funky or not, I went to 16 327's, 25 strings of 8. I think this will fit inverter parameters.

        Thanks for the help.

        J.P.M.
        Correction: 2 strings of 8

        J.P.M.