    Maximum System Voltage

    What exactly does the maximum system voltage of a solar panel refer too?

    I
  • Mike90250
    Moderator
    • May 2009
    • 16020

    #2
    It means you can string a lot of panels in series, to make a high voltage array, for powering a Grid-Tie inverter. A year ago, 600V was the common voltage, the inverters run up to 500V input, for less amps and less loss. (20 panels in series is only 4 amps, but 550V)

    I don't know why a large safety rating would be a bad thing.
    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister

    Comment

    • JTSOLAR
      Junior Member
      • Aug 2009
      • 8

      #3
      Assuming I string a bunch of panels together in series and the string voltage is 1000V would there be a problem finding components that are rated (wire, combiners, inverters, fuses...) at 1000V?

      Comment

      • Mike90250
        Moderator
        • May 2009
        • 16020

        #4
        Originally posted by JTSOLAR
        Assuming I string a bunch of panels together in series and the string voltage is 1000V would there be a problem finding components that are rated (wire, combiners, inverters, fuses...) at 1000V?
        Well, maybe, they are available, but expensive. I don't know of any inverters that need more than 500V to run, so, it's all theory so far.
        Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
        || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
        || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

        solar: http://tinyurl.com/LMR-Solar
        gen: http://tinyurl.com/LMR-Lister

        Comment

        • DaveC
          Junior Member
          • Aug 2009
          • 6

          #5
          I'm not sure if you need to follow NEC up there in Canada, but Article 690.7 (C) limits most residential PV systems to 600V.
          - Dave

          Comment

          • lile001
            Solar Fanatic
            • Feb 2010
            • 105

            #6
            wire - rated voltage

            Originally posted by DaveC
            I'm not sure if you need to follow NEC up there in Canada, but Article 690.7 (C) limits most residential PV systems to 600V.
            Residential wire is rated to 600V in most cases - stick with that, the high voltage wire is unneccesary and very expensive.
            Lawrence Lile, PE

            Comment

            • livewire1
              Junior Member
              • Feb 2010
              • 12

              #7
              What is the advantage of lets say your array producing 240V or 440V? Why is 440V better? Thanks Dave
              Smart Meters are Smart, but if you know how to outsmart them. Well its still all good!

              Comment

              • Sunking
                Solar Fanatic
                • Feb 2010
                • 23301

                #8
                Originally posted by livewire1
                What is the advantage of lets say your array producing 240V or 440V? Why is 440V better? Thanks Dave
                Simple less current for a given amount of wattage.

                Both Canada and USA limits the voltage to 600 volts. However no system is designed to go that high. Solar panels have a negative temperature coefficient which means the colder it gets the higher the voltage the panel produce. So in colder climates you have to use lower voltages as not to exceed the maximum Voc rating.

                Just about all inverter used in grid tied systems have a maximum Voc input of 500 and some 600 volts. That means running maximum of about 375 to 480 volts on the panels @ 25 C depending on the inverter inputs
                MSEE, PE

                Comment

                • livewire1
                  Junior Member
                  • Feb 2010
                  • 12

                  #9
                  So the higher the VOC on your panels, the better. Right? Ive seen them from 22 to 44 VOC. What would be the best all around panel? I have a Fronius 2500LV. When looking for panels, what are the things to look for when it comes to a good grid tie panel. Thanks
                  Smart Meters are Smart, but if you know how to outsmart them. Well its still all good!

                  Comment

                  • Sunking
                    Solar Fanatic
                    • Feb 2010
                    • 23301

                    #10
                    Originally posted by livewire1
                    So the higher the VOC on your panels, the better. Right?
                    Correct.

                    Originally posted by livewire1
                    Ive seen them from 22 to 44 VOC. What would be the best all around panel?
                    That question is not so easily answered as it depends a bit on your location and temperature coefficient correction factor, how large the system will be in wattage, how many strings will be used, and future expansions. Its a puzzle you have to fit together once you know what the objective is.

                    For example if it is a small system of say 2000 watts in a warm climate, I may select a 185 watt panel and a VOC of 36 volts and string 12 panels together in series for a single string to make a 430 string at 75 degrees and leaves me plenty of wiggle room when it gets cold as not to exceed a 500 volt input limit on an inverter.

                    Where as in a colder climate on a fairly large system like 6000 watts with room to expand to 10,000 I may choose 200 watt panels with a Voc of 44 volts, and string 10 of them in series for a 2000 watt string, and select an inverter with a 600 volt max input.

                    It is all about component selection and matching the puzzle pieces up to fit.
                    MSEE, PE

                    Comment

                    • lile001
                      Solar Fanatic
                      • Feb 2010
                      • 105

                      #11
                      Originally posted by livewire1
                      What is the advantage of lets say your array producing 240V or 440V? Why is 440V better? Thanks Dave
                      Some inverters, such as the Sunny Boy, can operate at thier peak efficiency at voltages in the 200-400 volt range. Since they are making 240 volts AC, they don't have to work as hard to boost the DC voltage to make AC.

                      Now, high voltages are better only up to a point. Beyond 600V, the wire gets expensive. Beyond 500V, you start to run out of safety factor (NEC 690 requires your wire to be rated about 125% of the peak open-circuit voltage of your panel string, depending on local temperature extremes.)

                      There is a big difference in wire size, and expense, between 24V and 240V. Wire is ten times smaller, therefore ten times cheaper and easier to route!
                      Lawrence Lile, PE

                      Comment

                      • livewire1
                        Junior Member
                        • Feb 2010
                        • 12

                        #12
                        Ok... Sounds great, I appreciate the info.
                        Smart Meters are Smart, but if you know how to outsmart them. Well its still all good!

                        Comment

                        • Richie
                          Junior Member
                          • Apr 2013
                          • 1

                          #13
                          High Input Voltage Charge Controller

                          Good Day Everyone,

                          Would you please advise me a battery charge controller which works together with a solar panel has the following parameters: 319 V (!) 0.288 A (92W).

                          Solar panel's source:


                          Cheers,
                          Richie

                          Comment

                          • inetdog
                            Super Moderator
                            • May 2012
                            • 9909

                            #14
                            Originally posted by Richie
                            Good Day Everyone,

                            Would you please advise me a battery charge controller which works together with a solar panel has the following parameters: 319 V (!) 0.288 A (92W).

                            Solar panel's source:


                            Cheers,
                            Richie
                            You can easily find a grid tie inverter that will accept that panel voltage, but I do not know of a solar CC which is designed for that high an input voltage.
                            SunnyBoy 3000 US, 18 BP Solar 175B panels.

                            Comment

                            • SunEagle
                              Super Moderator
                              • Oct 2012
                              • 15124

                              #15
                              Originally posted by inetdog
                              You can easily find a grid tie inverter that will accept that panel voltage, but I do not know of a solar CC which is designed for that high an input voltage.
                              I wonder what the intent was to build a panel with such a high output voltage? Do you think they were going to some type of industrial use?

                              Comment