Hi all!
My first post as a forum member so be kind...my question is regarding a solar installation that has mismatched solar panel voltages tied together at a panel combiner. Here's the details:
I'm helping out at a NP facility that has a 20KW solar array using several MPPT charge controllers each with a Vmax of 150 volts.
There are five arrays, each with eight rows of seven 75 watt, 17v panels tied in series. Each row is connected to a combiner with an appropriate circuit breaker.
The rated outputs of the panel array is 152 v at 25 C. This is more than the Vmax of the charge controllers. Worse, when the Voc is calculated at 0 C, the Vmax jumps to 170 V.
Apparently a solar tech had tried to deal with the Vmax issue by taking one panel out of the series connection in each array. That is to say that there were seven rows of panels with a Voc of 152 v, and one row of six panels with a Voc of 130 V. All eight rows of panels are fed to a combiner where the panels are paralleled together prior to being fed to the charge controller.
This wiring method did serve to bring down the overall voltage from the combiner to the charge controller to about 147.8 volts Voc at 15 C, but it puts it above the Vmax for the charge controller when the temperature drops as it has in the last few weeks.
I'm proposing to change the wiring for the panels so that only six panels will be connected in series, then reconnecting the "extra" panels back into the array by adding more circuits to the combiners. My net change will be the voltage from the array will be less, but the amps should actually increase so the overall output from the solar array will not change dramatically.
I've tried to find information about the mismatching voltage connection between the rows of solar panels, but haven't found a definitive answer on what happens when this is done. To put it the best way I know, assume that there are seven 17 V panels wired in series, parallel wired to six 17 V panels wired in series. Seems to me that the six panels would somehow be damaged by the extra voltage generated by the seven panels.
Sorry for the long post, but hopefully I've stated the problem properly.
Thanks in advance for your thoughts, advice and opinions.
My first post as a forum member so be kind...my question is regarding a solar installation that has mismatched solar panel voltages tied together at a panel combiner. Here's the details:
I'm helping out at a NP facility that has a 20KW solar array using several MPPT charge controllers each with a Vmax of 150 volts.
There are five arrays, each with eight rows of seven 75 watt, 17v panels tied in series. Each row is connected to a combiner with an appropriate circuit breaker.
The rated outputs of the panel array is 152 v at 25 C. This is more than the Vmax of the charge controllers. Worse, when the Voc is calculated at 0 C, the Vmax jumps to 170 V.
Apparently a solar tech had tried to deal with the Vmax issue by taking one panel out of the series connection in each array. That is to say that there were seven rows of panels with a Voc of 152 v, and one row of six panels with a Voc of 130 V. All eight rows of panels are fed to a combiner where the panels are paralleled together prior to being fed to the charge controller.
This wiring method did serve to bring down the overall voltage from the combiner to the charge controller to about 147.8 volts Voc at 15 C, but it puts it above the Vmax for the charge controller when the temperature drops as it has in the last few weeks.
I'm proposing to change the wiring for the panels so that only six panels will be connected in series, then reconnecting the "extra" panels back into the array by adding more circuits to the combiners. My net change will be the voltage from the array will be less, but the amps should actually increase so the overall output from the solar array will not change dramatically.
I've tried to find information about the mismatching voltage connection between the rows of solar panels, but haven't found a definitive answer on what happens when this is done. To put it the best way I know, assume that there are seven 17 V panels wired in series, parallel wired to six 17 V panels wired in series. Seems to me that the six panels would somehow be damaged by the extra voltage generated by the seven panels.
Sorry for the long post, but hopefully I've stated the problem properly.
Thanks in advance for your thoughts, advice and opinions.