Solar Panel Installation on Tar and Gravel Roof

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • Jaxx
    Member
    • Jan 2012
    • 31

    #1

    Solar Panel Installation on Tar and Gravel Roof

    Hello fellow solar fans

    I am planning on installing a 2.2 KW micro-inverter system with 10 panels on a low slope tar and gravel roof.

    The roof is built up as shown on attached picture. There is no attic and the rafters are exposed on the inside of the house (vaulted ceilings).

    I'm currently looking for advice on how to mount the solar panel racking to the roof. Has anyone here done such an installation or has knowledge about how to do this? What hardware would I need?

    Could I:

    -Drill pilot holes through the particle board into the 4x6 rafters
    -Open up hole size on the top portion down to the rafter (reason -> see 3 items further down)
    -Put polyurethane into the hole
    -Install standoff bolts
    -Fill top of holes with roof patch/caulk
    -Install flashing?
    -Mount racking to standoff bolts with roughly 3-4 inches of clearance between panels and roof surface

    Is this a good plan? How could it be improved?

    Thanks a lot in advance for your help!
    Attached Files
  • Mike90250
    Moderator
    • May 2009
    • 16020

    #2
    I{ think you need to get an engineer on this, as to how many & what size, holes you can punch into the beams. Generally, roof/ceilings are separate, and have sort of a "stick built truss" system. But you are adding weight, putting holes in the main support members, and till the span, loads, and perforations are calculated, I've got no idea if it's going to be safe or not.
    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister

    Comment

    • Jaxx
      Member
      • Jan 2012
      • 31

      #3
      What kind of engineer would this be?

      Comment

      • Mike90250
        Moderator
        • May 2009
        • 16020

        #4
        Originally posted by Jaxx
        What kind of engineer would this be?
        Structural engineer, for housing.
        Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
        || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
        || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

        solar: http://tinyurl.com/LMR-Solar
        gen: http://tinyurl.com/LMR-Lister

        Comment

        • Naptown
          Solar Fanatic
          • Feb 2011
          • 6880

          #5
          That is how it is done on 99% of installations. You could use a flashing and set that in roof cement but a good polyurethane sealant in the hole and the L foot bedded into the sealant will last a very long time (20+ years on average)
          Just make sure the L on the mounting bracket is pointed downhill This keeps water running down the roof from flowing up and over the bolt which will be the weak point as the sealant will be exposed. Some good quality paint over the sealant will help with UV protection also.
          Depending on the spacing on your rafters try to spread the attachment points out. For example on a horizontal row of modules with the racking running perpendicular to the rafters and the rafters on 24" centers on the bottom rail attach at the ends and every other rafter between. On the next rail up attach at the ends and every other rafter but attach to the rafters that the first row was NOT bolted to. This spreads the weight out.
          For the most part a solar array flush to the roof doesn't need much more engineering than what the racking manufacturer reccomends. The array doesn't add much more than 3 -3 1/2 pounds per square foot to the dead loading or downward wind loading. It will however add to uplift so following the racking instructions is important.
          You will need to check with your local AHJ however to see what their requirements are. Some require engineering and some do not.
          NABCEP certified Technical Sales Professional

          [URL="http://www.solarpaneltalk.com/showthread.php?5334-Solar-Off-Grid-Battery-Design"]http://www.solarpaneltalk.com/showth...Battery-Design[/URL]

          [URL]http://www.calculator.net/voltage-drop-calculator.html[/URL] (Voltage drop Calculator among others)

          [URL="http://www.gaisma.com"]www.gaisma.com[/URL]

          Comment

          • Jaxx
            Member
            • Jan 2012
            • 31

            #6
            Thank you for your detailed response.

            Would L-brackets sit on the surface of the roof? I'm asking this because the 2" board that sits on the rafters is made of compressed wood fibers (similar to sound board that is used on walls for sound proofing). I don't expect this to be very structurally sound. I thought of an anchoring method where a long bolt is driven into the rafter which has coarse thread on the bottom half to go into the wood and then a regular fine thread at the top half to accept nuts. I would then mount the racking with standoff from the roof and would hold it in place with nuts (racking sandwiched between nuts). Would this work?

            Comment

            • Naptown
              Solar Fanatic
              • Feb 2011
              • 6880

              #7
              Originally posted by Jaxx
              Thank you for your detailed response.

              Would L-brackets sit on the surface of the roof? I'm asking this because the 2" board that sits on the rafters is made of compressed wood fibers (similar to sound board that is used on walls for sound proofing). I don't expect this to be very structurally sound. I thought of an anchoring method where a long bolt is driven into the rafter which has coarse thread on the bottom half to go into the wood and then a regular fine thread at the top half to accept nuts. I would then mount the racking with standoff from the roof and would hold it in place with nuts (racking sandwiched between nuts). Would this work?
              There are some flashing systems that are similar to that. I can't remember the name of them right now.
              You may want to take a look at Eco fasten flashing systems they may have something that works.
              NABCEP certified Technical Sales Professional

              [URL="http://www.solarpaneltalk.com/showthread.php?5334-Solar-Off-Grid-Battery-Design"]http://www.solarpaneltalk.com/showth...Battery-Design[/URL]

              [URL]http://www.calculator.net/voltage-drop-calculator.html[/URL] (Voltage drop Calculator among others)

              [URL="http://www.gaisma.com"]www.gaisma.com[/URL]

              Comment

              • russ
                Solar Fanatic
                • Jul 2009
                • 10360

                #8
                Originally posted by Jaxx
                Thank you for your detailed response.

                Would L-brackets sit on the surface of the roof? I'm asking this because the 2" board that sits on the rafters is made of compressed wood fibers (similar to sound board that is used on walls for sound proofing). I don't expect this to be very structurally sound. I thought of an anchoring method where a long bolt is driven into the rafter which has coarse thread on the bottom half to go into the wood and then a regular fine thread at the top half to accept nuts. I would then mount the racking with standoff from the roof and would hold it in place with nuts (racking sandwiched between nuts). Would this work?
                Just needs the loving examination of a structual engineer - you don't want to weaken the trusses too much.
                [SIGPIC][/SIGPIC]

                Comment

                • Jaxx
                  Member
                  • Jan 2012
                  • 31

                  #9
                  Thank you!

                  What would you expect this service to run at, cost-wise?

                  Thanks

                  Comment

                  • Mike90250
                    Moderator
                    • May 2009
                    • 16020

                    #10
                    Originally posted by Jaxx
                    Thank you!

                    What would you expect this service to run at, cost-wise?

                    Thanks
                    I just paid $1200 for an entire house set of plans. but everything was blueprints. Something already built will have to have a person on the engineers staff, verify the wood, size & spacing, and it might be $300- 800
                    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                    solar: http://tinyurl.com/LMR-Solar
                    gen: http://tinyurl.com/LMR-Lister

                    Comment

                    • Naptown
                      Solar Fanatic
                      • Feb 2011
                      • 6880

                      #11
                      Originally posted by Mike90250
                      I just paid $1200 for an entire house set of plans. but everything was blueprints. Something already built will have to have a person on the engineers staff, verify the wood, size & spacing, and it might be $300- 800
                      And many jurisdictions have engineers on staff as plan reviewers. In which case an engineer may not be required. Many of the racking manufacturers have already done the engineering on the various systems and are willing to provide it at no cost.
                      If the house was built and inspected the roof engineering has already been done as prescribed by code at the time. Live and dead loads have already been established.
                      Average engineering cost for this in Maryland is about $500.00 Generally it is unnecessary and only required in a few locations. Most jurisdictions will accept the engineering done by the manufacturer.
                      Check with your local building department before spending your money on an engineer. Tens of thousands of these have been installed without an engineers stamp. I have not heard of a single structural failure on a roof built to code and the loads required to be supported.
                      NABCEP certified Technical Sales Professional

                      [URL="http://www.solarpaneltalk.com/showthread.php?5334-Solar-Off-Grid-Battery-Design"]http://www.solarpaneltalk.com/showth...Battery-Design[/URL]

                      [URL]http://www.calculator.net/voltage-drop-calculator.html[/URL] (Voltage drop Calculator among others)

                      [URL="http://www.gaisma.com"]www.gaisma.com[/URL]

                      Comment

                      • amira12
                        Junior Member
                        • Apr 2012
                        • 4

                        #12
                        Solar Panel Installation on Tar and Gravel Roof

                        Yes this is possible . I have seen Many pics where solar panels are installed on Gravel Roof , as well they are working well .
                        [No advertising in signatures.]

                        Comment

                        • Jaxx
                          Member
                          • Jan 2012
                          • 31

                          #13
                          Originally posted by amira12
                          Yes this is possible . I have seen Many pics where solar panels are installed on Gravel Roof , as well they are working well .
                          Would you have some pictures that show installations on tar and gravel? Maybe even some closeups?

                          Thanks!

                          Comment

                          • Itsme
                            Member
                            • Jan 2014
                            • 37

                            #14
                            Originally posted by Jaxx
                            Would you have some pictures that show installations on tar and gravel? Maybe even some closeups?

                            Thanks!
                            Jaxx, how did your project turn out? My wife's school has a similar roof, and are considering Solar. So your experience would be a great case study for them

                            Many thanks

                            Comment