    Inverter question - DC inputs vs Strings?

    Dear all,

    I am a little confused regarding DC inputs on inverters and strings that an inverter can take. For example, I have a Fronius IG 3.6 here which has 6 DC inputs, but does that mean I would be able to run 6 different strings to combat shading problems? From my understanding, 6 strings would allow me to have 6 arrays on 6 different roof aspects, is that correct? Or does somebody have a good website describing strings and the DC input differences?

    Help would be much appreciated.

    A
  • Mike90250
    Moderator
    • May 2009
    • 16020

    #2
    The keyword to look for , is Independent MPPT , otherwise, they are just parallel terminals. (you can verify with ohm meter before you connect any power, or connect 1 array, and try to measure voltage on the other 5. I think you will discover they are "combiners" and not independent.)

    I know of no controller with 6 MPPT channels. I've heard there is one with 2 MPPT channels.
    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister

    Comment

    • themightykc
      Junior Member
      • Aug 2011
      • 3

      #3
      Thanks Mike,

      Just had a look at an SMA SB 2500 HF and the inverter itself has 1 MPPT tracker but 2 strings. Is that possible? And if so, could I have the solar modules on two different roof aspects and how would this affect shading? (sorry for all the questions!)

      Cheers,

      A

      Comment

      • Mike90250
        Moderator
        • May 2009
        • 16020

        #4
        Each MPPT tracker, can only manage cells/panels that are the same, and aimed in the same direction. If you mix arrays, it will "hunt" between them, with less than good results. Just having 2 or more sets of screw terminals, does not make MPPT magic happen.
        Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
        || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
        || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

        solar: http://tinyurl.com/LMR-Solar
        gen: http://tinyurl.com/LMR-Lister

        Comment

        • themightykc
          Junior Member
          • Aug 2011
          • 3

          #5
          Cheers Mike,

          Thanks for the help, much appreciated.

          A