Grounding Clips and DC Isolation faults

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • Oliver84
    Junior Member
    • Oct 2013
    • 17

    Grounding Clips and DC Isolation faults

    We've been having an issue for a while with DC Isolation faults. It happens mostly when it rains and won't clear up until it's had a few good dry days. But also some mornings (maybe because of dew?) we'll get DC Isolation faults. We've tried everything to isolation where the problem is and have replaced both inverters already but the system still persists. One thing I noticed is that when the system was reinstalled, many of the Unirac Grounding Clips were missing. I know these are important, but could they be the cause of these DC Isolation faults?
  • bcroe
    Solar Fanatic
    • Jan 2012
    • 5198

    #2
    I very much doubt the grounding clips have anything to do with ground
    current leakage. Check out the integrity of the wiring. Do you know how
    much leakage current flows? How is your array configured?

    In my string inverter cas,e I would unplug BOTH leads of a string and see
    if the leakage goes away. To test a disconnected string, under sun see if
    any power can be drawn from either end to ground (which must flow thru
    a ground fault. I use this test setup to detect current of a fraction of an amp,
    4 bulbs in series handle my 400VDC system. If the current is much less,
    use a plain old voltmeter. BUT a very high impedance meter, esp a digital
    type, will be too sensitive to static charges. SO put a resistor to draw maybe
    0.1A, IN PARALLEL with the volt meter leads to drain off static and show
    real flow. good luck, Bruce Roe

    PVtestLt.JPG


    Comment

    • SunEagle
      Super Moderator
      • Oct 2012
      • 15125

      #3
      Bruce. I really like your tester but you might have to provide a circuit diagram to those people that want to build one but don't really know how.

      Comment

      • Oliver84
        Junior Member
        • Oct 2013
        • 17

        #4
        The wiring has been replaced and we're still having the issue. Weird thing is that it's not all the time. Is that normal? When it's dry, it works perfectly fine. But if we have a bad storm or there's a lot of moisture, then we get the faults.

        I have 2 inverters, each one hooked up to 20 panels with optimizers at each panel. At first I had each 20 panel set on 1 string but then we broke it out to 2 strings thinking that might have been the issue. But we're still getting these faults even with 2 strings and new wires. Trying to figure out the best way to isolate the problem but it's complicated because on days that are great to work on it, I don't get any faults. Any thoughts on how water would affect the current leakage?

        Comment

        • Mike90250
          Moderator
          • May 2009
          • 16020

          #5
          Water will affect current leakage. You could have one bad panel. I don't know if you have a combiner box you can use to disconnect array sections.

          BE VERY careful if there is light. PV panels in a string can generate 100's of volts and quickly ruin a MC4 connector if it's connected/disconnected live. And that high
          voltage can also make you un-alive quickly
          Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
          || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
          || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

          solar: http://tinyurl.com/LMR-Solar
          gen: http://tinyurl.com/LMR-Lister

          Comment

          • bcroe
            Solar Fanatic
            • Jan 2012
            • 5198

            #6
            Originally posted by SunEagle
            Bruce. I really like your tester but you might have to provide a circuit diagram to those people that want to build one but don't really know how.
            Enough light bulbs wired in series to withstand the array voltage is not much.

            I FORGOT TO SAY, I only connect/disconnect panel wiring in the dark, under
            a work light. Plug the MC4s with dummys (latches ground off), then connect
            a meter under the sun. Even those bulbs draw a nice arc. Bruce Roe

            Comment

            • Mike 134
              Solar Fanatic
              • Jan 2022
              • 385

              #7
              Originally posted by Oliver84
              The wiring has been replaced and we're still having the issue. Weird thing is that it's not all the time. Is that normal? When it's dry, it works perfectly fine. But if we have a bad storm or there's a lot of moisture, then we get the faults.

              I have 2 inverters, each one hooked up to 20 panels with optimizers at each panel. At first I had each 20 panel set on 1 string but then we broke it out to 2 strings thinking that might have been the issue. But we're still getting these faults even with 2 strings and new wires. Trying to figure out the best way to isolate the problem but it's complicated because on days that are great to work on it, I don't get any faults. Any thoughts on how water would affect the current leakage?
              You mentioned optimizers I'm guessing Solar Edge? They use the brand Multi Contact for their connectors that is now owned by Staubli . What brand are the connectors from the modules? Solar Edge has posted on their tech pages that "compatible" connectors can cause ground fault problems. They recommend all connectors be of the same manufacturer or have been tested and certified by a 3rd party to be compatible
              Last edited by Mike 134; 04-14-2022, 07:15 AM.

              Comment

              • Oliver84
                Junior Member
                • Oct 2013
                • 17

                #8
                Originally posted by Mike 134

                You mentioned optimizers I'm guessing Solar Edge? They use the brand Multi Contact for their connectors that is now owned by Staubli . What brand are the connectors from the modules? Solar Edge has posted on their tech pages that "compatible" connectors can cause ground fault problems. They recommend all connectors be of the same manufacturer or have been tested and certified by a 3rd party to be compatible
                Oh man, we've replaced a bunch of the connectors as well. This problem is so crazy because I've been told it could be literally any part of the system. One tech told me it was the inverters. So we replaced both inverters and that wasn't it. Then it was the wires, we ran new wiring and split the strings. That wasn't it. We replaced a bunch of the connectors, still not it. They suggested it could be bad optimizers (no idea which ones) or bad modules. That's pretty much every aspect of the system.

                Comment

                • Mike 134
                  Solar Fanatic
                  • Jan 2022
                  • 385

                  #9
                  Originally posted by Oliver84

                  Oh man, we've replaced a bunch of the connectors as well. This problem is so crazy because I've been told it could be literally any part of the system. One tech told me it was the inverters. So we replaced both inverters and that wasn't it. Then it was the wires, we ran new wiring and split the strings. That wasn't it. We replaced a bunch of the connectors, still not it. They suggested it could be bad optimizers (no idea which ones) or bad modules. That's pretty much every aspect of the system.
                  those new connectors you put on have MC stamped into them? connector1.JPG

                  Comment

                  • Oliver84
                    Junior Member
                    • Oct 2013
                    • 17

                    #10
                    I'll need to check, that was another installer that gave up on this job. I'm thinking I will try with the process of elimination now and see if I can narrow down where the problem is. Try just 1 string of 10, then add another string of 10, etc until I start seeing some faults again. Hopefully this will help me at least narrow down the problem to a single string of 10 and then I can work from there.

                    Comment

                    • oregon_phil
                      Solar Fanatic
                      • Jan 2019
                      • 496

                      #11
                      Oliver84 , it was implied that you have a Solar Edge system. Solar Edge has an app note for isolation fault detection. Whether or not the procedure works, I have no idea.
                      Attached Files

                      Comment

                      • Mike 134
                        Solar Fanatic
                        • Jan 2022
                        • 385

                        #12
                        Originally posted by oregon_phil
                        Oliver84 , it was implied that you have a Solar Edge system. Solar Edge has an app note for isolation fault detection. Whether or not the procedure works, I have no idea.
                        That's handy to have just in case.........

                        Comment

                        • Oliver84
                          Junior Member
                          • Oct 2013
                          • 17

                          #13
                          Thank you, the setApp doesn't work with my inverters even though they're solarEdge but I have done the same thing on the inverter itself. You can go into the maintenance menu and look at the DC Isolation Diagnostics menu and it'll help you locate the string. However, we've never been able to find this to be accurate. We've had probably 5 or 6 other technicians out here trying to find this "leak" and nobody's been able to find it yet. I'm in South Florida and apparently there aren't any recommended SolarEdge contractors out here to help.

                          I believe we may have isolated the problem within 8 panels. I have 32 that seem to be working but we would need a good rain storm to be sure. I'll post an update after we get some rain and see if the faults come back.