    So, after messing around too much trying to get present under-powered system to function reliably, I decided to add 3 270w panels that I had lying around. I also have an Epever 3210 on hand. Problem is they're not compatible. Epever has an input limit of 100v and open circuit for panels - in series - is 115v.

    I'd really like to use what I have on hand, so, question 1: If I parallel the 3 panels would 31v be enough to drive Epever for 24v bank? (I don't think so)
    Question 2: If not, is the solution to buy a PWN instead? Or... anyone know of a cheap MPPT that works at 125vdc?

    No shading or wiring issues, the latter is already established. My goal is to add an extra 20~ amps to system, a 30% increase.

    Thanks
  • SunEagle
    Super Moderator
    • Oct 2012
    • 15208

    #2
    An odd number of panels can be a big problem with an off grid system. I would think getting a 4th 270w panel and wire them 2S2P to the charge controller should work if you do not exceed any of the Max input values.

    If you go with a PWM type CC you will lose at least 33% of the panel wattage for charging. Remember PWM is Amps in = Amps out. You will also need some type of combiner box once you exceed 2 parallel panels.

    Comment

    • -robw-
      Member
      • Sep 2019
      • 78

      #3
      Yes, sir, exactly what I'm undertaking right now. Epever also limits total wattage at 880, but 1pm, clear blue sky and 80 degrees is only supporting 60x8, or 240w/panel (only 2 panels connected) instead of panel rating of 270w. So I waste 80w with 2x2 but still seems to be best solution.

      That 240 is also about the best they'll do because they're mounted flat. Perfect for summer (when they're needed) but otherwise not tilted properly.

      Comment

      • SunEagle
        Super Moderator
        • Oct 2012
        • 15208

        #4
        With the panels laying flat you may get only 80% output which seems a waste but if you are ok with that then fine.

        If you want to use more panels then you will need to increase the CC size to say 60amps or arrange the panels with half pointing to the East and the other half pointing to the West. This will allow you to charge during more of the day without exceeding the input wattage of your CC

        Comment

        • -robw-
          Member
          • Sep 2019
          • 78

          #5
          Agreed, but the extra power is just to help handle AC season when almost dead flat is best here. The rest of the year they'll help treat batteries better, I guess, but that's it.

          Thanks for confirming.

          Comment

          • -robw-
            Member
            • Sep 2019
            • 78

            #6
            Originally posted by SunEagle
            With the panels laying flat you may get only 80% output which seems a waste but if you are ok with that then fine.

            If you want to use more panels then you will need to increase the CC size to say 60amps or arrange the panels with half pointing to the East and the other half pointing to the West. This will allow you to charge during more of the day without exceeding the input wattage of your CC
            So adding to system appears to be almost a total waste of time. Whereas before my Classic 150 would consistently (on cloudless days) generate 9kWh for day, now it only generates 7kWh, leaving the other 2 kWh to the Epever 3210. Apparently, my battery bank will only accept 50-60a @ bulk. This is very disheartening, especially given how many tech's had told me, "sorry, you're too light on PV. Nothing I can suggest except adding more". I always disagreed too. 1800wh PV for a 610ah bank seemed just fine for my location.

            Question, if you would: Spec sheet for CR-305 indicates "Max. Charge Current (48V)" is 100 Adc. Does that mean Max charge at 24v is half of that, or 50Adc?

            2x4 CR-305, equalized every 2 weeks
            6 awg wiring from CC to bank, 2/0 serial cabling
            Battery temp @ 29.2C
            Both controllers calibrated for 29.1v absorb for 5 hours (cause 3 hrs didn't work)

            I don't think I am, but am I missing anything?

            Comment

            • SunEagle
              Super Moderator
              • Oct 2012
              • 15208

              #7
              Originally posted by -robw-

              So adding to system appears to be almost a total waste of time. Whereas before my Classic 150 would consistently (on cloudless days) generate 9kWh for day, now it only generates 7kWh, leaving the other 2 kWh to the Epever 3210. Apparently, my battery bank will only accept 50-60a @ bulk. This is very disheartening, especially given how many tech's had told me, "sorry, you're too light on PV. Nothing I can suggest except adding more". I always disagreed too. 1800wh PV for a 610ah bank seemed just fine for my location.

              Question, if you would: Spec sheet for CR-305 indicates "Max. Charge Current (48V)" is 100 Adc. Does that mean Max charge at 24v is half of that, or 50Adc?

              2x4 CR-305, equalized every 2 weeks
              6 awg wiring from CC to bank, 2/0 serial cabling
              Battery temp @ 29.2C
              Both controllers calibrated for 29.1v absorb for 5 hours (cause 3 hrs didn't work)

              I don't think I am, but am I missing anything?
              Again. With a 610Ah battery system you need about 60 amps of charging. That Epever 3210 is only a 30amp CC. While your panel system may deliver more amps while the sun shines the CC will max out at 30amps and not provide what a 610Ah system needs.

              So what is your total panel wattage and how it is wired to the CC and what is their Vmp rating?

              Remember that Epever 3210 is only rated 780watt for a 24V battery system but it still can only provide 30amps of charging which is not enough for a 610Ah battery system no matter what the voltage is. If you are using 2 of those 3210 type they may work together on the same battery system or they may fight each other depending on if they communicate with each other.

              If you have a Classic 150 why do you need the Epever CC?
              Last edited by SunEagle; 08-11-2020, 12:36 PM. Reason: added last sentence

              Comment

              • -robw-
                Member
                • Sep 2019
                • 78

                #8
                Primary system is 1800w PV connected to Classic 150
                Secondary (just added) system is 1080w PV connected to Epever 3210

                Both connected to 2x4 CR-305's.

                I used the Epever because I was told that because the wattage of secondary panels (270w) is higher than primary panels (180w) I could not tie both into same controller.

                Comment

                • SunEagle
                  Super Moderator
                  • Oct 2012
                  • 15208

                  #9
                  Originally posted by -robw-
                  Primary system is 1800w PV connected to Classic 150
                  Secondary (just added) system is 1080w PV connected to Epever 3210

                  Both connected to 2x4 CR-305's.

                  I used the Epever because I was told that because the wattage of secondary panels (270w) is higher than primary panels (180w) I could not tie both into same controller.
                  What is strange is that 1800watts should deliver over 60amps into a 24V battery system. Those 8 CR305 wired 2Px4S create a 610Ah 24V system which should match up to that Classic 150 just fine.

                  My first concern is having a second pv charging system connected to the same batteries.
                  My second concern is having 1080w connected to the Epever 3210 which exceeds it's max watt input by close to 300watts. Unless you point the panels in different directions you could overload the Epever.

                  Comment

                  • -robw-
                    Member
                    • Sep 2019
                    • 78

                    #10
                    Originally posted by SunEagle

                    What is strange is that 1800watts should deliver over 60amps into a 24V battery system. Those 8 CR305 wired 2Px4S create a 610Ah 24V system which should match up to that Classic 150 just fine.

                    My first concern is having a second pv charging system connected to the same batteries.
                    My second concern is having 1080w connected to the Epever 3210 which exceeds it's max watt input by close to 300watts. Unless you point the panels in different directions you could overload the Epever.
                    Agreed, hence my bitch: "This is very disheartening, especially given how many tech's had told me, "Sorry, you're too light on PV. Nothing I can suggest except adding more""

                    62 amps is 'recommended' charge current per Crown (20% of 310), but if max current rate is 100a I should be able to go higher if situation demanded. I thought I could, and with so many tech's recommending more PV, I figured they did too. Problem is, although I have double and triple checked resistance factors, batteries won't accept more than that 62a.

                    That doesn't seem right unless max current rate of these Crown 305's is not 100a.

                    Comment

                    • -robw-
                      Member
                      • Sep 2019
                      • 78

                      #11
                      Site is not allowing me to edit my post so a couple of post-edits:

                      1) I was responding to "What is strange is that 1800watts should deliver over 60amps into a 24V battery system"
                      2) Max PV for 3210 is 1170w, although max charge current is 780. We both acknowledged I would be wasting some wattage but doing so was a compromise.

                      Why is the 2nd controller a concern? afaik, it was the only way I could wattage to system, short of purchasing another Classic 150.

                      Comment

                      • sdold
                        Moderator
                        • Jun 2014
                        • 1490

                        #12
                        Sorry about the post problems, the site tries to figure out who is a spammer based on their behavior and I guess something you did, maybe editing a couple of times, gave it a false positive. It puts it into a moderation status, but we'll try to fix it quickly when we see that it has happened. --Steve

                        Comment

                        • SunEagle
                          Super Moderator
                          • Oct 2012
                          • 15208

                          #13
                          Originally posted by -robw-
                          Site is not allowing me to edit my post so a couple of post-edits:

                          1) I was responding to "What is strange is that 1800watts should deliver over 60amps into a 24V battery system"
                          2) Max PV for 3210 is 1170w, although max charge current is 780. We both acknowledged I would be wasting some wattage but doing so was a compromise.

                          Why is the 2nd controller a concern? afaik, it was the only way I could wattage to system, short of purchasing another Classic 150.
                          Sorry you are having issues posting. Steve should be able to get it under control

                          The reason I am concerned with a second CC connected to the same battery system is that in the past unless the two CC can communicate with each other they can fight each other.

                          Maybe the Classic will take over as the lead charger with the Epever doing the rest but if the battery system is up to a specific voltage a second CC will think all it done and not provide any additional charging amps.

                          The Classic should be able to provide up to 96amps but I do not have hands on experience to know how much wattage that requires for a 24V systems without exceeding its 150VDC input rating.

                          The batteries should be able to handle a C/8 charge rate which would be about 76amps. Maybe the Classic is not set up correctly to continue to charge even with enough panel wattage.

                          Also even though you may have 1800 watts connected to the Classic the panels may not be optimumly pointed to generate full output.

                          Comment

                          • -robw-
                            Member
                            • Sep 2019
                            • 78

                            #14
                            Originally posted by sdold
                            Sorry about the post problems, the site tries to figure out who is a spammer based on their behavior and I guess something you did, maybe editing a couple of times, gave it a false positive. It puts it into a moderation status, but we'll try to fix it quickly when we see that it has happened. --Steve
                            It's all good. If you're curious as to what I did: 1) sent reply 2) edited to add quoting of Suneagle's response 3) tried re-editing to embolden a statement by Suneagle.

                            Originally posted by SunEagle
                            The reason I am concerned with a second CC connected to the same battery system is that in the past unless the two CC can communicate with each other they can fight each other.

                            Maybe the Classic will take over as the lead charger with the Epever doing the rest but if the battery system is up to a specific voltage a second CC will think all it done and not provide any additional charging amps.

                            The Classic should be able to provide up to 96amps but I do not have hands on experience to know how much wattage that requires for a 24V systems without exceeding its 150VDC input rating.

                            The batteries should be able to handle a C/8 charge rate which would be about 76amps. Maybe the Classic is not set up correctly to continue to charge even with enough panel wattage.

                            Also even though you may have 1800 watts connected to the Classic the panels may not be optimumly pointed to generate full output.
                            Classic does take over as lead charger, and Epever isn't terrible in backup role. For example, my larger system has 2 FM-80's and where I would rather each supply current 50-50, instead one always drops off later in the absorb cycle as "charged". So, right now one of them is supplying 40+ amps while the other is "charged" - not supplying anything. At least the Epever is supplying 1 amps right now while Classic is supplying 11.5a.

                            Thanks for the 76a rate. I was looking for that all morning because Crown had no idea.

                            As far as panel tilt, they're perfect for this time of year at 13 degrees. As far as Classic config, not only have I spent the past month talking with techs at Crown, Midnite Solar, Epever, and the people I bought equipment from, trying to solve SG issue, but I can't imagine what setting besides "max output amperage" (set at 80a) would control this. I have played with absorb voltage (currently at default: 29.1v), time (3-6 hrs, set at 5hr), I have done more frequent equalizations. Ending amps is and has been at 0.

                            If you recall, this all started with me wanting a consistent 1.26+ SG every night. But as it is, if I dedicate my day I can achieve that (restarting, equalizing, etc.), but no config will achieve that by itself. My primary system hits 1.27 every. single. night.

                            Comment

                            • SunEagle
                              Super Moderator
                              • Oct 2012
                              • 15208

                              #15
                              Originally posted by -robw-

                              It's all good. If you're curious as to what I did: 1) sent reply 2) edited to add quoting of Suneagle's response 3) tried re-editing to embolden a statement by Suneagle.



                              Classic does take over as lead charger, and Epever isn't terrible in backup role. For example, my larger system has 2 FM-80's and where I would rather each supply current 50-50, instead one always drops off later in the absorb cycle as "charged". So, right now one of them is supplying 40+ amps while the other is "charged" - not supplying anything. At least the Epever is supplying 1 amps right now while Classic is supplying 11.5a.

                              Thanks for the 76a rate. I was looking for that all morning because Crown had no idea.

                              As far as panel tilt, they're perfect for this time of year at 13 degrees. As far as Classic config, not only have I spent the past month talking with techs at Crown, Midnite Solar, Epever, and the people I bought equipment from, trying to solve SG issue, but I can't imagine what setting besides "max output amperage" (set at 80a) would control this. I have played with absorb voltage (currently at default: 29.1v), time (3-6 hrs, set at 5hr), I have done more frequent equalizations. Ending amps is and has been at 0.

                              If you recall, this all started with me wanting a consistent 1.26+ SG every night. But as it is, if I dedicate my day I can achieve that (restarting, equalizing, etc.), but no config will achieve that by itself. My primary system hits 1.27 every. single. night.
                              Well something is not working up to par with your system. You should be getting that 75amps of charging with 1800watts.

                              Since you have gone over all the possibilities for the Classic maybe one or more of the panels is not putting out what it is listed for and your system is rated below that 1800watt total.

                              Comment