junction between PV cables and THWN in conduit

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • RShackleford
    Solar Fanatic
    • Sep 2019
    • 311

    #46
    Originally posted by bob-n
    You're right. GE Silicone II appears to be neutral cure. They refer to it as GE Silicone 2+ below, but I think that's the same thing. Great to know. Thank you.
    https://www.gesealants.com/Frequentl...questions.aspx
    I didn't try to use the Silicon2 on wirenuts, rest assured.

    However, I did try to use an old tube of it for something else, and it was a rude shock. It never cured, and just turned into this nasty black grease. I complained to GE and they basically said "tough titty, it's only guaranteed for 3 years". Evidently the catalyst that causes curing wears out.

    Comment

    • bob-n
      Solar Fanatic
      • Aug 2019
      • 572

      #47
      Yes, I learned that lesson the hard way, too. Undried silicone is a yucky mess.
      7kW Roof PV, APsystems QS1 micros, Nissan Leaf EV

      Comment

      • ZhangSheng
        Junior Member
        • Nov 2026
        • 4

        #48
        Good approach overall — a few protection details that matter at this transition, beyond the box size and the connector choice:
        1. Keep the UV-exposed run short. PV cable is sunlight-resistant, but every metre left lying on the ground or across the rack is a metre that can be abraded, chewed or stepped on. Get the MC4 leads into the box and into conduit as soon as practical, support the cable so it does not rest on sharp rack edges, and use UV-rated ties rather than ordinary ones that go brittle in a season.

        2. Drip loop before the box. Let each PV cable drop below the gland level and come back up into the box, so rainwater running along the cable drips off instead of following it through the seal. Enter the box from below or from the side, never from the top, and put one cable per gland, sized to the cable diameter — a gland packed with two cables rarely seals on either of them.

        3. Deburr and bush the conduit ends. A freshly cut conduit edge is a knife edge. File it smooth and fit an insulating bushing where the THWN leaves the conduit into the box, so vibration and thermal movement do not wear through the insulation at the entry point. Leave a little slack inside the box as well, so a connector can be remade without pulling the conductors tight.

        4. Seal the box, but plan for water anyway. A gasketed weatherproof box with a proper lid seal is the right start, and a small drain provision at the lowest point is worth considering — a perfectly sealed box that does get water in stays wet. Keep the splices above the bottom of the box, and use grease-filled weatherproof connectors for the splices rather than ordinary wire nuts; as noted above, ordinary silicone caulk is corrosive to copper, while silicone grease is not.

        5. Grounding conductor in the conduit. Run the equipment grounding conductor inside the conduit with the circuit conductors, bond the box itself, and keep the array grounding continuous back to the main system ground. A separate bare ground run outside the conduit can work, but it is exposed to damage and corrosion, and it is easy to lose continuity at a clamp that was never properly tightened.

        Comment

        • SunEagle
          Super Moderator
          • Oct 2012
          • 15211

          #49
          Originally posted by ZhangSheng
          Good approach overall — a few protection details that matter at this transition, beyond the box size and the connector choice:
          1. Keep the UV-exposed run short. PV cable is sunlight-resistant, but every metre left lying on the ground or across the rack is a metre that can be abraded, chewed or stepped on. Get the MC4 leads into the box and into conduit as soon as practical, support the cable so it does not rest on sharp rack edges, and use UV-rated ties rather than ordinary ones that go brittle in a season.

          2. Drip loop before the box. Let each PV cable drop below the gland level and come back up into the box, so rainwater running along the cable drips off instead of following it through the seal. Enter the box from below or from the side, never from the top, and put one cable per gland, sized to the cable diameter — a gland packed with two cables rarely seals on either of them.

          3. Deburr and bush the conduit ends. A freshly cut conduit edge is a knife edge. File it smooth and fit an insulating bushing where the THWN leaves the conduit into the box, so vibration and thermal movement do not wear through the insulation at the entry point. Leave a little slack inside the box as well, so a connector can be remade without pulling the conductors tight.

          4. Seal the box, but plan for water anyway. A gasketed weatherproof box with a proper lid seal is the right start, and a small drain provision at the lowest point is worth considering — a perfectly sealed box that does get water in stays wet. Keep the splices above the bottom of the box, and use grease-filled weatherproof connectors for the splices rather than ordinary wire nuts; as noted above, ordinary silicone caulk is corrosive to copper, while silicone grease is not.

          5. Grounding conductor in the conduit. Run the equipment grounding conductor inside the conduit with the circuit conductors, bond the box itself, and keep the array grounding continuous back to the main system ground. A separate bare ground run outside the conduit can work, but it is exposed to damage and corrosion, and it is easy to lose continuity at a clamp that was never properly tightened.
          you do understand the original post is over 6years old

          Comment