    Isolating generator from solar system

    I have a customer who just had a whole house generator installed at their home where I had put solar panels a couple of years ago. The solar system backfeeds the main panel through a 40-amp breaker. The power to the house comes underground for a pedestal about 150' from the house. The electrician put the transfer switch by the pedestal and ran power down from the generator which is off in a different direction. Normally I would either tie the solar into a line-side tap on the utility side of the transfer switch or connect the solar to the main panel by way of a normally open contactor that is tied to the dry contacts in the transfer switch (when utility power fails, the contactor opens). Currently there is no way that I know of to tell where the power in the house is coming from (utility or generator) and no way to connect the solar to the transfer switch way down at the pedestal. (Apparently the conduit to the house is thought to be damaged, so pulling the main feed to the house and adding a signal wire is not possible).
    Anybody got any ideas?
  • Ampster
    Solar Fanatic
    • Jun 2017
    • 3649

    #2
    Where is the meter in this scenerio? Is that generator installation done according to code?
    9 kW solar, 42kWh LFP storage. EV owner since 2012

    Comment

    • Gordy
      Junior Member
      • May 2013
      • 6

      #3
      The meter is at the pedestal. Yes, the generator is done according to code. The only thing unusual is that the transfer switch is at the pedestal instead of at the house.

      Comment

      • Ampster
        Solar Fanatic
        • Jun 2017
        • 3649

        #4
        The only thing I can think of is a latching relay that would open contacts in the second or two between the time the grid drops and the time it takes the generator to start.

        Not an elegant solution and your customer would have to manually reset once power was restore. That reset is a weak link if some one inadvertently hit the reset while grid is down and generator is running. Is the solar inverter a more recent UL 1741 model? Is there a way to tweak the generator frequency?
        Last edited by Ampster; 11-07-2019, 09:51 AM.
        9 kW solar, 42kWh LFP storage. EV owner since 2012

        Comment

        • Gordy
          Junior Member
          • May 2013
          • 6

          #5
          Where would I get a latching relay?
          Would you happen to have a manufacturer who makes such a device?
          This may be the best solution given the circumstances.
          Maybe I could combine this with some sort of indicator light to remind them the solar is off until reset.

          Comment

          • bcroe
            Solar Fanatic
            • Jan 2012
            • 5198

            #6
            Originally posted by Gordy
            Where would I get a latching relay?
            When some power is available at the time needed, latching can be accomplished with
            an electrical circuit. For complete power loss, a 9V battery powering some CMOS logic
            could last the battery shelf life. Bruce Roe

            Comment

            • Ampster
              Solar Fanatic
              • Jun 2017
              • 3649

              #7
              Originally posted by Gordy
              Where would I get a latching relay?
              Would you happen to have a manufacturer who makes such a device?
              This may be the best solution given the circumstances.
              Maybe I could combine this with some sort of indicator light to remind them the solar is off until reset.
              I found some searching for latching relay on Google, Digikey, Amazon or other electronic suppliers. You will have to find one with coils for 240 v or use two with 120 coils. I will look in my archives for a two relay combo that works electronically as a latching relay. That is a good idea of a indicator light with a warning to not push reset when generator is on.

              What did you find out about the frequency specs of the generator or the inverter you installed (UL1741)? That would possible be a more foolproof method if you can tweak the generator output by a few Hz. That is just a theoretical solution from an anonymous guy on the Internet, I would get a second opinion before I tried that because you could damage the generator if not done property.
              Last edited by Ampster; 11-07-2019, 06:43 PM.
              9 kW solar, 42kWh LFP storage. EV owner since 2012

              Comment

              • Mike90250
                Moderator
                • May 2009
                • 16020

                #8
                latching relays https://www.grainger.com/category/el...nd-accessories

                Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
                || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
                || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

                solar: http://tinyurl.com/LMR-Solar
                gen: http://tinyurl.com/LMR-Lister

                Comment

                • SunEagle
                  Super Moderator
                  • Oct 2012
                  • 15123

                  #9
                  Any latching circuit component needs to insure the "contacts" are rated for the amperage going through them.

                  Building a system that can switch between grid, solar and a generator really needs some engineering so I advise the OP to get some expertise if they intend to pursue this endeavor.

                  Comment

                  • Ampster
                    Solar Fanatic
                    • Jun 2017
                    • 3649

                    #10
                    @Gordy , did the original solar install have the usual stickers on the service entrance? If so, the generator installer would have been on notice that there was solar downstream of his installation. If your solar install was UL1741 compliant there should be no risk to your equipment. I am not suggesting that you or your customer test that assumption. Based on @SunEagle 's comment that generator installer needs to verify the engineering. It is possible the generator could be at risk if for some reason the solar inverter did backfeed the generator. You may be able to use that as leverage for your customer to force the generator installer to fix the issue.
                    9 kW solar, 42kWh LFP storage. EV owner since 2012