1200W 24V Off Grid System Design Questions.

Collapse
X
 
  • Time
  • Show
Clear All
new posts
  • Shane.R13
    Junior Member
    • Apr 2018
    • 29

    #1

    1200W 24V Off Grid System Design Questions.

    Hi Everyone. I've been browsing these forums for a few days now. Collected a lot of information but nothing that gives me definite answers. So hence my creating a new topic.

    I am in the planing stages of an off grid solar system. I've obtained 4 300watt panels. VMP 36.1v IMP 8.30a VOC 44.6v ISC 8.87. This is all I have obtained regarding my system so i'm looking for advice on size of everything else to purchase. Oh and I'll be running about 1000w AC max through an inverter for now. 13 led lights a tv (50 inch plasma 400 watt - i know it will be replaced with more efficient technology one day) and satellite with the odd phone charger and cordless tool charger.

    How do i wire my panels for the most efficient system while keeping controller costs down? 2 series 2 parallel? How can I combine these parallels? combiner box or MC4 connectors? I've come to learn that i'll likely use an MPPT 60a controller?

    Currently my batteries are small. 2 12v 50ah in series for total 24v. I know this will not power my requirements for long. ( I have a generator after solar runs out with a 24v charger) This is basically to just make sure the system will run and keep my costs down the first year. Next year i plan to purchase 4 6v 428ah batteries to run in 24v.

    Heck I don't even know what size cables to run from the panels to the controller and from the controller to batteries and then from batteries to inverter.

    I know i've asked a lot and don't know a lot but any help with any of my questions would be kindly appreciated.

    Shane Solar Panel.png
  • Mike90250
    Moderator
    • May 2009
    • 16020

    #2
    1200w pv = 960w harvest under optimum conditions and about 38A output @ 25V So you are in the big boys game. You can reliably charge 380ah of battery, the tall case 428ah batteries will suffer from insufficient bubbling in the final stages of charge and will be prone to stratify.

    Your existing 12V 50ah batteries can only be charged at 5A, for longer life. But I know of no 50ah deep cycle battery, so they are on the way out. You need a charge contoller that can have a current limit set to not cook your batteries. I suggest a Morningstar Tristar MPPT 60. It has a handy web server in it, so you hook it to your home network, and can monitor with any browser
    Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
    || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
    || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

    solar: http://tinyurl.com/LMR-Solar
    gen: http://tinyurl.com/LMR-Lister

    Comment

    • Shane.R13
      Junior Member
      • Apr 2018
      • 29

      #3
      Thank you for the reply. I was worried about cooking my current batteries, but was hoping i could get a system running that would allow me to change some parameters as i upgrade batteries. Unfortunately This is a remote off grid setup so remotely monitoring isn't an option. With the Morningstar controller am i able to program the charge rate and basically leave it set? or does it need to be constantly monitored? Thanks for the info regarding my future battery setup. A local solar company suggested that amount of amp hours, so i will have to conference with them on that.

      Comment

      • Shane.R13
        Junior Member
        • Apr 2018
        • 29

        #4
        Also, would i maybe be better suited to just buy a cheap PWM charger for these size batteries? and buy say the morning star when i Purchase the larger aH batteries?

        Comment

        • Sunking
          Solar Fanatic
          • Feb 2010
          • 23301

          #5
          Until you get new batteries, wiring up a single panel is simple. Forget that power hog of a TV because because those batteries you have now will give out in a hour or so. Your current batteries are made for a 150 to 200 watt panel and inverter. When you get some real batteries of 400 to 500 AH wire the panels 2S2P but for now just 1 panel is a bit too large for your batteries.
          Last edited by Sunking; 04-15-2018, 11:02 AM.
          MSEE, PE

          Comment

          • Sunking
            Solar Fanatic
            • Feb 2010
            • 23301

            #6
            Originally posted by Shane.R13
            Also, would i maybe be better suited to just buy a cheap PWM charger for these size batteries?
            Not a terrible idea when use with just one panel. Waste of time and money with 2 or more panels. At 8 amps will knock that panel wattage down to just under 200 watts and be a good fit for a 50 AH battery.
            MSEE, PE

            Comment

            • Shane.R13
              Junior Member
              • Apr 2018
              • 29

              #7
              Thank you. So I guess it seems like for now it will be one panel into a pwm controller until I get real batteries. What amp pwm should be I get? Should I still be running batteries in 24v? The reason I ask is that I have a couple 400w 12v inverters already and would rather use them than buy a 1000w 24v and waste power converting that I won

              Comment

              • Shane.R13
                Junior Member
                • Apr 2018
                • 29

                #8
                That I won

                Comment

                • Sunking
                  Solar Fanatic
                  • Feb 2010
                  • 23301

                  #9
                  Originally posted by Shane.R13
                  Thank you. So I guess it seems like for now it will be one panel into a pwm controller until I get real batteries. What amp pwm should be I get? Should I still be running batteries in 24v? The reason I ask is that I have a couple 400w 12v inverters already and would rather use them than buy a 1000w 24v and waste power converting that I won
                  You are welcome. Each panel is rated for 8 amps.

                  PWM Output Current = Input Current.

                  8 amps per panel is the magic answer. OK I just gave you a trick answer. Note the equation above. 8 amps of current is perfect for a 50 AH battery. So if you used 24 volt battery only one panel. But if you wire the batteries in parallel makes a 12 volts @ 100 AH battery and can easily handle 16 amps of current and to do that you would wire two panels in parallel.

                  Here is the trick and what is confusing you right now asking WTF is going on. Watts = Volts x Amps.

                  8 amps x 12 volts = 96 watts.
                  8 amps x 24 volts = 192 watts

                  You have 300 watt panels and each panel max output is 8 amps. So two panels in PARALLEL is 16 amps

                  16 amps x 12 volts = 192 watts from 600 watts of panels

                  MPPT is different. MPPT Output Current = Panel Wattage / Battery Voltage.

                  Try running numbers like 300 watts / 12 volts = ??

                  or

                  300 watts / 24 volts = ??

                  What is in common? Either way you get 300 watts with MPPT. Know the math, and you have the power and rule.







                  MSEE, PE

                  Comment

                  • Shane.R13
                    Junior Member
                    • Apr 2018
                    • 29

                    #10
                    Ok, so lets say i have a 60amp MPPT controller, if i hook one 300w 8amp panel into it. That means my output amperage to the batteries is going to be 300/24 = 12.5 amps or 300/12 = 25amps? What i'm gathering from your previous post is that no matter the size of my controller amperage wise it will only output panel watts/battery voltage? less panels less output more panels more output.

                    on another note, if i did one panel at 8amps with a 10amp controller (25% safety margin) then i wont cook my batteries?

                    Comment

                    • clinecustoms
                      Junior Member
                      • Oct 2018
                      • 4

                      #11
                      This post seems the most relevant to my question, and I need some quick help as I am ordering batteries asap.
                      I am going for a backup system off grid mainly for small items with genset for larger items.
                      I have decided on an mppt 80a 24v controller (to allow for possible expansion) and 4 305w Canadian panels, my last question is the batteries as I don't plane to discharge more then 50% I am okay with 4 t105re's at 24v, however for 50% more I have the option of 4 L16-b 6v 375's also at 24v, but I am worried my panels may not keep up with those bigger batteries charge needs in one day if discharged to 50%
                      I know there are many factors and math things, but I really just need to know for the life of the battery will it be better to go cheaper with the t105re's and have excess power or go closer to the capability of the panels with the larger batteries that likely won't get discharged as deeply. Is it more of a preference? Hoping for quick reply, cant post new thread but mods please feel free to move.

                      Comment

                      • MambaJack
                        Member
                        • Sep 2018
                        • 51

                        #12
                        Originally posted by Mike90250
                        1200w pv = 960w harvest under optimum conditions and about 38A output @ 25V So you are in the big boys game. You can reliably charge 380ah of battery, the tall case 428ah batteries will suffer from insufficient bubbling in the final stages of charge and will be prone to stratify.
                        Couple of questions here. with 960w of output from the panels, would a 40A mppt charger controller work?
                        In the case of the batteries and reliably charging 380ah, is that the bank size, or the amount being charged. In my case, have a 470ah bank, but don't plan to go below 50% usage?

                        Comment

                        • SunEagle
                          Super Moderator
                          • Oct 2012
                          • 15186

                          #13
                          Originally posted by MambaJack

                          Couple of questions here. with 960w of output from the panels, would a 40A mppt charger controller work?
                          In the case of the batteries and reliably charging 380ah, is that the bank size, or the amount being charged. In my case, have a 470ah bank, but don't plan to go below 50% usage?
                          While the numbers are not exact you can quickly calculate the amount of charging amps by dividing the battery voltage into the panel wattage.

                          So 960w / 24v = 40amps. And based on a C/10 charge rate (where C = the battery Ah rating) that allows you to charge a 24v 400Ah battery bank.

                          With a 470Ah battery and only 40Amps you have about a C/12 (470Ah / 40A = 11.75h). Which is the slowest you should charge an FLA type battery.

                          Comment

                          • MambaJack
                            Member
                            • Sep 2018
                            • 51

                            #14
                            Originally posted by SunEagle

                            While the numbers are not exact you can quickly calculate the amount of charging amps by dividing the battery voltage into the panel wattage.

                            So 960w / 24v = 40amps. And based on a C/10 charge rate (where C = the battery Ah rating) that allows you to charge a 24v 400Ah battery bank.

                            With a 470Ah battery and only 40Amps you have about a C/12 (470Ah / 40A = 11.75h). Which is the slowest you should charge an FLA type battery.
                            Thanks Sun Eagle. So would I be better off adding 2 more panels for a C/7.83 charge rate/

                            Comment

                            • SunEagle
                              Super Moderator
                              • Oct 2012
                              • 15186

                              #15
                              Originally posted by MambaJack

                              Thanks Sun Eagle. So would I be better off adding 2 more panels for a C/7.83 charge rate/
                              Depends on the panels and CC. You would have to increase the size of your CC to be able to handle the total wattage of your panel system.

                              Typically a 24V 60 amp battery charger should be able to accept up to 1440 watts but a 40amp CC might only accept about 1000 watts.

                              Comment

                              Working...