    Originally posted by peakbagger
    I am bit confused with the extra rake boards on each side of the array, aesthetics or practical?
    Yeah, they sort of ended up being somewhat vestigial. I had started with a consistent 24" spacing, but then doubled up on both sides of the posts, for additional support. I may just remove the boards at the end.

    I have a little cheap-o meter that I installed on my car charging outlet a few years ago. I may swap that over to this circuit, just for an easy way to view/tally power/energy production; but I'll wait until after I've gotten all my inspections. The inspector is supposed to be coming today.

    Leave a comment:


  • peakbagger
    replied
    Looks a nice profession job. I am bit confused with the extra rake boards on each side of the array, aesthetics or practical? I would suggest trimming back the trees at the back of the array to cut down on squirrel traffic. It appears as though the bottom of the panels are less than 8 feet from the ground, some AHJs require that the array under the array be enclosed with locked fence. Alternatively you may need to enclose the wiring underneath the panels with hardware cloth or similar mechanically attached barrier. I like the hardware cloth option as it also may be good rodent and bird proofing.

    If you just cant wait for a network connection, flip al the breakers in the house off except for the PV and use the house meter to calculate the production. Good excuse to exercise all the breakers, of course the inevitable darn flashing clocks will drive you nuts until you reset them.

    Leave a comment:


  • brant2000
    replied
    I got my panels installed over the weekend. It is now definitely apparent that shading is probably a little worse than I had expected and I need to do some tree trimming. That said, I think it turned out really great and can't wait to get the final approvals to go live full time. I don't have my network connection installed yet, so no way to meter production. I was able to verify that my meter was spinning in reverse, so at least know that the system was live.

    IMG_20170917_153242388.jpg

    Leave a comment:


  • brant2000
    replied
    Originally posted by sensij

    Have you passed inspection and been given the OK to generate by your power company?
    Not to generate, but am allowed up to 2 hours for "testing purposes".

    Leave a comment:


  • sensij
    replied
    Originally posted by brant2000
    As I'll have all of my AC cabling and ground connected first, is there any reason that I can't power the system up and begin connecting panels as I get them installed?
    Have you passed inspection and been given the OK to generate by your power company?

    Leave a comment:


  • brant2000
    replied
    Last evening I installed the conduit inside my garage and finished pulling the wire between a disconnect switch and the subpanel where I am tying in. I made all connections and tested to ensure that the multigates power up. I now just need to make the connections to tie my micros into the multigate and finish up some grounding. Perhaps I'll have panels going up this weekend .

    As I'll have all of my AC cabling and ground connected first, is there any reason that I can't power the system up and begin connecting panels as I get them installed?

    Leave a comment:


  • Mike90250
    replied
    Originally posted by max2k

    why not 1000' ? Now you have to live with that For me it's pretty impressive.
    I got lucky that it didn't end up being 1020 feet. That would have been bad. I used a measuring wheel down a wooded hillside, bought and laid conduit and counted the 20' pieces used, then ordered reels of cable.
    cables3.jpg

    Leave a comment:


  • max2k
    replied
    Originally posted by foo1bar

    It reads:
    "Raceways, other than busways or exposed raceways having hinged or removable covers, shall be installed complete ... prior to the installation of conductors."

    A PVC raceway doesn't have those covers - therefore it doesn't fall into the exception for ones having covers.
    Since it doesn't fall into that exception it would be subject to the rule.
    And the rule is that it must be installed completely BEFORE pulling wires.

    busways with covers they make an exception for - so those can have the wires installed while they are still being put together.
    For example, a set of busways at the top of rows of computer racks. With this exception the electrician can do just a few racks, and put in the wire, then extend the busway to the next set of racks, install the wire, and so on. Without the exception they'd have to install the *complete* set before running any wires.



    If you are careful about it, you can probably make it so noone can tell the difference.
    But you still were not doing the install to code.
    OK, I stand corrected and admit that reading/understanding NEC is not my strong point, thanks for clarification. Weird requirement though, I'd expect it to be the exact opposite in PVC case. I also completely assembled my exposed EMT raceway which has covers on pulling elbows and then pulled the wires as it was easier this way.

    Leave a comment:


  • foo1bar
    replied
    Originally posted by max2k

    my point was different- there's no way anyone can tell the difference and my overall understanding is NEC mostly concerned with the finished result, not the process which produced it. Otherwise inspectors would need to be present at all times to oversee the construction. That might be sometimes the case but not on residential jobs.

    BTW, 2014 NEC reads: "Raceways, other than busways or exposed raceways having hinged or removable covers, shall be installed complete between outlet, ..." which makes sense- why on Earth someone would install raceway with covers in parts while it can be fully assembled and then wires pulled through using those covers? In OP case his PVC raceway does not have those covers so for me the jury is out why it is not code complaint.
    It reads:
    "Raceways, other than busways or exposed raceways having hinged or removable covers, shall be installed complete ... prior to the installation of conductors."

    A PVC raceway doesn't have those covers - therefore it doesn't fall into the exception for ones having covers.
    Since it doesn't fall into that exception it would be subject to the rule.
    And the rule is that it must be installed completely BEFORE pulling wires.

    busways with covers they make an exception for - so those can have the wires installed while they are still being put together.
    For example, a set of busways at the top of rows of computer racks. With this exception the electrician can do just a few racks, and put in the wire, then extend the busway to the next set of racks, install the wire, and so on. Without the exception they'd have to install the *complete* set before running any wires.

    my point was different- there's no way anyone can tell the difference
    If you are careful about it, you can probably make it so noone can tell the difference.
    But you still were not doing the install to code.

    Leave a comment:


  • bcroe
    replied
    Originally posted by max2k

    well, if its threaded raceway I'd understand the point to avoid twisting wires in already pulled section otherwise
    PVC elbow can be pulled over wire and glued in place without jeopardizing quality. You won't be able to tell how
    it was done after the fact.
    The end elbows were glued on. Bruce Roe

    Leave a comment:


  • max2k
    replied
    Originally posted by Mike90250
    I pulled 980' of #6 x3 aluminum when I did my runs. About 6 quarts of elephant snot (cable lube) and 4 pull stations, each manned, and did it in one pass. Used the tractor to hold a bank of pulleys up high, to feed the spools down into the conduit. I used the nylon webbing pull tape
    why not 1000' ? Now you have to live with that For me it's pretty impressive.
    Last edited by max2k; 09-13-2017, 10:44 PM.

    Leave a comment:


  • max2k
    replied
    Originally posted by foo1bar

    You won't be compliant with NEC 300.18A

    Whether you can get away with it is a completely different question.
    my point was different- there's no way anyone can tell the difference and my overall understanding is NEC mostly concerned with the finished result, not the process which produced it. Otherwise inspectors would need to be present at all times to oversee the construction. That might be sometimes the case but not on residential jobs.

    BTW, 2014 NEC reads: "Raceways, other than busways or exposed raceways having hinged or removable covers, shall be installed complete between outlet, ..." which makes sense- why on Earth someone would install raceway with covers in parts while it can be fully assembled and then wires pulled through using those covers? In OP case his PVC raceway does not have those covers so for me the jury is out why it is not code complaint.
    Last edited by max2k; 09-13-2017, 10:43 PM.

    Leave a comment:


  • AzRoute66
    replied
    Ha. When I worked at the copper mine (30ish years ago), I can tell you that the conduit was frequently installed from the ends towards the middle, even if a full pull was pretty feasible. That was an IBEW union shop too.

    Leave a comment:


  • Mike90250
    replied
    I pulled 980' of #6 x3 aluminum when I did my runs. About 6 quarts of elephant snot (cable lube) and 4 pull stations, each manned, and did it in one pass. Used the tractor to hold a bank of pulleys up high, to feed the spools down into the conduit. I used the nylon webbing pull tape

    Leave a comment:


  • foo1bar
    replied
    Originally posted by max2k
    well, if its threaded raceway I'd understand the point to avoid twisting wires in already pulled section otherwise PVC elbow can be pulled over wire and glued in place without jeopardizing quality. You won't be able to tell how it was done after the fact.
    You won't be compliant with NEC 300.18A

    Whether you can get away with it is a completely different question.

    Leave a comment: