Exactly. I'm combining pairs of strings in the equipment shed, with two charge controllers. The box at the array end is just a place to transition from PV wire pairs for each string to the 10x9 cable.
That ninth conductor works nicely as a backup EGC, with my metallic conduit (lock nuts on both interior and exterior of the boxes) serving as the other EGC.
That ninth conductor works nicely as a backup EGC, with my metallic conduit (lock nuts on both interior and exterior of the boxes) serving as the other EGC.