The conductors between the main panel and the subpanel form an interesting area for discussion when PV backfeed is involved. Some inspectors assume that some day someone might tap a load to the feeder somewhere between the main and the sub, thus creating a situation where the feeder could be fed from both ends and overloaded. This, in their minds, justifies applying the 120% rule to the feeder conductors.
Others argue (with logic but not necessarily literal code support) that if there are no taps on the feeder now you can calculate on the basis that there will never be a load in the middle of the feeder. So the current in the feeder cannot exceed the larger of the PV output current or the feeder breaker current.
Others argue (with logic but not necessarily literal code support) that if there are no taps on the feeder now you can calculate on the basis that there will never be a load in the middle of the feeder. So the current in the feeder cannot exceed the larger of the PV output current or the feeder breaker current.