    Xantrex XW6048 Bulk & Absorb voltages seem low

    HI Guys

    No matter if my Xantrax Inverter/charger is on Gen or solar it seems that the max voltage I see on the charge screen is 53.8v. The custom setting are
    Bulk 58.8v
    Absorb 58.8
    Float 54.8

    The batteries are used solidly overnight so I would expect it to go thru its cycles of voltages

    Am I missing something


    Thanks
    Steve
  • gmanInPA
    Solar Fanatic
    • Mar 2016
    • 173

    #2
    This is just a stab in the dark, but the Xantrex XW chargers are often temperature-compensated. I wonder if this might be adjusting your charge voltages? Do you have the BTS installed? Also... I find that some of my settings don't seem to "stick" unless I reboot the inverter. That's not always the case, but the software (at least the combox software) is wonky.

    Comment

    • gmanInPA
      Solar Fanatic
      • Mar 2016
      • 173

      #3
      Looking into this a bit further... if you don't have a BTS installed, this is how the XW inverter behave:

      When the internal temperature of the Xantrex XW Series Inverter/Charger exceeds a preset limit, it begins to limit output power automatically to ensure maximum internal temperatures are not exceeded.
      It does so based on the default battery temperature settings:

      Default Batt Temp



      Selects the battery temperature charging compensation if a battery temperature sensor is not installed. In the absence of a battery temperature sensor, the charger uses one of three settings: Cool (5 °C/41 °F), Warm (25 °C/77 °F), or Hot (40 °C/104 °F).
      If you have the BTS installed, rather than using the default, it will of course use the BTS temperature.

      This is where I'd look further to figure that out. If you don't have a BTS, it would probably be preferred over using a default temp - especially since that would need to otherwise change frequently. If you do have a BTS - this might be an expected behavior for your battery temperature. I believe those values are "not to exceed" values.

      Comment

      • SteveVk
        Junior Member
        • Mar 2016
        • 2

        #4
        Thanks GmaninPa I'll check the BTS tomorrow, I think it does.. but if its attached close enough to the terminate to actually work I look at (I didn't do the install).. And a re boot. I was wondering if they have reasonable use (load) over night would I be better on a 2 stage cycle than 3?

        Comment

        • gmanInPA
          Solar Fanatic
          • Mar 2016
          • 173

          #5
          I have my XW's charger set to use 2 stage and my CC's set to use 3-stage - but I don't rely on my PV for the sole source of recharging, or even my generator - unless I am off-grid for long-enough to warrant so. If I recall correctly - If you do any grid sell, 2 stage appears to be the Schneider-recommended approach for the inverter's charger because otherwise it won't sell power unless the batteries have reached float - which can be a very long time. If you have an AGS installed, the triggers for such will determine much of how the generator works with the XW's charger.

          Personally, I don't want my generator bringing my batteries to float - just to absorption or to a DoD around 95% - otherwise, the amount of fuel used is substantial, and usually unnecessary unless there is a long period without sun. If I were off-grid (or WHEN I am off-grid), I would continue to use the same setup I have now - though I'd probably attempt to follow the Smoke Model of charging outlined in the battery section.

          If you're off-grid, the other off-grid folks here - especially those with XWs (ie Mike90250 I think) probably have more keen insights into the best settings for such.

          Comment

          • gmanInPA
            Solar Fanatic
            • Mar 2016
            • 173

            #6
            Originally posted by SteveVk
            ... but if its attached close enough to the terminate to actually work I look at (I didn't do the install)..
            The BTS probes should be either directly on the terminal, or stuck to the sides of the battery using the included sticky tape. If you have Schneiders MPPT CC's, they should also have BT probes. I think the XW does also. If you have Schneider gear and connected via modbus, I believe you only need one probe for temp, and one for mid-point voltage. These could be easily relocated if necessary - assuming safely done.

            Comment

            • Mike90250
              Moderator
              • May 2009
              • 16020

              #7
              I can't add much, I use the BTS. and have changed my set-points for my bank, the generator charges my NiFe bank up to 64V.
              Powerfab top of pole PV mount (2) | Listeroid 6/1 w/st5 gen head | XW6048 inverter/chgr | Iota 48V/15A charger | Morningstar 60A MPPT | 48V, 800A NiFe Battery (in series)| 15, Evergreen 205w "12V" PV array on pole | Midnight ePanel | Grundfos 10 SO5-9 with 3 wire Franklin Electric motor (1/2hp 240V 1ph ) on a timer for 3 hr noontime run - Runs off PV ||
              || Midnight Classic 200 | 10, Evergreen 200w in a 160VOC array ||
              || VEC1093 12V Charger | Maha C401 aa/aaa Charger | SureSine | Sunsaver MPPT 15A

              solar: http://tinyurl.com/LMR-Solar
              gen: http://tinyurl.com/LMR-Lister

              Comment

              • Sunking
                Solar Fanatic
                • Feb 2010
                • 23301

                #8
                Originally posted by SteveVk
                The batteries are used solidly overnight so I would expect it to go thru its cycles of voltages

                Am I missing something
                Most likely you are missing something. Enough panel wattage and knowledge how batteries work. Just because you set a voltage point on a charger does not mean that is the voltage you are going to see. You will only see those voltages if the batteries actually get charged up to that voltage, otherwise they will always be lower. Why you asked. Because you do not have enough panel wattage to recharge your batteries.

                As for the generator, I can only speculate you do not run your generator long enough to recharge the batteries.

                Answer these simple questions.

                1. Panel Wattage.
                2. Controller make and model
                3. Battery Capacity Amp Hours
                4. Generator Size


                In the meantime read:

                Bulk, Absorb, Float Equalize
                Killing Your Batteries

                Lastly never use you equipment to measure voltages. Use your DMM.
                MSEE, PE

                Comment

                • Sunking
                  Solar Fanatic
                  • Feb 2010
                  • 23301

                  #9
                  Originally posted by gmanInPA
                  This is just a stab in the dark, but the Xantrex XW chargers are often temperature-compensated. I wonder if this might be adjusting your charge voltages? .
                  If that is the case, battery voltage set point goes higher in cold, not lower.

                  MSEE, PE

                  Comment

                  • gmanInPA
                    Solar Fanatic
                    • Mar 2016
                    • 173

                    #10
                    Sunking - would you be open to doing any paid consultation/review of my system?

                    Comment

                    • Sunking
                      Solar Fanatic
                      • Feb 2010
                      • 23301

                      #11
                      Originally posted by gmanInPA
                      Sunking - would you be open to doing any paid consultation/review of my system?
                      You do know I am in Panama right? Send me a PM with your email address.
                      MSEE, PE

                      Comment

                      • gmanInPA
                        Solar Fanatic
                        • Mar 2016
                        • 173

                        #12
                        Originally posted by Sunking
                        If that is the case, battery voltage set point goes higher in cold, not lower.

                        Ok, but if you had no BTS and a default setting of HOT or WARM in the inverter, wouldn't that lower the set point voltage?

                        Comment

                        • gmanInPA
                          Solar Fanatic
                          • Mar 2016
                          • 173

                          #13
                          Originally posted by Sunking

                          You do know I am in Panama right? Send me a PM with your email address.
                          I don't seem to be able to send people PMs in any way. It tells me to try logging in as someone else Sigh. If you have access to Skype or something similar, it doesn't matter to me where you're located .

                          Comment

                          • Sunking
                            Solar Fanatic
                            • Feb 2010
                            • 23301

                            #14
                            Originally posted by gmanInPA


                            Ok, but if you had no BTS and a default setting of HOT or WARM in the inverter, wouldn't that lower the set point voltage?
                            yes it would. But I still suspect he just does not have enough panel wattage to recharge. Disable it and he will know. If he had a hydrometer he would know exactly what is going on.
                            MSEE, PE

                            Comment

                            • Sunking
                              Solar Fanatic
                              • Feb 2010
                              • 23301

                              #15
                              Originally posted by gmanInPA

                              I don't seem to be able to send people PMs in any way. It tells me to try logging in as someone else Sigh. If you have access to Skype or something similar, it doesn't matter to me where you're located .
                              Crap I forgot PM do not work.

                              MSEE, PE