Hey everyone, I've done my best to sort through the information here and on Mike Holt's forums, and this is what I came up with. Does anyone care to sanity check my plan before I start drilling holes?
I've got 21 280w SolarWorld panels with Enphase m215 w/IG micro inverters split into strings of 10 and 11. I figure these will run at 9 and 9.9 amps respectively. I've got the Enphase trunk cable running through a Soladeck roof penetration probably to a j-box just inside the attic to make the transition to 12/3 NM (to get around any possible NM on the roof concerns). These two circuits run for about 75' to two 20amp breakers in a 100amp load center. These combine there then go to a 60amp AC disco, to the solar generation meter, then to a 30amp breaker in the 150amp main panel.
Other than the 20amp breakers, the load center, and the disco being oversized, does anyone see any glaring mistakes here? I am using the circuits as the EGC for the racking through the micro inverters IG, and didn't see any specific size requirement for it. In the future I might tie the top right 4 panels into the string with 10 and add more panels on the garage into the string that would be left with 7 panels on it, but that would require me to upgrade my main panel. The new 14 panel string would be at 12.6 amps which still works with 12/3 right?
I also know the 280w panels lie outside the recommended spec of the m215's, but my house faces more west than south, and I figure after first year degradation....maybe I'm just being cheap.
Thanks in advance.
I've got 21 280w SolarWorld panels with Enphase m215 w/IG micro inverters split into strings of 10 and 11. I figure these will run at 9 and 9.9 amps respectively. I've got the Enphase trunk cable running through a Soladeck roof penetration probably to a j-box just inside the attic to make the transition to 12/3 NM (to get around any possible NM on the roof concerns). These two circuits run for about 75' to two 20amp breakers in a 100amp load center. These combine there then go to a 60amp AC disco, to the solar generation meter, then to a 30amp breaker in the 150amp main panel.
Other than the 20amp breakers, the load center, and the disco being oversized, does anyone see any glaring mistakes here? I am using the circuits as the EGC for the racking through the micro inverters IG, and didn't see any specific size requirement for it. In the future I might tie the top right 4 panels into the string with 10 and add more panels on the garage into the string that would be left with 7 panels on it, but that would require me to upgrade my main panel. The new 14 panel string would be at 12.6 amps which still works with 12/3 right?
I also know the 280w panels lie outside the recommended spec of the m215's, but my house faces more west than south, and I figure after first year degradation....maybe I'm just being cheap.
Thanks in advance.